PowerChute Network Shutdown 4.1 Not shutting down host

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute Network Shutdown 4.1 Not shutting down host
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 01:47 AM . Last Modified: ‎2024-02-29 10:33 PM

0 Likes
3
2784
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:47 AM . Last Modified: ‎2024-02-29 10:33 PM

PowerChute Network Shutdown 4.1 Not shutting down host

Hello all,

I'm having the following situation:
I have 2 Esxi 6.0 Hosts with a few VM's and a VCSA 6.0 and a PowerChute Network Shutdown appliance running.

I got everything configured but now I cant get everything to shut down properly.
The problem is this, first the PwoerChute appliance tries to put the hosts in maintenance mode. All VM's excetp VCSA and the powerchut appliance shut down. Then the Maintenance mode request is cancelled and the VCSA is shut down. The PowerChute appliance sees this and after the configured time the host with VCSA is shut down. But then the PowerChute Appliance is shut down and I'm left with 1 host running no VM's?!

I followed the manual and made a global user on vcenter and the hosts. With that account I can login so it works. I dont' have an AD. I dont see errors in error.log..

Or is the solution to run PowerChute on each host and shutdown that host? That seems to work but itsn't the best solution I think...

Who can help me fix this issue?

Thanks in advance!

Here the last eventlog, here I tried without VM shut down configured in PowerChute but configured in ESXI hosts

10/14/2015    10:59:48    UPS has switched to battery power.
10/14/2015    11:00:48    UPS critical event: On Battery.
10/14/2015    11:00:48    Shutdown sequence started on Hosts 10.10.1.10, 10.10.1.11 in response to UPS critical event: On Battery.
10/14/2015    11:00:51    Starting Maintenance Mode Task on Host 10.10.1.11.
10/14/2015    11:00:51    Starting Maintenance Mode Task on Host 10.10.1.10.
10/14/2015    11:00:51    Exit maintenance mode on Host 10.10.1.11.
10/14/2015    11:00:51    Exit maintenance mode on Host 10.10.1.10.
10/14/2015    11:00:52    Shutting down vCenter Server VM VCSA 6.0.
10/14/2015    11:00:53    Maintenance Mode Task cancelled on Host 10.10.1.10 as VCSA VM is shutting down.
10/14/2015    11:03:59    Cannot connect to vCenter Server. PowerChute may not be able to issue commands to Virtual Machines or Hosts.
10/14/2015    11:03:59    Shutting down vCenter Server VM Host 10.10.1.10.
10/14/2015    11:04:01    Shutting down physical machine that PowerChute is running on.
10/14/2015    13:19:48    PowerChute successfully opened UDP port 3052.
10/14/2015    13:20:15    Communication has been established.
10/14/2015    13:20:16    PowerChute Network Shutdown version 4.1.0 monitoring started.
10/14/2015    13:20:17    PowerChute successfully opened TCP port 3052.
10/14/2015    13:20:17    PowerChute successfully opened TCP port 6547.

And this eventlog with shutdown in PowerChute appliance configured and not in ESXI hosts

10/14/2015    13:20:47    Available runtime has been exceeded.
10/14/2015    13:37:18    UPS has switched to battery power.
10/14/2015    13:38:18    UPS critical event: On Battery.
10/14/2015    13:38:18    Shutdown sequence started on Hosts 10.10.1.10, 10.10.1.11 in response to UPS critical event: On Battery.
10/14/2015    13:38:20    Starting Maintenance Mode Task on Host 10.10.1.11.
10/14/2015    13:38:20    Shutting down VMs on Host 10.10.1.11.
10/14/2015    13:38:20    Starting Maintenance Mode Task on Host 10.10.1.10.
10/14/2015    13:38:20    Shutting down VMs on Host 10.10.1.10.
10/14/2015    13:40:20    Exit maintenance mode on Host 10.10.1.11.
10/14/2015    13:40:20    Exit maintenance mode on Host 10.10.1.10.
10/14/2015    13:40:21    Shutting down vCenter Server VM VCSA 6.0.
10/14/2015    13:40:21    Maintenance Mode Task cancelled on Host 10.10.1.10 as VCSA VM is shutting down.
10/14/2015    13:41:49    Cannot connect to vCenter Server. PowerChute may not be able to issue commands to Virtual Machines or Hosts.
10/14/2015    13:43:22    Starting Maintenance Mode Task on Host 10.10.1.10.
10/14/2015    13:43:23    Host 10.10.1.10 has successfully entered maintenance mode.
10/14/2015    13:43:24    Shutting down vCenter Server VM Host 10.10.1.10.
10/14/2015    13:43:25    Shutting down physical machine that PowerChute is running on.
10/14/2015    13:49:12    PowerChute successfully opened UDP port 3052.
10/14/2015    13:49:39    Communication has been established.
10/14/2015    13:49:40    PowerChute Network Shutdown version 4.1.0 monitoring started.
10/14/2015    13:49:41    PowerChute successfully opened TCP port 3052.
10/14/2015    13:49:41    PowerChute successfully opened TCP port 6547.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
mchomicz_apc
Crewman mchomicz_apc
Crewman

Posted: ‎2021-07-08 01:47 AM . Last Modified: ‎2024-02-29 10:32 PM

0 Likes
0
2782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:47 AM . Last Modified: ‎2024-02-29 10:32 PM

Roel,

I would also check /opt/APC/PowerChute/group1/pcnsconfig.ini file and make sure this line says 'true'

isPCNSonVM = true

I have had one installation where for some mysterious reason PCNS running on a virtual appliance had  this set to FALSE and also this line was present:

shutdownCommand = /opt/APC/PowerChute/group1/bin/shutdown

Effectively, the VM installation thought it was running on a physical machine and was issuing /sbin/shutdown -h command.

Had it been running on a physical host - that would have had the effect of powering it off... Alas one node in the cluster was always staying up. The VM was powering itself off though.

Hope this helps someone!

Michael

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:47 AM . Last Modified: ‎2024-02-29 10:32 PM

0 Likes
0
2782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:47 AM . Last Modified: ‎2024-02-29 10:32 PM

Hi,

Both test show that PCNS is attempting to power down both hosts. The log indicates PCNS appliance is running on 10.10.1.11 is this the host that is not powering down? 

10/14/2015    11:04:01    Shutting down physical machine that PowerChute is running on.

10/14/2015    13:43:25    Shutting down physical machine that PowerChute is running on.

You should run the second test again while PCNS is in debug mode. Kbase FA230514 "How to put PCNS version 3.1 and above into debug mode?" will help. Also, you should check the host log to see if it is receiving the power down command. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:47 AM . Last Modified: ‎2024-02-29 10:32 PM

0 Likes
0
2783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:47 AM . Last Modified: ‎2024-02-29 10:32 PM

That is indeed the host that didn't shut down.

I will try one more time with debug mode and come back here and post the output.

Reply

Link copied. Please paste this link to share this article on your social media post.

mchomicz_apc
Crewman mchomicz_apc
Crewman

Posted: ‎2021-07-08 01:47 AM . Last Modified: ‎2024-02-29 10:32 PM

0 Likes
0
2783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:47 AM . Last Modified: ‎2024-02-29 10:32 PM

Roel,

I would also check /opt/APC/PowerChute/group1/pcnsconfig.ini file and make sure this line says 'true'

isPCNSonVM = true

I have had one installation where for some mysterious reason PCNS running on a virtual appliance had  this set to FALSE and also this line was present:

shutdownCommand = /opt/APC/PowerChute/group1/bin/shutdown

Effectively, the VM installation thought it was running on a physical machine and was issuing /sbin/shutdown -h command.

Had it been running on a physical host - that would have had the effect of powering it off... Alas one node in the cluster was always staying up. The VM was powering itself off though.

Hope this helps someone!

Michael

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore