PowerChute Bussines Edition Shutdown ONLY BEFORE to run the command.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute Bussines Edition Shutdown ONLY BEFORE to run the command.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

0 Likes
5
1585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

PowerChute Bussines Edition Shutdown ONLY BEFORE to run the command.

Hi.

I have 3 APC Smart UPS RC 3000 without Ethernet adapter. Only serial cable connected to different Windows 2003 and 2008 servers. PowerChute Bussines Edition.

If i right click the host under Hostname list, then Properties... Apears Device Properties windows for that host UPS.

Then i click the + Server Shutdown (left side list) and Shutdown Sequence.

After that i click Configure Shutdown Sequence (the blue link in the right panel under the list).

Mark Command File box and press Next button.

Select the default.cmd, that i have edited with my script content that works OK. (pressed Test button). After that i press Next.

And here it comes the problem: I can t figure out how to put FIRST the command to run the command BEFORE the system shutdown. It's impossible. I can' t understand how the programmer think that you can run a .cmd script IF THE SYSTEM IS ALREADY SHUTTING DOWN!!! The cmd shoud run in FIRST place, the system shut down in SECOND!

¿Can you explain to me how to revert the order?

Cheers!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • before
  • command
  • first
  • PowerChute
  • shutdown
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

0 Likes
0
1585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

Hi,

Changes were made to versions that work with Microlink Smart-UPS i.e. SMT, SMX, SRT, SMC that allows for a greater number.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

0 Likes
0
1585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

Hi,

PowerChute is written to run the command file prior to the OS shutdown. I pulled the information below from the help file that explains how to adjust the delays and duration. The delay is the time PowerChute will wait before running the command or starting the shutdown. The duration is the amount of time that it will take to execute. Example if you set a delay of 2 minutes and a duration of 3 minute to run a command file PowerChute will wait 2 minutes after an event and then run the command file. IT will then wait 3 minutes before starting the OS shutdown. 

Shutdown Sequence

When a shutdown commences, the following occurs:

  • After its configured delay time, any specified command file is executed.
    After their individually configured delay times, any selected applications are shut down.
  • After its configured delay time, the OS begins to shut down.
  • After the time for shutting down the OS expires, the UPS continues its countdown before turning itself off.

Configure Shutdown Sequence

Configure Shutdown Sequence

Clicking on the Configure Shutdown Sequence underlined text in the Shutdown Sequence dialog box starts a wizard. The wizard enables you to specify command files and set times for their execution and to specify any installed applications to shut down.

You can also set OS shutdown delay and duration times.

At the first dialog box, you can select from among those applications installed on your system.

In the next dialog box, you can select one command file to be run prior to a shutdown. 

If you have selected the Siebel application, the following two dialog boxes ask for a logon user name and password and also the path to the Enterprise and Gateway servers.

The next dialog box in the wizard enables you to set the time delays and durations to be used during a shutdown.

How to Set the Delay and Duration Times

You can configure delay and duration times for individual command files, and application or OS shutdowns. Each horizontal line in the graph is labeled on the left, for example, Command File, Siebel, SQL, OS.

Note: The scale of this diagram varies according to the runtime of your UPS. For example, if runtim...



Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

0 Likes
0
1585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

On 11/19/2015 9:10 AM, Bill said:

Hi,

PowerChute is written to run the command file prior to the OS shutdown. I pulled the information below from the help file that explains how to adjust the delays and duration. The delay is the time PowerChute will wait before running the command or starting the shutdown. The duration is the amount of time that it will take to execute. Example if you set a delay of 2 minutes and a duration of 3 minute to run a command file PowerChute will wait 2 minutes after an event and then run the command file. IT will then wait 3 minutes before starting the OS shutdown. 

Shutdown Sequence

When a shutdown commences, the following occurs:

  • After its configured delay time, any specified command file is executed.
    After their individually configured delay times, any selected applications are shut down.
  • After its configured delay time, the OS begins to shut down.
  • After the time for shutting down the OS expires, the UPS continues its countdown before turning itself off.

Configure Shutdown Sequence

Configure Shutdown Sequence

Clicking on the Configure Shutdown Sequence underlined text in the Shutdown Sequence dialog box starts a wizard. The wizard enables you to specify command files and set times for their execution and to specify any installed applications to shut down.

You can also set OS shutdown delay and duration times.

At the first dialog box, you can select from among those applications installed on your system.

In the next dialog box, you can select one command file to be run prior to a shutdown. 

If you have selected the Siebel application, the following two dialog boxes ask for a logon user name and password and also the path to the Enterprise and Gateway servers.

The next dialog box in the wizard enables you to set the time delays and durations to be used during a shutdown.

How to Set the Delay and Duration Times

You can configure delay and duration times for individual command files, and application or OS shutdowns. Each horizontal line in the graph is labeled on the left, for example, Command File, Siebel, SQL, OS.

Note: The scale of this diagram varies according to the runtime of your UPS. For example, if runtim...



Hi Bill

Thank you for all of the support you give to us here at apc forums

In the post above you indicated that "Note: The scale of this diagram varies according to the runtime of your UPS. For example, if runtime is low you can’t set long delay or duration times."

In my environment i can not set the delay value from the console for running the command file past 52 min even though i have 116 min

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

0 Likes
0
1585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

Hi,

The maximum allowable number is 60 minutes. The default OS duration is 3 minutes so the delay can be 57 minutes. The maximum allowable number for command files is 57 (56 for delay 1 minute duration) when the OS delay is set for 57 minutes and the OS duration is 3 minutes. If you push to the limits OS delay can be set for 60 minutes with a 20 second duration and command file delay can be set for 59 minutes with a 1 minute duration. However the OS delay will get set to zero and the duration will be set to 20 seconds.

If you want to keep the OS delay at 47 minutes then the command file delay and duration must not be greater that 47 minutes. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

0 Likes
0
1585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

Hi Bill

Thanks for replying

So why is there a 60 min maximum time limit? I think it is a flaw because if you have 112 min of run time then you should be able to schedule the shutdown just before the runtime limit is reached. So in my case the ups will be just under 50% drained when the shutdown sequence is initiated.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

0 Likes
0
1586
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

Hi,

Changes were made to versions that work with Microlink Smart-UPS i.e. SMT, SMX, SRT, SMC that allows for a greater number.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of