Management software for MULTIPLE UPS'

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Management software for MULTIPLE UPS'
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 01:52 AM . Last Modified: ‎2024-02-29 10:27 PM

0 Likes
6
5358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:52 AM . Last Modified: ‎2024-02-29 10:27 PM

Management software for MULTIPLE UPS'

Hi,

- We are going to use six or seven "SURT6000XLIM" UPS' in the ship. Is there a software that can monitor and manage all of these UPS' from single location? As far as I know PowerChute is connected directly to the UPS and manages that single UPS.

- For smart-UPS familiy, is there any option to have SNMP and serial interface at the same time?

Thanks in advance for helping.

Barış

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • multiple
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:27 PM

0 Likes
0
5358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:27 PM

PowerChute Business Edition users using PowerChute Business Edition console which includes a GUI that monitors the PowerChute Business Edition Agents connected to each UPS. Thus, the console shows all of the agents. I believe SURT6000XLIM UPS though ships with a UPS Network Management Card but if I look at the picture on the website, I don't see it there. The question is are you adding a UPS Network Management Card to the UPS SmartSlot? Users would use that to manage the UPS in conjunction with PowerChute Network Shutdown or if you have no management card, you use PowerChute Business Edition via serial connection. If you are using the serial connection, you'd want to check into PowerChute Business Edition and using the Agent, Server, and Console components if you have multiple UPSs on the same network you'd like to see with one GUI -> http://www.apc.com/products/family/index.cfm?id=125. 

The tool we offer for managing multiple UPS Network Management Cards is StruxureWare Data Center Expert -> http://www.apc.com/products/family/index.cfm?id=350 It uses SNMP to manage and monitor the devices and can do APC devices (which it is catered to) but also has support for third party devices. The VM Trial version allows you to monitor (5) devices for free I think. You can get it in VM form or as a hardware appliance if you wish. Other options you may have would be to just look into a generic SNMP monitoring tool depending on what capabilities you want. StruxureWare can do mass firmware upgrades, configurations, alarms, etc but if you just want basic monitoring or alarms, it may be overkill for you.

Regarding your second question, the UPS has a serial port for use with PowerChute. UPS Network Management Cards also have a serial port and SNMP interface on them if you're using that. If using a UPS Network Management Card, you wouldn't use the serial interface on the UPS itself. With AP9630/31 UPS Network Management Card, yes you can use both SNMP and serial connection at the same time.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:27 PM

0 Likes
0
5359
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:27 PM

PowerChute Business Edition users using PowerChute Business Edition console which includes a GUI that monitors the PowerChute Business Edition Agents connected to each UPS. Thus, the console shows all of the agents. I believe SURT6000XLIM UPS though ships with a UPS Network Management Card but if I look at the picture on the website, I don't see it there. The question is are you adding a UPS Network Management Card to the UPS SmartSlot? Users would use that to manage the UPS in conjunction with PowerChute Network Shutdown or if you have no management card, you use PowerChute Business Edition via serial connection. If you are using the serial connection, you'd want to check into PowerChute Business Edition and using the Agent, Server, and Console components if you have multiple UPSs on the same network you'd like to see with one GUI -> http://www.apc.com/products/family/index.cfm?id=125. 

The tool we offer for managing multiple UPS Network Management Cards is StruxureWare Data Center Expert -> http://www.apc.com/products/family/index.cfm?id=350 It uses SNMP to manage and monitor the devices and can do APC devices (which it is catered to) but also has support for third party devices. The VM Trial version allows you to monitor (5) devices for free I think. You can get it in VM form or as a hardware appliance if you wish. Other options you may have would be to just look into a generic SNMP monitoring tool depending on what capabilities you want. StruxureWare can do mass firmware upgrades, configurations, alarms, etc but if you just want basic monitoring or alarms, it may be overkill for you.

Regarding your second question, the UPS has a serial port for use with PowerChute. UPS Network Management Cards also have a serial port and SNMP interface on them if you're using that. If using a UPS Network Management Card, you wouldn't use the serial interface on the UPS itself. With AP9630/31 UPS Network Management Card, yes you can use both SNMP and serial connection at the same time.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

0 Likes
0
5358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

Hi Angela,

Thank you very much for your detailed answer, it was really useful. We can buy whatever we have to buy in order to meet the requirements. So we can buy AP9630/9631.

We are using serial interface for turning-on the UPS by short cutting related pins of the serial DB-9 interface ( dry-contact). It seems we can do it on SURT6000XLIM too.

According to documentation Default ports for SURT6000XLIM : DB-9 RS-232, RJ-45 10/100 Base-T, Smart-Slot (http://www.apc.com/shop/tr/tr/products/APC-Smart-UPS-RT-6000VA-230V-Marine/P-SURT6000XLIM)

Do you know if we can use the default 10/100 Base-T interface for management software ? If we can, we don't have to buy AP9630/31. But i dont know if powerchute works via ethernet. Perhaps it works only with serial connection? And the other The centralized managemet solution (StruxureWare Data Center Expert) works only if we install AP9630/31?

Regards

Barış

  • Tags:
  • ::
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

0 Likes
0
5358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

Hi Angela, i have another question since i found the expert;

 SURT6000XLIM MARINE UPS 

In the marine applications, input supply of the UPS is Line1 and Line2. Where measured  vrms 

between Line1 and Line2 is 220 VAC,

between Line1 and safety ground is 110 VAC and

measured value between Line2 and safety ground is 110 VAC.

Can we assume the same values for the output of the SURT6000XLIM MARINE UPS?

Thanks for helping.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

0 Likes
0
5358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

Hi Baris,

Yes, you can use the DB-9 serial port as a dry contact interface and use the SmartSlot Network Management Card. I see what you mean on the tech specs mentioning 10/100 Base-T. I checked the US/English product page here (http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SURT6000XLIM) and actually it does not list 10/100 Base T! I asked the product manager to look into the problem and in the meantime I decided to check the Build of Materials (BOM) on this UPS to see if a Network Management Card is included because I did not think it was meaning 10/100 shouldn't be listed there as the UPS itself only has a DB-9 serial port. 10/100base T is only available with the Network Management Card.

Long story short, I don't see that an AP9630/31 is included with this UPS. PowerChute Business Edition can only be used on USB (this UPS doesn't offer USB) or serial connections.

If you buy an AP9630/31 and need graceful shutdown, you install the management card in the UPS and use the PowerChute Network Shutdown on your servers/clients.

Yes, StruxureWare Data Center Expert only will monitor the management cards. There is a way to get it to "look" at PowerChute Business Edition agents but the support is so very limited I wouldn't even recommend it. I believe it only works on Windows and relies on Windows SNMP service or something like that. I think you'd be severely disappointed with the basic support, especially if you're buying StruxureWare just to manage them. You're better off using PowerChute Business Edition Console.

On your second question, here is what I know on input/output voltages and other features of the UPS -> http://www.apcmedia.com/salestools/PAYS-8ACJ4C/PAYS-8ACJ4C_R3_EN.pdf . Hope it helps. I don't have one of these to double check and measure any output voltages. I believe this UPS just cases what the L-L voltage is and it has different settings as noted in the specifications - 220, 230, 240 - and the legs will add up to that somehow.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

0 Likes
0
5358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

hi Angela,

Thanks a lot for detailed and clear explanations, that helped us quite a lot. Now we can work on the issue as you lead. if you don't mind I will keep asking you some more boring questions until we select the right HW and SW for our project 🙂

Baris

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

0 Likes
0
5358
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:53 AM . Last Modified: ‎2024-02-29 10:26 PM

OK tongue-out

Note here in the USA is the Thanksgiving Day holiday is next Thursday (and we get the day after off too). 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore