PowerChute Business Edition reporting multiple power failures

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute Business Edition reporting multiple power failures
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:26 AM . Last Modified: ‎2024-03-07 11:04 PM

0 Likes
5
1094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:26 AM . Last Modified: ‎2024-03-07 11:04 PM

PowerChute Business Edition reporting multiple power failures

We have 3 Smart-UPS 750 RMs installed in our rack. We currently have 3 of our 5 servers connected via USB to manage them. I have configured them to be managed by our main server. I have also configured it to email my cell phone when the power fails. he issue that I am having, is that in the last 24 hours, all 3 UPSes have reported power failures. The power has not failed however. When viewing the event log in the management console, it shows power failures. It then reports power being restored no more than 5 seconds later (usually 2 or 3 seconds) My question: is this an issue with the UPSes, the software, or our utility company?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:26 AM . Last Modified: ‎2024-03-07 11:04 PM

0 Likes
0
1094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:26 AM . Last Modified: ‎2024-03-07 11:04 PM

Thank you for clarifying that. I will test that out the next time that I am able to take the servers offline (which might be a week or two since other users might try to lynch me if i take the servers down during the week) I need to rewire the enclosure, so that would likely be the best time to try it. However since changing the sensitivity i haven't received any notices of the power failing.

As far as the point of the UPSes, it is to protect against brown outs, and outright power outages. However I would rather only be notified if the power actually fails, not just if it deviates.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 07:26 AM . Last Modified: ‎2024-03-07 11:04 PM

0 Likes
0
1094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:26 AM . Last Modified: ‎2024-03-07 11:04 PM

There are two things you can try to eliminate the USB port not being completely active, and utility power (mainly, harmonic distortion), being the root cause of this.

1. Lower the UPS Sensitivity to "Low". By default it's set to High.

2. Brain-dead the UPS to ensure that the USB port is fully active and that partial communication is not being shared between the USB and serial ports:

A. Power off the Load/UPS
B. Disconnect the UPS from utility power and remove all communication cables
C. Depress the Off button for approximately 4-6 seconds until you hear a click and the front LED's flash
D. Power everything back up, connecting only the USB cable.
E. Continue to monitor to see if it was a harmonic distortion issue, or a communication issue.

Message was edited by: The Notorious K.M.P.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:26 AM . Last Modified: ‎2024-03-07 11:04 PM

0 Likes
0
1094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:26 AM . Last Modified: ‎2024-03-07 11:04 PM

I have lowered the sensitivity to low, we'll see how that goes. I'm not quite sure what you mean by brain-dead the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:26 AM . Last Modified: ‎2024-03-07 11:04 PM

0 Likes
0
1094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:26 AM . Last Modified: ‎2024-03-07 11:04 PM

I've been present when we've had the slightest drops or brown outs in power. Discern-able as just a flicker in the lights, it has nonetheless caused the UPS to trigger an event, which is what I expect it to do. The machines stay up and undisturbed. This is why we have the UPS's I think, at least in my case it is one of the big reasons, as we rarely have an extended power outage in our building.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 07:26 AM . Last Modified: ‎2024-03-07 11:04 PM

0 Likes
0
1094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:26 AM . Last Modified: ‎2024-03-07 11:04 PM

Cory, please see my edited post. Apparently the boards didn't like the 5 space return I put between the start of the line and the letter indicating an indent. Hope this clarifies.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:26 AM . Last Modified: ‎2024-03-07 11:04 PM

0 Likes
0
1095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:26 AM . Last Modified: ‎2024-03-07 11:04 PM

Thank you for clarifying that. I will test that out the next time that I am able to take the servers offline (which might be a week or two since other users might try to lynch me if i take the servers down during the week) I need to rewire the enclosure, so that would likely be the best time to try it. However since changing the sensitivity i haven't received any notices of the power failing.

As far as the point of the UPSes, it is to protect against brown outs, and outright power outages. However I would rather only be notified if the power actually fails, not just if it deviates.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore