PowerChute Business Edition does not detect USB SmartUPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute Business Edition does not detect USB SmartUPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:28 AM . Last Modified: ‎2024-03-13 05:32 AM

0 Likes
2
4094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:28 AM . Last Modified: ‎2024-03-13 05:32 AM

PowerChute Business Edition does not detect USB SmartUPS

This is a new server running Windows Server 2012R2 Essentials.  The UPS is a SmartUPS-1500 and attached via USB.  In device manager it is displayed under Batteries as HID UPS Battery.  When I attempt to install the PowerChute Agent software it does not detect the UPS and asks which port I am using, DB9 or RJ45.  Neither obviously.

 

Please advise.  Thanks.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:28 AM . Last Modified: ‎2024-03-13 05:32 AM

0 Likes
1
4085
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:28 AM . Last Modified: ‎2024-03-13 05:32 AM

Paul,

The reason the software ask DB9 or RJ45 is because since the software cannot auto-detect the UPS it needs to know what the available serial connection is to determine which version of PBEAgent to install. If DB9 then the version of Agent installed should be 9.0.3. If RJ45 the version will be 9.1.1 (this is assuming you are running the latest version of PCBE installer).

If connected properly the software should auto-detect the UPS and install the proper version of the Agent. It seems that the system is detecting the UPS since it is loading HID UPS Battery. If your Smart-UPS is model SMT, SMX, SMC, or SRT download and run USBTerm.exe tester. The tester can be downloaded from this link 

https://schneider-electric.box.com/s/h2i9n2f2ek27p0wkmyspjsay3gl729et

If the Smart-UPS is detected then USBTerm.exe will return the model and serial number of the UPS. If USBTerm.exe returns the proper information then you should follow the instruction in Kbase FA164514 to manually load the APC UPS driver and then install PowerChute. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:28 AM . Last Modified: ‎2024-03-13 05:32 AM

0 Likes
1
4086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:28 AM . Last Modified: ‎2024-03-13 05:32 AM

Paul,

The reason the software ask DB9 or RJ45 is because since the software cannot auto-detect the UPS it needs to know what the available serial connection is to determine which version of PBEAgent to install. If DB9 then the version of Agent installed should be 9.0.3. If RJ45 the version will be 9.1.1 (this is assuming you are running the latest version of PCBE installer).

If connected properly the software should auto-detect the UPS and install the proper version of the Agent. It seems that the system is detecting the UPS since it is loading HID UPS Battery. If your Smart-UPS is model SMT, SMX, SMC, or SRT download and run USBTerm.exe tester. The tester can be downloaded from this link 

https://schneider-electric.box.com/s/h2i9n2f2ek27p0wkmyspjsay3gl729et

If the Smart-UPS is detected then USBTerm.exe will return the model and serial number of the UPS. If USBTerm.exe returns the proper information then you should follow the instruction in Kbase FA164514 to manually load the APC UPS driver and then install PowerChute. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Jay_jan
Jay_jan
Cadet

Posted: ‎2024-02-01 08:18 PM

In response to BillP
0 Likes
0
2006
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-01 08:18 PM

Hello 
how to stablish communication with UPS in powerchute serial shutdown as i am getting "communication Lost".i am using APC UPS SMT1500 wndows server 19.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore