Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

PowerChute Business Edition 9.0.1.606 - Can it present inaccurate information?

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute Business Edition 9.0.1.606 - Can it present inaccurate information?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5026
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
RTech_apc
Crewman RTech_apc
Crewman

Posted: ‎2021-07-08 12:50 AM

0 Likes
6
370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 12:50 AM

PowerChute Business Edition 9.0.1.606 - Can it present inaccurate information?

This was originally posted on APC forums on 7/1/2015


Hello,

We have PowerChute Business Edition 9.0.1.606 agent installed on Server 2008. On April 2 2015, I replaced a battery on one of our Smart UPS 3000 RM. Last week, the battery indicates that it needs replaced again. This software has been installed prior to my arrival, so I have changed nothing and actually I don't know much about it anyway. Is there anything within the software that could be presenting false information, such as a bad battery; even when it ran fine for 3 months? We did lose power around the time it began reporting that the battery was bad, and our generator kicked on. After that, it stated the battery needed replaced. At this point I am leary of running a calibration as I don't need a major event so close to a holiday.

Lastly, I have another identical unit which just had a new battery installed. I don't see anyway to manage this particulatr unit within the software, so I swapped the newest battery with the original; and it is still stating that it is bad.

Could the batteries actually be bad even though one is bnrand new, and the other is 3 months old?

Very odd situation and timing considering the power outage. It just seems very very weird.

Thoughts?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:50 AM

0 Likes
0
370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 12:50 AM

This reply was originally posted by Bill on APC forums on 7/6/2015


Scott,

There is a chance that running a self-test could cause power to be dropped. It is rare but can happen so if you are concerned you should schedule the test for none production hours.

See Answer In Context

Reply
Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:50 AM

0 Likes
0
370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 12:50 AM

This reply was originally posted by Jordan on APC forums on 7/1/2015


Scott,

What is the exact model of your Smart UPS unit?

Have you gone into the "battery management" section of the PowerChute software and updated the "battery replacement" field?  Is it just the software that indicates a battery replacement is required or the physical interface of the unit as well?  Are you using genuine APC batteries that have not been sitting in storage for more than 4 months?

Reply
RTech_apc
Crewman RTech_apc
Crewman

Posted: ‎2021-07-08 12:50 AM

0 Likes
0
370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 12:50 AM

This was originally posted on APC forums on 7/1/2015


The model is DLA3000RMU2 and the unit also shows the battery is bad, just as the software does. I just thought it was odd that a "new" battery would go bad so soon. When the original new battery was replaced, I did update the information and at first the battery was online and all was as expected for 3 months. Perhaps it is actually bad, but it seems odd the two new batteries would be bad all at once.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:50 AM

0 Likes
0
370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 12:50 AM

This reply was originally posted by Angela on APC forums on 7/1/2015


Can you show us your PowerChute event and data logs just to see? You can also try to run another self test and see what happens and if it clears the alarm. It won't clear on its own and requires a self test to clear it (or to see if it remains). Self test illuminates the replace battery LED and a self test is a comparison of battery voltage drop while on battery with a load. If the battery is new and you don't believe it was stored or older as Jordan suggested, it could've been a fluke.. If it is an APC battery, it should have a serial number on it and they also have a 1 year warranty if it did fail prematurely.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:50 AM

0 Likes
0
370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 12:50 AM

This reply was originally posted by Bill on APC forums on 7/3/2015


Scott,

PowerChute reports what the UPS is telling it. And as you wrote the UPS displays replace battery so I would expect PowerChute to do the same. To test the UPS you should run a self-test. If it passes then the replace battery error will clear. If it fails then the battery needs replacement or needs to be calibrated. You can do a manual run-time calibration. Instruction can be found in this Kbase FA156538. After calibrating run another self-test and if it fail then the battery should be replaced.

Reply
RTech_apc
Crewman RTech_apc
Crewman

Posted: ‎2021-07-08 12:50 AM

0 Likes
0
370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 12:50 AM

This was originally posted on APC forums on 7/3/2015


Thanks for the response. Is there any chance that doing either of those tests in a suspect battery could cause the unit to completely fail? I prefer not to risk a total failure as I have no spare batteries.

Thank you again.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:50 AM

0 Likes
0
371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-08 12:50 AM

This reply was originally posted by Bill on APC forums on 7/6/2015


Scott,

There is a chance that running a self-test could cause power to be dropped. It is rare but can happen so if you are concerned you should schedule the test for none production hours.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc