PowerChute 4.3.0 + VMware vCenter and ESXi host shutdown flow

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute 4.3.0 + VMware vCenter and ESXi host shutdown flow
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:25 PM . Last Modified: ‎2024-02-14 11:55 PM

0 Likes
2
998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:25 PM . Last Modified: ‎2024-02-14 11:55 PM

PowerChute 4.3.0 + VMware vCenter and ESXi host shutdown flow

Hi team

In PC 4.3 I like to have PC to shutdown the VM's and afterwards vCenter and then the both ESXi hosts. But it went a bit strange:

  1. simulate the shutdown seq by removing the NMC communications
  2. almost directly the VM's are shutdown, except from vCenter and PCNS.
  3. Took a while then ESX2 got a shutdown, PCNS was running on that host
  4. PCNS got booted at ESX1, and start vCenter
  5. PCNS scans for triggers and sees that the comm with NMC still is disconnected
  6. vCenter shutdown
  7. PCNS and ESX1 will never shutdown.

How can i overcome the last steps to shutdown everything?

 

06/12/2019 18:53:24 PowerChute cannot communicate with the Network Management Card.
06/12/2019 18:53:24 UPS critical event: PowerChute cannot communicate with the NMC.
06/12/2019 18:53:24 Shutdown sequence started on Hosts esx2.domain.x, esx1.domain.x in response to UPS critical event: PowerChute cannot communicate with the NMC.
06/12/2019 18:53:25 Shutting down VMs on Host esx1.domain.x.
06/12/2019 18:53:25 Starting vApp shutdown process.
06/12/2019 18:53:25 No vApp to shutdown on Host esx1.domain.x.
06/12/2019 18:53:27 Shutting down VMs on Host esx2.domain.x.
06/12/2019 18:53:42 Cannot connect to https://192.168.1.16:443
06/12/2019 18:55:37 Shutting down vCenter Server VM vCenter.
06/12/2019 18:57:46 Cannot connect to vCenter Server. PowerChute may not be able to issue commands to Virtual Machines or Hosts.

06/12/2019 19:01:15 PowerChute is attempting to open UDP port 3052.
06/12/2019 19:01:15 PowerChute successfully opened UDP port 3052.
06/12/2019 19:01:18 Cannot connect to https://192.168.1.16:443
06/12/2019 19:01:19 PowerChute Network Shutdown version 4.3.0 monitoring started.
06/12/2019 19:01:19 PowerChute is attempting to open TCP port 6547.
06/12/2019 19:01:19 PowerChute is attempting to open TCP port 3052.
06/12/2019 19:01:19 PowerChute successfully opened TCP port 3052.
06/12/2019 19:01:19 PowerChute successfully opened TCP port 6547.
06/12/2019 19:02:39 Cannot connect to vCenter Server. PowerChute may not be able to issue commands to Virtual Machines or Hosts.

06/12/2019 19:02:39 Attempting to start vCenter Server VM vCenter.
06/12/2019 19:03:15 PowerChute cannot communicate with the Network Management Card.
06/12/2019 19:03:15 UPS critical event: PowerChute cannot communicate with the NMC.
06/12/2019 19:03:15 Shutdown sequence started on Hosts esx2.domain.x, esx1.domain.x in response to UPS critical event: PowerChute cannot communicate with the NMC.
06/12/2019 19:03:15 PowerChute cannot locate the vCenter Server VM in the Inventory. See the troubleshooting section in the Online Help.
06/12/2019 19:03:18 Cannot connect to https://192.168.1.16:443
06/12/2019 19:03:33 Shutting down VMs on Host esx1.domain.x.
06/12/2019 19:03:33 Cannot connect to vCenter Server. PowerChute will not be able to perform vApp Shutdown.
06/12/2019 19:05:34 vCenter Server is accessible. PowerChute will be able to issue commands to Virtual Machines or Hosts.
06/12/2019 19:05:49 Could not enter maintenance mode on Host esx2.domain.x.
06/12/2019 19:05:52 Shutdown Host failed for Host esx2.domain.x.

 

 

 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:25 PM . Last Modified: ‎2024-02-14 11:55 PM

0 Likes
0
998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:25 PM . Last Modified: ‎2024-02-14 11:55 PM

Hi Bill

I think you're right, there was an issue with a none conclusive DNS record which prevents the host from reaching the AD.

 

tnx Rob

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:25 PM . Last Modified: ‎2024-02-14 11:55 PM

0 Likes
0
998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:25 PM . Last Modified: ‎2024-02-14 11:55 PM

Hi,

The PCNS VM should not be migrated to another host. Do you have HA enabled? If so what are the settings and is migration enabled in PCNS?

On 6/12/2019 2:05 PM, Rob said:

06/12/2019 19:05:49 Could not enter maintenance mode on Host esx2.domain.x.
06/12/2019 19:05:52 Shutdown Host failed for Host esx2.domain.x.

This looks to be a permissions issue. Please see setting up users starting on page 58 of the User's Guide. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:25 PM . Last Modified: ‎2024-02-14 11:55 PM

0 Likes
0
999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:25 PM . Last Modified: ‎2024-02-14 11:55 PM

Hi Bill

I think you're right, there was an issue with a none conclusive DNS record which prevents the host from reaching the AD.

 

tnx Rob

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore