Power chute will not Discover

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Power chute will not Discover
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

0 Likes
10
3235
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

Power chute will not Discover

I have PowerChute Business Deluxe installed on a server. I have UPS devices configured around the network, some on the same segment and some on another. PowerChute will not find anything...I even try to click new and add in manualy and it will not find them, yet I can http:// right to them without problem..

Any ideas?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:12 PM

0 Likes
0
3233
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:12 PM

I agree with voidstar. In your scenario, I would configure email on all of the NMCs, that way you can get email notifications based on events. As far as monitoring all of your devices, ISX MGR can do this, you would need the appliance, as well as a license key, depending on the amount of nodes you will monitor and if you are looking to grow in the near future.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

0 Likes
0
3233
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

What version of Deluxe do you have?
What types of UPS's do you have?

Try adding by hitting "New" and entering in the target IP address. Please note if you get an error doing this or not.

Just something to get you started!

Message was edited by: EZ Button

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

0 Likes
0
3234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

Version 7.0.5 isntalled on Win2003R2 box
UPS's are 1500 and 3000 smart ups
Cards are AP9617

I can http into all of them form the server itself.
I have tried to manual add but get a msg. saying: Failed to add

Reply

Link copied. Please paste this link to share this article on your social media post.

EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

0 Likes
0
3234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

Ok, well that makes this a bit interesting.

I assume what you mean is that you have a network management card in each UPS. If that's the case, then send back the PCBE deluxe software back to where you purchased it because that software requires a direct serial connection to each UPS.

Since you have Management Cards, you should be installing Powerchute Network Shutdown on each computer that you have being powered by each UPS. This is free software that can be downloaded from the site below. This software talks to the Management Cards and perform graceful shutdowns accordingly to your configuration.

http://www.apcc.com/tools/download/index.cfm?isocountrycode=US&tsk=


Now... if you're looking to centrally manage those Network Management Cards, you can use either a local Network Management Station and use SNMP, or you may want to look into an ISX Manager linked below. You'll be able to centrally manage all our UPS's, do mass configurations, mass firmware upgrades, and receive email alerts from one central station instead of having to set that up on each UPS.

http://www.apcc.com/resource/include/techspec_index.cfm?base_sku=AP92200

Hope that clears things up!

Message was edited by: EZ Button

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

0 Likes
0
3234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

ahhh, I was told that I would be able to have this software watch up to 25 networked UPS systems and have them all under one screen.
These are not connected to individual systems, they are in network closets and on multiple servers.

Reply

Link copied. Please paste this link to share this article on your social media post.

EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

0 Likes
0
3234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

Sorry to hear that's what you were told. PCBE does provide you an interface to view multiple agents, but those agents do need a physical, not network, connection to the server. (Hence the serial and USB ports / cables)

If you already have the Management cards, then definitely use Powerchute Network Shutdown. It's much more convenient when you don't have to run cables everywhere.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

0 Likes
0
3234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

I too was told that same thing. I bought 6 management cards and installed in my SU3000RM units and try to monitor with the business edition software. I too was told that it would monitor all 6 of my units thru the network. This came from APC support, and that is where I bought the management cards from.

So what software can I use to monitor my units. I have units in different areas of the building, in power closets, so I can provide backup power in sections of the building. So I can not monitor thru serial cable, unless I did it the old way and walked around with a laptop to check each unit. That is why I spent the money to buy the management cards and ran network cables to each of the power closets.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

0 Likes
0
3234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

Since it's only 6 devices, buying something like the ISX Manager and a 25-node lisence isn't the least invasive way to do this. Create a bookmark folder within IE, and bookmark the IP addresses of all the NMC's installed in the UPS. If you have servers/PC's that need graceful shutdown, install PowerChute Network Shutdown on each of those Clients, and that will provide the shutdown portion of the UPS.

The software is available here:

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SFPCNS223

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

0 Likes
0
3234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:13 PM

The problem with using the web browser is that you only get a snapshot of the status of the unit. You have to constantly refresh the page to see any changes. This is not real time as was told to me by the tech support that sold me the network management cards. I was expecting real time monitoring thru the network using the Business software.

I have done as suggested, to bookmark the ip addresses but it is a pain to load each page and log in constantly and also have to refresh the pages constantly to monitor. Tech support needs to have a better handle on this issue before telling customers that real time monitoring can be done thru the network using the Business software and network management cards.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:12 PM

0 Likes
0
3234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:12 PM

rjstuart, you can set up the NMCs to notify you about any change in status, through administration->notifications. E-mail works pretty well, although I find I prefer the trap receiver approach since the NMC can generate them faster. I hope these notification mechanisms meet your needs.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:12 PM

0 Likes
0
3234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:19 AM . Last Modified: ‎2024-03-07 11:12 PM

I agree with voidstar. In your scenario, I would configure email on all of the NMCs, that way you can get email notifications based on events. As far as monitoring all of your devices, ISX MGR can do this, you would need the appliance, as well as a license key, depending on the amount of nodes you will monitor and if you are looking to grow in the near future.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore