
Posted: 2021-06-28 04:44 AM . Last Modified: 2024-03-18 04:10 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:44 AM . Last Modified: 2024-03-18 04:10 AM
Power On Delay after a power failure
Hello,
In 2 datacenters, i have Switched Rack PDU AP7951.
I want to know if it's possible to set Power On Delay for each outlet after a power failure ?
In the setup, i can set Power On Delay for each outlet, but the Help told it's only after an On Delayed command.
Could you help me?
Thanks
Best regards
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:44 AM . Last Modified: 2024-03-18 04:10 AM
By the way you can also do the same thing for ALL the outlets by changing the Coldstart Delay on the main Device Manager page through the NMC.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:44 AM . Last Modified: 2024-03-18 04:10 AM
The power on delays that you set under "Configuration" on the Switched RPDU's apply whenever the outlets receive a "turn on" command, including after the unit has been shut down after power failure. For instance, I set my "Delay" to wait 17 seconds for outlet 8, unplug my RPDU entirely, plug it back in, and the other outlets turn on as soon as the RPDU reboots, but outlet 8 waited 17 seconds.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:44 AM . Last Modified: 2024-03-18 04:10 AM
By the way you can also do the same thing for ALL the outlets by changing the Coldstart Delay on the main Device Manager page through the NMC.
Link copied. Please paste this link to share this article on your social media post.

