Power Off Delay

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Power Off Delay
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
mmzxz_apc
Crewman mmzxz_apc
Crewman

Posted: ‎2021-06-30 12:21 AM . Last Modified: ‎2024-03-11 04:09 AM

0 Likes
6
7115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:21 AM . Last Modified: ‎2024-03-11 04:09 AM

Power Off Delay

Hi folks,

I have some questions and hope any of you can provide some clarification.

Setup:

  • vCenter on physical machine connected to outlet group 2. Powerchute Network Shutdown also runs on this machine.
  • vSphere/ESXi host with a bunch of VM's connected to outlet group 1.
  • Network Management Card 2 on a SMX3000.
  • Communication with vCenter, PNS and NMC2 configured and working.

Where do I define at what moment the UPS sents a signal to PNS indicating that it should start a shutdown procedure? Do I configure that on the NMC2 in Outlet Group Configuration>Power Off Delay? Suppose I want PNS to start shutting down VM's after 30 secs. of power outage, do I configure that on the NMC2>Outlet Group Configuration>Group 1>Power Off Delay>30seconds ?

Also, I have set VM Prioritization and VM Shutdown Duration in Powerchute Network Shutdown software. The total VM shutdown duration given in PNS is 8minutes. After shutting down VM's, PWS goes shutting down the vSphere/ESXi host.....correct? Next PWS goes shutting down the vCenter server.....correct?

Thanks in advance

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 12:21 AM . Last Modified: ‎2024-03-11 04:09 AM

0 Likes
0
7107
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:21 AM . Last Modified: ‎2024-03-11 04:09 AM

So, by default the UPS will not shut down on power failure. It continues to run on battery until depleted.

You can set up software to command a UPS shutdown during a power failure. Generally this will use delays. One exception is the "Load Shedding" settings where "Skip outlet delays"  is the default, but you can and should unset that. Load shedding is disabled by default.

PowerChute uses the off delay to ensure it has enough time to safely power off the load before the UPS de-energizes the outlets.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:21 AM . Last Modified: ‎2024-03-11 04:09 AM

0 Likes
0
7108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:21 AM . Last Modified: ‎2024-03-11 04:09 AM

Hi,

The shutdown process is explained and diagrammed on page 87 of the users guide http://www.apc.com/salestools/PMAR-9DNLQK/PMAR-9DNLQK_R3_EN.pdf?sdirect=true When the UPS switches to battery depending on the PCNS configuration a delay will happen and then the shut down process starts. When the process starts the shutdown signal is sent to the outlet group. The outlet group will wait the delay specified in the NMC and then power down. 

On 4/7/2018 11:10 AM, First said:

So if I understand this correctly: the total VM shutdown duration I have set in PNS is set to 1260 seconds (which works fine). I also have set Turn off the UPS Outlet Group in PNS. In NMC2 I have set Power Off Delay to 1500 seconds (1260 + 4 minutes). This will result in NMC receiving a Turn off Outlet group signal at the begin/end (??)

The shut down is triggered at the beginning as listed in the diagram.

On 4/7/2018 11:10 AM, First said:

of the PNS shutdown procedure and then NMC waits 1500 seconds to turn off the outlet groups.....correct?

Correct.

On 4/7/2018 11:10 AM, First said:

Can I see pending/scheduled Outlet Group shutdowns initiated by PNS somewhere in NMC?

The shutdown signal is logged in the NMC event log and you can see the remaining time left of the delay under Status - Outlet Groups

On 4/7/2018 11:10 AM, First said:

Also, the Power Off Delay in NMC2 for group 2 seems to reset from 1500 to 3180 (happened multiple times).

That is as designed. When you configured PCNS to power down the outlet group the VM shut down delays are added to the outlet group power off delay. As an example sent VM power off delays to 840 second and the outlet off delay on the NMC had been set to 120 seconds. The outlet off delay will be increased to 920 seconds. If you want 15 minute delay set the VM shut down delays to equal 1260 and set the outlet off delay on the NMC to 240.  

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:21 AM . Last Modified: ‎2024-03-11 04:09 AM

0 Likes
0
7108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:21 AM . Last Modified: ‎2024-03-11 04:09 AM

Hi,

If you want the shutdown to start when the UPS has been on battery for x amount of time you can do that in PCNS. Go to Configure Events - UPS on Battery. Select shutdown, then select Enable shutdown and add the delay. The delay is the amount of time the UPS will run on battery before PCNS start the shut down process. 

On 4/4/2018 8:14 AM, First said:

PWS goes shutting down the vSphere/ESXi host.....correct? Next PWS goes shutting down the vCenter server.....correct?

Correct. After the VMs and the host have been powered down the PCNS service and vCenter service will be stopped and the system PCNS and vCenter are running on will power off. 

Reply

Link copied. Please paste this link to share this article on your social media post.

mmzxz_apc
Crewman mmzxz_apc
Crewman

Posted: ‎2021-06-30 12:21 AM . Last Modified: ‎2024-03-11 04:09 AM

0 Likes
0
7108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:21 AM . Last Modified: ‎2024-03-11 04:09 AM

Thanks for your reply, this mostly answers my question. Though I would like to know a bit more on NMC2>Outlet Groups Configuration>Power Off Delay

I have read this about Power Off Delay:

"When this outlet group is on, it waits this delay before turning off when "Off with Delay," "Reboot with Delay," or "Shutdown with Delay, AC Restart" is selected as the action for this outlet group. (During a delayed reboot, the outlet group then waits the number of seconds configured as Reboot Duration and Power On Delay before it turns on.)"

Does this mean this setting only works in conjunction with Control > Outlet Groups > *action* ? Does this also mean that whenever I have a power failure, this setting does not relate to anything that happens because of the power failure? For example, suppose I have a power failure and Power Off Delay is set to 120 secs, the UPS doesn't Power Off after 120 secs because the Power Off Delay setting is only applicable to manual actions in Control > Outlet Groups > *action*  ..........correct?

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 12:21 AM . Last Modified: ‎2024-03-11 04:09 AM

0 Likes
0
7108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:21 AM . Last Modified: ‎2024-03-11 04:09 AM

So, by default the UPS will not shut down on power failure. It continues to run on battery until depleted.

You can set up software to command a UPS shutdown during a power failure. Generally this will use delays. One exception is the "Load Shedding" settings where "Skip outlet delays"  is the default, but you can and should unset that. Load shedding is disabled by default.

PowerChute uses the off delay to ensure it has enough time to safely power off the load before the UPS de-energizes the outlets.

Reply

Link copied. Please paste this link to share this article on your social media post.

mmzxz_apc
Crewman mmzxz_apc
Crewman

Posted: ‎2021-06-30 12:21 AM . Last Modified: ‎2024-03-11 04:09 AM

0 Likes
0
7108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:21 AM . Last Modified: ‎2024-03-11 04:09 AM

So if I understand this correctly: the total VM shutdown duration I have set in PNS is set to 1260 seconds (which works fine). I also have set Turn off the UPS Outlet Group in PNS. In NMC2 I have set Power Off Delay to 1500 seconds (1260 + 4 minutes). This will result in NMC receiving a Turn off Outlet group signal at the begin/end (??) of the PNS shutdown procedure and then NMC waits 1500 seconds to turn off the outlet groups.....correct?

This doesn't seem to work in my setup. The outlet groups won't switch off while I have set the Power Off Delay and unchecked Skip outlet off delay. Can I see pending/scheduled Outlet Group shutdowns initiated by PNS somewhere in NMC?

edit:
Also, the Power Off Delay in NMC2 for group 2 seems to reset from 1500 to 3180 (happenend multiple times). I would find this logical when the VM shutdown time set in PNS would exceed the Power Off Delay, but this doesn't seem to be the case:

(PNS)
EcbuST6qRuDJoeWvRzLbJA%3D%3D.pngEcbuST6qRuDJoeWvRzLbJA%3D%3D.png

NMC2

CrDNUhtiKAkTUucBpVpQSA%3D%3D.pngCrDNUhtiKAkTUucBpVpQSA%3D%3D.png

PNS

ku7t7WmuKgydJsmy8t6sJg%3D%3D.pngku7t7WmuKgydJsmy8t6sJg%3D%3D.png

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:21 AM . Last Modified: ‎2024-03-11 04:09 AM

0 Likes
0
7109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:21 AM . Last Modified: ‎2024-03-11 04:09 AM

Hi,

The shutdown process is explained and diagrammed on page 87 of the users guide http://www.apc.com/salestools/PMAR-9DNLQK/PMAR-9DNLQK_R3_EN.pdf?sdirect=true When the UPS switches to battery depending on the PCNS configuration a delay will happen and then the shut down process starts. When the process starts the shutdown signal is sent to the outlet group. The outlet group will wait the delay specified in the NMC and then power down. 

On 4/7/2018 11:10 AM, First said:

So if I understand this correctly: the total VM shutdown duration I have set in PNS is set to 1260 seconds (which works fine). I also have set Turn off the UPS Outlet Group in PNS. In NMC2 I have set Power Off Delay to 1500 seconds (1260 + 4 minutes). This will result in NMC receiving a Turn off Outlet group signal at the begin/end (??)

The shut down is triggered at the beginning as listed in the diagram.

On 4/7/2018 11:10 AM, First said:

of the PNS shutdown procedure and then NMC waits 1500 seconds to turn off the outlet groups.....correct?

Correct.

On 4/7/2018 11:10 AM, First said:

Can I see pending/scheduled Outlet Group shutdowns initiated by PNS somewhere in NMC?

The shutdown signal is logged in the NMC event log and you can see the remaining time left of the delay under Status - Outlet Groups

On 4/7/2018 11:10 AM, First said:

Also, the Power Off Delay in NMC2 for group 2 seems to reset from 1500 to 3180 (happened multiple times).

That is as designed. When you configured PCNS to power down the outlet group the VM shut down delays are added to the outlet group power off delay. As an example sent VM power off delays to 840 second and the outlet off delay on the NMC had been set to 120 seconds. The outlet off delay will be increased to 920 seconds. If you want 15 minute delay set the VM shut down delays to equal 1260 and set the outlet off delay on the NMC to 240.  

Reply

Link copied. Please paste this link to share this article on your social media post.

mmzxz_apc
Crewman mmzxz_apc
Crewman

Posted: ‎2021-06-30 12:21 AM . Last Modified: ‎2024-03-11 04:09 AM

0 Likes
0
7108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:21 AM . Last Modified: ‎2024-03-11 04:09 AM

Thank you very much for your reply. This greatly clarifies things!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of