Power Factor - Confuse

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Power Factor - Confuse
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 04:59 AM . Last Modified: β€Ž2024-03-13 01:07 AM

0 Likes
10
1920
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 04:59 AM . Last Modified: β€Ž2024-03-13 01:07 AM

Power Factor - Confuse

Hi,
I am having a project that need UPS has power factor higher 0.95.
I read documents and know that have two types of power factor. Input power factor and output power factor.
So, what is difference between them?
What have I consider when choose an UPS?
Thank you so much.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 05:00 AM . Last Modified: β€Ž2024-03-13 01:06 AM

0 Likes
0
1921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:00 AM . Last Modified: β€Ž2024-03-13 01:06 AM

you're very welcome.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 04:59 AM . Last Modified: β€Ž2024-03-13 01:07 AM

0 Likes
0
1921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 04:59 AM . Last Modified: β€Ž2024-03-13 01:07 AM

Thank you so much Mr. i picKed a winna but the document you gived does not have any infomation about input power factor and output power factor.
Can you give me more exactly explaination?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 04:59 AM . Last Modified: β€Ž2024-03-13 01:07 AM

0 Likes
0
1921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 04:59 AM . Last Modified: β€Ž2024-03-13 01:07 AM

Hi Ms. I picKed a winna,
Thank you so much for your help.
In Vietnam, maybe do not have the UPS with prefix is RMX.
So, Hope you will do a favor for me in the next time I post a question.
Best Regards,E

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 04:59 AM . Last Modified: β€Ž2024-03-13 01:07 AM

0 Likes
0
1921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 04:59 AM . Last Modified: β€Ž2024-03-13 01:07 AM

Can anyone help me?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 05:00 AM . Last Modified: β€Ž2024-03-13 01:07 AM

0 Likes
0
1921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:00 AM . Last Modified: β€Ž2024-03-13 01:07 AM

see if this helps at all -> http://www.apcmedia.com/salestools/SADE-5TNQYL_R1_EN.pdf

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 05:00 AM . Last Modified: β€Ž2024-03-13 01:07 AM

0 Likes
0
1921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:00 AM . Last Modified: β€Ž2024-03-13 01:07 AM

that is ms. i picKed a winna πŸ˜‰

i did some research here with a UPS expert.

output power factor is the difference between watts and VA. for example, our Symmetra LX UPS can do 16000 VA but only 12800 watts. you'd size your load based on the watt rating usually. VA is the apparent power and watts are the real power. input power factor is the power factor of the Power Factor Correction (PFC) stage of an online UPS. line interactive models do not have an input power factor because it just passes power straight through to the load based on the design. so the input power factor would just be the load's power factor. output factor of the UPS is what is the most important for sizing a load.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 05:00 AM . Last Modified: β€Ž2024-03-13 01:07 AM

0 Likes
0
1921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:00 AM . Last Modified: β€Ž2024-03-13 01:07 AM

Thanh you so much Ms. i picKed a winna :). Please forgive me 'cause I am a newbie.
I understand more clearly now. All I need seem have to know what is Power Factor Correction.
So, another question please: do you know what is type of UPS has power factor higher than 0.95?
I have seached many times on Internet but can not get an expect result?
Thank you so much again.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 05:00 AM . Last Modified: β€Ž2024-03-13 01:07 AM

0 Likes
0
1921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:00 AM . Last Modified: β€Ž2024-03-13 01:07 AM

no problem πŸ™‚

we don't have many UPSs with an output power factor of 0.95 or higher. Some of our three phase UPSs do have a unity factor.

can you clarify if you are looking for a single phase or three phase power application? then i can check further.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 05:00 AM . Last Modified: β€Ž2024-03-13 01:06 AM

0 Likes
0
1921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:00 AM . Last Modified: β€Ž2024-03-13 01:06 AM

Sorry you, Ms. i picKed a winna. I live in Vietnam so our time is difference with you.
I am looking for ups 3KVA and 5 KVA with 1 phase input and output. And 15KVA with 3 phase input and 3/1 phase output (or only 3 phase output).
All UPS must can be mounted on rack cabinet.

Thank you so much. Hope to receive your help soon.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 05:00 AM . Last Modified: β€Ž2024-03-13 01:06 AM

0 Likes
0
1921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:00 AM . Last Modified: β€Ž2024-03-13 01:06 AM

i understand. no problem πŸ™‚

i had to ask around a bit. majority of our Smart UPS lines range between 0.7 to a 0.8 power factor. any UPS that we have with the prefix SMX (which I am not sure those are available in Vietnam) are 0.95. Any SURT is generally 0.7 as well.

We also have Symmetra LX with a power factor of around 0.8 but I am told it depends if you input 3 phase or single phase to it where it can then differ depending on the setting.

what i suggest you might try to see what you get, is try our UPS selector. http://www.apc.com/tools/ups_selector/index.cfm

input your data into there and let me know what it returns. when i know what it suggests for you and in what configuration/SKUs, i can then verify if the power factor would meet your requirements.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 05:00 AM . Last Modified: β€Ž2024-03-13 01:06 AM

0 Likes
0
1922
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:00 AM . Last Modified: β€Ž2024-03-13 01:06 AM

you're very welcome.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore