Please help!! (APC Support MIA) New SMX3000HV sudden reboots killing workloads!!

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Please help!! (APC Support MIA) New SMX3000HV sudden reboots killing workloads!!
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
ElCoyote271
Crewman ElCoyote271
Crewman

Posted: ‎2024-08-30 11:50 AM

0 Likes
2
763
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-30 11:50 AM

Please help!! (APC Support MIA) New SMX3000HV sudden reboots killing workloads!!

Hi,

 

On Aug 26th my brand new (two months old) SMX3000HV experienced a sudden reset, turning off and on all outlets and killing my workloads.

A few hours later, another reset cycle was experienced killing again my workloads.

There was no utility power, the weather was good and pleasant yet the UPS which is supposed to protect against power failures killed my workloads -twice- in the same day and for no reason.

 

I have been submitting support tickets to APC (France). One of my support tickets is over one week old and nobody has even reached out to contact me.

 

Please help, if anybody from APC is reading this forum, the tickets are:

https://www.se.com/myschneider/contact/cases/detail?id=111165591
https://www.se.com/myschneider/contact/cases/detail?id=111417757

 

Please help, this is a brand new unit and it's supposed to -protect- my workloads, not restart them!

Vincent

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
ElCoyote271
Crewman ElCoyote271
Crewman

Posted: ‎2024-09-05 12:41 AM

In response to Teken
0 Likes
0
678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-05 12:41 AM

Hi Teken,

 

APC Support finally reached out and the UPS will be getting replaced.

On Aug 19th was the first unexpected restart. It was captured by the AP9640 card.

The logs show:

 08/19/2024 05:24:48 Device UPS: The output power is now turned on.
 08/19/2024 05:24:48 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on.
 08/19/2024 05:24:48 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on.
 08/19/2024 05:24:48 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on.
 08/19/2024 05:23:51 Device UPS: The output power is turned off.
 08/19/2024 05:23:51 Device UPS: The graceful shutdown period has ended.
 08/19/2024 05:23:47 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off.
 08/19/2024 05:23:47 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off.
 08/19/2024 05:23:47 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.
 08/19/2024 05:22:18 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to reboot with off delay.
 08/19/2024 05:22:18 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to reboot with off delay.
 08/19/2024 05:22:18 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to reboot with off delay.

 

This is a bit strange has:
- this was a brand new UPS.

- I had not scheduled -anything- on the UPS. APC Support was unable to find the culprit.

 

Following this incident, I pulled the AP9640 card out and the subsequent events of Augh 26th were not captured. The event logs did not have anything when we looked at them with APC Support.
On Aug 27th, since the UPS had experienced two unexpected outages in the same day, I took the decision to re-insert the AP9640 card and I now have logs again.

The unexpected reboots have not come back (yet) but APC support is proactively replacing the UPS

Vincent

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Teken
Kirk Teken
Kirk

Posted: ‎2024-09-02 06:32 AM

0 Likes
1
747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-02 06:32 AM

What do the event and data logs show for this unit?!? Please upload both for review along with the serial number.

Reply

Link copied. Please paste this link to share this article on your social media post.

ElCoyote271
Crewman ElCoyote271
Crewman

Posted: ‎2024-09-05 12:41 AM

In response to Teken
0 Likes
0
679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-05 12:41 AM

Hi Teken,

 

APC Support finally reached out and the UPS will be getting replaced.

On Aug 19th was the first unexpected restart. It was captured by the AP9640 card.

The logs show:

 08/19/2024 05:24:48 Device UPS: The output power is now turned on.
 08/19/2024 05:24:48 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on.
 08/19/2024 05:24:48 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on.
 08/19/2024 05:24:48 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on.
 08/19/2024 05:23:51 Device UPS: The output power is turned off.
 08/19/2024 05:23:51 Device UPS: The graceful shutdown period has ended.
 08/19/2024 05:23:47 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off.
 08/19/2024 05:23:47 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off.
 08/19/2024 05:23:47 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.
 08/19/2024 05:22:18 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to reboot with off delay.
 08/19/2024 05:22:18 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to reboot with off delay.
 08/19/2024 05:22:18 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to reboot with off delay.

 

This is a bit strange has:
- this was a brand new UPS.

- I had not scheduled -anything- on the UPS. APC Support was unable to find the culprit.

 

Following this incident, I pulled the AP9640 card out and the subsequent events of Augh 26th were not captured. The event logs did not have anything when we looked at them with APC Support.
On Aug 27th, since the UPS had experienced two unexpected outages in the same day, I took the decision to re-insert the AP9640 card and I now have logs again.

The unexpected reboots have not come back (yet) but APC support is proactively replacing the UPS

Vincent

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore