Please Help APC 1500

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Please Help APC 1500
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 10:24 PM . Last Modified: ‎2024-03-04 10:45 PM

0 Likes
4
1553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:24 PM . Last Modified: ‎2024-03-04 10:45 PM

Please Help APC 1500

Hello,

I'm Bryan and new here. I have a problem that maybe some one could help me with. I have 5 UPS back ups that run my DVRS Infrared and other stuff..  I had a spare APC 1500 and thought I would put it to use.  I put new batteries into it and plugged 1 DVR (4 channel Zmodo) 1 Power supply for 1 camera and a VGA to HDMI converter.. Nothing the APC can't handle. Well about 6-9 hours after I hooked it up, I noticed the AVR Trim lights was on.. I never seen this light on for longer than a few secs on my other APC's so I googled it. I found the owners manual and according to them, it means that the UPS is seeing higher than normal voltages. Not 10 minutes after the 1 started to do this, but the other 2 now have it on as well. I seriously doubt that I have 3 defective units. I powered on and off all 3 with out no luck. I even called the power company to see if they are experiencing any electrical problems in my area. They are not. I decided to pull out the volt meter and check outlets. I am getting about 127v AC from all of them.

I do not understand why the AVR Trim lights are on, and its got me scared of an electrical fire..  The 1 that I hooked up today is on a seperate wall circuit than the other 5. (2 APC 3 TrippLites) And I decided to unplug and power down the one I hooked up today.

Any and all help would be greatly appreciated.

Bryan

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-07-07 10:24 PM . Last Modified: ‎2024-03-04 10:44 PM

0 Likes
0
1552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:24 PM . Last Modified: ‎2024-03-04 10:44 PM

As Terry pointed out earlier, a problem with the neutral circuit in the house or to the street can cause a low voltage problem on one "leg" of the 240 volt supply while the other leg sees a high voltage. I suggest you measure some other recepticals in the house to see if any read a low voltage at the same time the receptical for the UPS reads a high voltage. For example, if you read 127 volts at the receptical for the UPS, and 113 at any other receptical in the house you likely have a problem that you should consult with an electrician about. On the other hand, if other recepticals all read close to 126 volts (+/- 1 volt?) it would suggest the local utility is just running on the high side of the normal range. The sum of both legs should equal 240 volts +/- 5% (up to 252 volts (or 126 volts on both legs) is considered "normal" utility voltage in the US).

Another question: is the 127 volt reading continuous, or does it change to a more "normal" value at other times? If it changes, this could suggest some high power load is turning on and off and potentially overloading the old wiring.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 10:24 PM . Last Modified: ‎2024-03-04 10:45 PM

0 Likes
0
1553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:24 PM . Last Modified: ‎2024-03-04 10:45 PM

In this topic, Angela says that on at least one model of UPS, the AVR trim comes on at 126.5V, but that other UPS models may do it at a different voltage. 127V is a little outside of the +/- 5% that I would expect to see in the continental UPS, but not enough that I would worry about it, except in one condition. If you ever notice some of your lights getting brighter when something that pulls a lot of power (like a microwave, air conditioner, etc) turns on, you could have a dangerous situation known as a "loose neutral" and you should call your utility company. It is acceptable for lights to dim slightly when something that pulls a lot of power turns on, and for them to get a little brighter when the device turns off. It's the opposite that you need to worry about. However, this is almost certainly not what you are experiencing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 10:24 PM . Last Modified: ‎2024-03-04 10:44 PM

0 Likes
0
1552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:24 PM . Last Modified: ‎2024-03-04 10:44 PM

Hi Terry,

ok, so I don't have a whole lot to worry about. I still wouldlike to call my electrician to check things out and get this figured out. Just saying. Funny thing is that the Tripp-Lites don't have a AVR light. They seem to be unaffected by this. My entire network runs and is dependant on these UPS. If they fail, everything fails. Just saying. Any idea of where to look at for a high voltage issue? The building is very old and so is the wiring.

Thanks in advance,

Bryan

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 10:24 PM . Last Modified: ‎2024-03-04 10:44 PM

0 Likes
0
1553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:24 PM . Last Modified: ‎2024-03-04 10:44 PM

Unlike low voltage, which can come from too-thin, overloaded, or badly connected wires, high voltage is almost always due to the electric utility delivering too high a voltage.

Reply

Link copied. Please paste this link to share this article on your social media post.

wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-07-07 10:24 PM . Last Modified: ‎2024-03-04 10:44 PM

0 Likes
0
1553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:24 PM . Last Modified: ‎2024-03-04 10:44 PM

As Terry pointed out earlier, a problem with the neutral circuit in the house or to the street can cause a low voltage problem on one "leg" of the 240 volt supply while the other leg sees a high voltage. I suggest you measure some other recepticals in the house to see if any read a low voltage at the same time the receptical for the UPS reads a high voltage. For example, if you read 127 volts at the receptical for the UPS, and 113 at any other receptical in the house you likely have a problem that you should consult with an electrician about. On the other hand, if other recepticals all read close to 126 volts (+/- 1 volt?) it would suggest the local utility is just running on the high side of the normal range. The sum of both legs should equal 240 volts +/- 5% (up to 252 volts (or 126 volts on both legs) is considered "normal" utility voltage in the US).

Another question: is the 127 volt reading continuous, or does it change to a more "normal" value at other times? If it changes, this could suggest some high power load is turning on and off and potentially overloading the old wiring.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore