Posted: 2021-06-26 05:41 AM . Last Modified: 2024-03-19 12:38 AM
Hi All,
We have 3 units of Galaxy 5000 100KVA in Parrallel redundant set up, "PFC Fault" is giving us lot of trouble as UPS forced to bypass.Could you share some assessment with this PFC Fault experienced?
Many Thanks for the advanced input.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:42 AM . Last Modified: 2024-03-19 12:38 AM
No a PFC fault will most likely require a trained technician.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:42 AM . Last Modified: 2024-03-19 12:38 AM
No a PFC fault will most likely require a trained technician.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:42 AM . Last Modified: 2024-03-19 12:38 AM
hello,
i asked someone who supports this unit and they told me:
Possible reasons for (PFC fault) :
a. Input source out of tolerance
b. Open input power fuse
c. Faulty CSNEN/CSNON module including SCR
d. Faulty DCHEN/DCHON
e. Faulty MIZNUS PCA
f. DC capacitor shorted
beyond that, i'd probably advise that you contact your local support to see which issue you may be seeing specifically and how to address it.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:42 AM . Last Modified: 2024-03-19 12:38 AM
Hi,
Thanks for the info.
btw, can we correct the fault by ourselves? thru configuration?
Thanks,E
Link copied. Please paste this link to share this article on your social media post.