Posted: 2021-06-30 06:49 AM . Last Modified: 2024-03-07 11:53 PM
Hi , I am using AP7921 and experencing the problem like the subject. Can you please tell me what meaning it is? Is this unit faulty?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:49 AM . Last Modified: 2024-03-07 11:53 PM
Hi , I am using AP7921 and experencing the problem like the subject. Can you please tell me what meaning it is? Is this unit faulty?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:49 AM . Last Modified: 2024-03-07 11:53 PM
Thanks for the reply.
Sorry I wrote the wrong part number .
Please see the following info of this unit.
Model Number: AP7951
Serial Number: ZA0703012622
Hardware Revision: B2
Manufacture Date: 01/20/2007
MAC Address: 00 C0 B7 2D CE 6C
Management Uptime: 14 Days 2 Hours 9 Minutes
This issue occured with firmware 2.7.4. After upgrading firmware to v3.3.1, it was gone for 2 days. Now this issue happened again.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:49 AM . Last Modified: 2024-03-07 11:53 PM
Hi Ann,
Please upgrade to the latest fw, v3.5.5.
http://www.apc.com/tools/download/software_comp.cfm?sw_sku=SFRPDU355&id=55&family=70&part_num=AP7951...
Keep an eye on it, let us know if it comes back again. If it does, we'll need to gather the events, data, and config logs.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:49 AM . Last Modified: 2024-03-07 11:53 PM
Hi , I am using AP7921 and experencing the problem like the subject. Can you please tell me what meaning it is? Is this unit faulty?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-11-04 04:14 AM
On the internet are various sources how to repair this.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-11-04 04:14 AM
I had the same problems with some Zero-U Rack PDU's (7951, 7952, 7953).
Since the warranty ended on these units, there is only one thing you can do...
After looking at the problem I found the following:
In most of the units, there is a CPU part (near the ethernet/serial port) which holds a Lithium BR2032 battery. This was still fine after >10 years for me.
The CPU, It's universal. It sends it's data on a BUS network which has the relays for the sockets.
Mostly the CPU and the BUS are fine. The thing that breaks is the internal Power Supply (PSU).
It has a PSU based of 2 parts, which are exactly the same. I saw that the 47μF 400V capacitors were bulky, so I measured the capacity... dead.. I first replaced one (but then the fuse in my house blew and the other one was bulky too). SO finally I replaced the two capacitors by part: Panasonic EEUEE2G470, Ø16x25mm.
Then it worked great and can continue for another 15+ years!
TLDR: Replace the 47μF 400V capacitors by Panasonic part: EEUEE2G470, Ø16x25mm (need soldering). It's a typical repair after 10-15 years in which the capacitors get old.. dry.. get warm.. bulky.. dead...