PCPE issue

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCPE issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:00 AM . Last Modified: ‎2024-03-07 11:41 PM

0 Likes
4
1047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:00 AM . Last Modified: ‎2024-03-07 11:41 PM

PCPE issue

My UPS model is BR500I . I installed PCPE v2.0 on my windows XP.
My question : When the mains power is restored after the PC has shutdown and switched off, but before the UPS has switched off, the UPS does a power cycle on my PC . However the time period between switching the power off and switching it back on is too short so my PC can not detect it. Can I change that time period ?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:00 AM . Last Modified: ‎2024-03-07 11:41 PM

0 Likes
0
1047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:00 AM . Last Modified: ‎2024-03-07 11:41 PM

My UPS model is BR500I . I installed PCPE v2.0 on my windows XP.
My question : When the mains power is restored after the PC has shutdown and switched off, but before the UPS has switched off, the UPS does a power cycle on my PC . However the time period between switching the power off and switching it back on is too short so my PC can not detect it. Can I change that time period ?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: ‎2021-06-30 07:00 AM . Last Modified: ‎2024-03-07 11:41 PM

0 Likes
0
1047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:00 AM . Last Modified: ‎2024-03-07 11:41 PM

Sounds like you're running a test by pulling the plug, letting it shut down your pc, plugging the UPS back in, then manually powering on your computer... (at this point during boot up the UPS reboots and your computer reboots).

The reason for this is the UPS has a turn off delay. Once the shutdown process starts the UPS will wait about 180 seconds and power off. In the event of an extended power outage, you would see the UPS shut down the computer, and then 180 seconds later the UPS would go to sleep mode and not return power until it is restored from the source.

Even in the event of a relatively short power outage which causes a shutdown, the UPS will essentially do the same thing. UPS shuts down computer -> Power returns at the wall (computer is still shut down) -> 180 seconds after shutdown begins, UPS goes into sleep mode (shuts off) -> immediately comes out of sleep mode and the computer reboots because it sees input power again (this last part is a computer bios setting to wake when power is present).

Hope that helps!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:00 AM . Last Modified: ‎2024-03-07 11:41 PM

0 Likes
0
1047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:00 AM . Last Modified: ‎2024-03-07 11:41 PM

Thanks for the reply but I am afraid there was mix up.
As for my question, What I want is this: when the mains power is restored AFTER the PC has shut down and switched off, but BEFORE the UPS has switched off, the UPS does a power cycle on the outlet where I connected my PC. By power cycle I mean that UPS switches the power off to my PC, then shortly afterwards switches the power on. The purpose of this is obviously to allow my PC (probably
only the power supply unit in the PC, as the PC has shut down and
switched off already) to detect that the power was lost, so that it can
start booting when the power is regained. HOWEVER, the time period
between switching the power off and switching it back on (on the outlet
where my PC is connected to UPS) is too short. So, my question to you
is: can I do something to delay the switching the power on to my PC in
this situation, so that it can detect that the power was lost, and thus
start the boot up process?

In other words, if I connect the PC to the mains (without UPS) and shut
it down, then switch off the mains, then switch it back on, the PC
starts booting automatically, which is important since this is a web
server. However, when connected to UPS, in the situation described above
UPS provides the continuous power supply and then only briefly
"simulates" the power loss on the outlet where my PC is connected to
UPS. This discontinuation of power supply to my PC is TOO SHORT for my
PC, which is now in the switched off state, to detect that the power has
been lost and start booting. All I want to achieve is somehow
reconfigure, if possible, my UPS so that this discontinuation in power
supply is a little bit longer than it is currently.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 07:00 AM . Last Modified: ‎2024-03-07 11:41 PM

0 Likes
0
1047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:00 AM . Last Modified: ‎2024-03-07 11:41 PM

Hello,

I am still going to refer to my original answer, as there are other APC UPS customers that are not experiencing this problem with a large variety of power supplies.

The duration of the reboot of the UPS is not a characteristic of the UPS that can be changed. I would recommend checking with your computer manufacturer to see if there is something within the BIOS of the PC that can be adjusted to resolve this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:00 AM . Last Modified: ‎2024-03-07 11:41 PM

0 Likes
0
1048
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:00 AM . Last Modified: ‎2024-03-07 11:41 PM

My UPS model is BR500I . I installed PCPE v2.0 on my windows XP.
My question : When the mains power is restored after the PC has shutdown and switched off, but before the UPS has switched off, the UPS does a power cycle on my PC . However the time period between switching the power off and switching it back on is too short so my PC can not detect it. Can I change that time period ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore