PCPE 2.1.1, hibernation and shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCPE 2.1.1, hibernation and shutdown
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

0 Likes
9
1951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

PCPE 2.1.1, hibernation and shutdown

Hello,

When the UPS switch on the battery, the PC enter into an hibernation mode.
I would prefer that it always shutdown the computer, whatever the UPS battery load is.

How can I configure PCPE to make it always shutdown the PC?

Thanks.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

0 Likes
0
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

I have used the requested command and used the first runtime mode (because it takes less time to test).
And effectively, the PC is now entering a true shutdown mode. Thanks for the solution to this problem.

Now, I can observe a slightly different behavior of the UPS compared to the one reported in this post : Referenced content removed

When Windows was entering an hibernation mode, the UPS was restarted itself as soon as PCPE was active.

Now that Windows enter a shutdown mode, the UPS remains on the battery (even if the main power is back) until I switch on the computer.
As soon as the computer is switched on, the UPS restart itself and all UPS outlets are switched off for a few second.
From there, the UPS is on the main power source again and I can switch-on the PC again.
This is a little bit better than with hibernation mode because Windows has not yet started when the PC is switched-off.

So, is there a way to avoid the UPS to restart after the main computer has been switched off by PCPE?

Thanks for your help.

Message was edited by: superloupiot

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

0 Likes
0
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

OK, I have executed the requested command.
Which problem do you expect this command will solve?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

0 Likes
0
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

Hello,

When the UPS switch on the battery, the PC enter into an hibernation mode.
I would prefer that it always shutdown the computer, whatever the UPS battery load is.

How can I configure PCPE to make it always shutdown the PC?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

0 Likes
0
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

Guys,

In my configuration, the UPS backup a NAS (FreeNas) and the main computer.
I have written a script to shutdown the NAS when the main computer shutdown.
Unfortunately, until now, all tests I have done show that PCPE does not shutdown Windows but put it into hibernation.
As a results, the script is not executed in case of power loss and the NAS is not shutdown properly.

Is there a way to configure PCPE to execute a true shutdown rather than to put Windows into hibernation?
Or, is there a way to ask PCPE to execute a script rather than putting the computer into hibernation?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

0 Likes
0
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

You will need to disable hibernation on your Operating System. If you have this disabled the PC will then use the normal Shutdown when commanded by PCPE.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

0 Likes
0
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

Hibernation is disabled, however, PCPE put the PC into hibernation.

Message was edited by: superloupiot

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

0 Likes
0
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

What is the operating system of that PC and how did you disable hibernation?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

0 Likes
0
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

My operating system is Windows 7 Ultimate - 64 bit (french version).
I disable hibernation : Control Pannel -> System and security -> Power supply options -> There I select "High performance" and the option behind "High performance" are:
- Computer hibernation : Never
- Screen extinction : 15 minutes.

I have a French version of Windows, so this is an inaccurate translation of the Windows control panel.
How do you disable hibernation?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

0 Likes
0
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

If you use the powercfg /off command, it should disable the hibernate option. When the UPS commands the PC to turn off it'll use the shutdown and it should not put the PC on hibernate state.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

0 Likes
0
1951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM . Last Modified: ‎2024-03-07 01:38 AM

I have used the requested command and used the first runtime mode (because it takes less time to test).
And effectively, the PC is now entering a true shutdown mode. Thanks for the solution to this problem.

Now, I can observe a slightly different behavior of the UPS compared to the one reported in this post : Referenced content removed

When Windows was entering an hibernation mode, the UPS was restarted itself as soon as PCPE was active.

Now that Windows enter a shutdown mode, the UPS remains on the battery (even if the main power is back) until I switch on the computer.
As soon as the computer is switched on, the UPS restart itself and all UPS outlets are switched off for a few second.
From there, the UPS is on the main power source again and I can switch-on the PC again.
This is a little bit better than with hibernation mode because Windows has not yet started when the PC is switched-off.

So, is there a way to avoid the UPS to restart after the main computer has been switched off by PCPE?

Thanks for your help.

Message was edited by: superloupiot

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore