Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

PCPE 2.1.1, hibernation and shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCPE 2.1.1, hibernation and shutdown
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
superloupiot_apc
Ensign superloupiot_apc
Ensign

Posted: ‎2021-06-30 08:01 PM

0 Likes
9
565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM

PCPE 2.1.1, hibernation and shutdown

This was originally posted on APC forums on 1/3/2011


Hello,

When the UPS switch on the battery, the PC enter into an hibernation mode.
I would prefer that it always shutdown the computer, whatever the UPS battery load is.

How can I configure PCPE to make it always shutdown the PC?

Thanks.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
superloupiot_apc
Ensign superloupiot_apc
Ensign

Posted: ‎2021-06-30 08:01 PM

0 Likes
0
564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM

This was originally posted on APC forums on 1/3/2011


I have used the requested command and used the first runtime mode (because it takes less time to test).
And effectively, the PC is now entering a true shutdown mode. Thanks for the solution to this problem.

Now, I can observe a slightly different behavior of the UPS compared to the one reported in this post : Referenced content removed

When Windows was entering an hibernation mode, the UPS was restarted itself as soon as PCPE was active.

Now that Windows enter a shutdown mode, the UPS remains on the battery (even if the main power is back) until I switch on the computer.
As soon as the computer is switched on, the UPS restart itself and all UPS outlets are switched off for a few second.
From there, the UPS is on the main power source again and I can switch-on the PC again.
This is a little bit better than with hibernation mode because Windows has not yet started when the PC is switched-off.

So, is there a way to avoid the UPS to restart after the main computer has been switched off by PCPE?

Thanks for your help.

Message was edited by: superloupiot

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
superloupiot_apc
Ensign superloupiot_apc
Ensign

Posted: ‎2021-06-30 08:01 PM

0 Likes
0
564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM

This was originally posted on APC forums on 1/3/2011


OK, I have executed the requested command.
Which problem do you expect this command will solve?

Reply

Link copied. Please paste this link to share this article on your social media post.

superloupiot_apc
Ensign superloupiot_apc
Ensign

Posted: ‎2021-06-30 08:01 PM

0 Likes
0
564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM

This was originally posted on APC forums on 1/3/2011


Hello,

When the UPS switch on the battery, the PC enter into an hibernation mode.
I would prefer that it always shutdown the computer, whatever the UPS battery load is.

How can I configure PCPE to make it always shutdown the PC?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

superloupiot_apc
Ensign superloupiot_apc
Ensign

Posted: ‎2021-06-30 08:01 PM

0 Likes
0
564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM

This was originally posted on APC forums on 1/3/2011


Guys,

In my configuration, the UPS backup a NAS (FreeNas) and the main computer.
I have written a script to shutdown the NAS when the main computer shutdown.
Unfortunately, until now, all tests I have done show that PCPE does not shutdown Windows but put it into hibernation.
As a results, the script is not executed in case of power loss and the NAS is not shutdown properly.

Is there a way to configure PCPE to execute a true shutdown rather than to put Windows into hibernation?
Or, is there a way to ask PCPE to execute a script rather than putting the computer into hibernation?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:01 PM

0 Likes
0
564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM

This reply was originally posted by Jonathan on APC forums on 1/3/2011


You will need to disable hibernation on your Operating System. If you have this disabled the PC will then use the normal Shutdown when commanded by PCPE.

Reply

Link copied. Please paste this link to share this article on your social media post.

superloupiot_apc
Ensign superloupiot_apc
Ensign

Posted: ‎2021-06-30 08:01 PM

0 Likes
0
564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM

This was originally posted on APC forums on 1/3/2011


Hibernation is disabled, however, PCPE put the PC into hibernation.

Message was edited by: superloupiot

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:01 PM

0 Likes
0
564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM

This reply was originally posted by Jonathan on APC forums on 1/3/2011


What is the operating system of that PC and how did you disable hibernation?

Reply

Link copied. Please paste this link to share this article on your social media post.

superloupiot_apc
Ensign superloupiot_apc
Ensign

Posted: ‎2021-06-30 08:01 PM

0 Likes
0
564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM

This was originally posted on APC forums on 1/3/2011


My operating system is Windows 7 Ultimate - 64 bit (french version).
I disable hibernation : Control Pannel -> System and security -> Power supply options -> There I select "High performance" and the option behind "High performance" are:
- Computer hibernation : Never
- Screen extinction : 15 minutes.

I have a French version of Windows, so this is an inaccurate translation of the Windows control panel.
How do you disable hibernation?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:01 PM

0 Likes
0
564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM

This reply was originally posted by Jonathan on APC forums on 1/3/2011


If you use the powercfg /off command, it should disable the hibernate option. When the UPS commands the PC to turn off it'll use the shutdown and it should not put the PC on hibernate state.

Reply

Link copied. Please paste this link to share this article on your social media post.

superloupiot_apc
Ensign superloupiot_apc
Ensign

Posted: ‎2021-06-30 08:01 PM

0 Likes
0
565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:01 PM

This was originally posted on APC forums on 1/3/2011


I have used the requested command and used the first runtime mode (because it takes less time to test).
And effectively, the PC is now entering a true shutdown mode. Thanks for the solution to this problem.

Now, I can observe a slightly different behavior of the UPS compared to the one reported in this post : Referenced content removed

When Windows was entering an hibernation mode, the UPS was restarted itself as soon as PCPE was active.

Now that Windows enter a shutdown mode, the UPS remains on the battery (even if the main power is back) until I switch on the computer.
As soon as the computer is switched on, the UPS restart itself and all UPS outlets are switched off for a few second.
From there, the UPS is on the main power source again and I can switch-on the PC again.
This is a little bit better than with hibernation mode because Windows has not yet started when the PC is switched-off.

So, is there a way to avoid the UPS to restart after the main computer has been switched off by PCPE?

Thanks for your help.

Message was edited by: superloupiot

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc