Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

PCNS workflow stopped

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS workflow stopped
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BrianOwen_apc
Ensign BrianOwen_apc
Ensign

Posted: ‎2021-07-08 01:15 AM

0 Likes
8
780
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:15 AM

PCNS workflow stopped

This was originally posted on APC forums on 8/25/2015


I had one VM that does not have VMware Tools that may have caused a stop in the workflow. All VMs and one host shutdown fine. Then this troubled VM and the vCenter Server along with two hosts did not shutdown. Why didn't PCNS power off the VM without VMware Tools? Or maybe that wasn't the issue? I am trying to piece this together to make sure this goes more smoothly next time. I would appreate any help to figure out what happened.

-Here's my setup.

  • PCNS 4.0 on a physical Windows Server
  • VCSA 5.5
  • 3 ESXI 5.5 Hosts
  • 30 VMs
  • 2 vApps
  • svc-or-pcns is the service account with admin access to VMware environment

-Attached is the events of the VM that would not shutdown.

-PCNS Event Log

08/21/2015    18:08:44    OR VMware/SAN UPSs: UPS's have switched to bypass in response to the UPS front-panel or a user-initiated software command, typically for maintenance.
08/21/2015    18:09:14    OR VMware/SAN UPSs: UPS critical event: Bypass: For Maintenance.
08/21/2015    18:09:15    OR VMware/SAN UPSs: UPS critical event: Bypass: For Maintenance triggered a shutdown on Hosts 10.8.3.65, 10.8.3.67, 10.8.3.66.
08/21/2015    18:09:16    Enter maintenance mode on Host 10.8.3.65.
08/21/2015    18:09:16    Enter maintenance mode on Host 10.8.3.67.
08/21/2015    18:09:16    Shutting down VMs on Host 10.8.3.65.
08/21/2015    18:09:16    Enter maintenance mode on Host 10.8.3.66.
08/21/2015    18:09:16    Shutting down VMs on Host 10.8.3.67.
08/21/2015    18:09:16    Shutting down VMs on Host 10.8.3.66.
08/21/2015    18:17:16    Shutting down vApp SharePoint in datacenter AFMS-2CON.
08/21/2015    18:17:16    Starting vApp shutdown process.
08/21/2015    18:17:16    Shutting down vApp SA in datacenter AFMS-2CON.
08/21/2015    18:25:16    Host 10.8.3.66 has successfully entered maintenance mode.
08/21/2015    18:25:17    Maintenance mode task cancelled on Host 10.8.3.65 as there are still powered on VMs. Please verify that sufficient time has been configured for VM/vApp/VCSA VM shutdown duration.
08/21/2015    18:25:17    Shutting down Host 10.8.3.65.
08/21/2015    18:25:19    Shutdown Host failed for Host 10.8.3.67.
08/21/2015    18:25:19    Shutting down Host 10.8.3.66.

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BrianOwen_apc
Ensign BrianOwen_apc
Ensign

Posted: ‎2021-07-08 01:15 AM

0 Likes
0
779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:15 AM

This was originally posted on APC forums on 8/27/2015


Sure, I would appreicate you looking at the logs. Which log in particular do you want? Or the whole log bundle of one of the ESXi hosts? Do you have somewhere I can upload it to?

See Answer In Context

Reply
Share
Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:15 AM

0 Likes
0
779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:15 AM

This reply was originally posted by Bill on APC forums on 8/25/2015


Hi,

PowerChute and VMware host cannot shut down any VMs that do not have VMware Tools installed. In your case the VM would have crashed since the host was commanded down. You should install VMware tools on all VMs you want powered down.

The log also shows Shutdown Host failed for Host 10.8.3.67. Normally is indicates a permissions issue. You can review the error log in the PCNS install folder. It should provide insight as to why the shutdown failed.

Is vCenter Server running on a VM and if so is it running on that host?

Reply
Share
BrianOwen_apc
Ensign BrianOwen_apc
Ensign

Posted: ‎2021-07-08 01:15 AM

0 Likes
0
779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:15 AM

This was originally posted on APC forums on 8/25/2015


Bill, thanks for your reply.

Oh. For some reason, I thought PCNS would power it off. Not a graceful shutdown. Unforuntely, I have VMs that cannot have VMware Tools installed since they are appliances from a vendor.

I just checked the error log and there are no events from the date of the shut down.

Yes, vCenter Server is running on a VM and it was on host 10.8.3.67.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:15 AM

0 Likes
0
780
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:15 AM

This reply was originally posted by Bill on APC forums on 8/25/2015


Hi,

When you view the host protection page is host .67 signified by the Vcenter icon? below host luna.scvmmgal.net has the VM that vCenter is install on.

If not you will need to install VMware Tools on the VM vCenter is running on. I suggest after adding the Tools rerunning PCNS configuration and rediscover vCenter.

Attachments
Reply
Share
BrianOwen_apc
Ensign BrianOwen_apc
Ensign

Posted: ‎2021-07-08 01:15 AM

0 Likes
0
780
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:15 AM

This was originally posted on APC forums on 8/25/2015


I verified host .67 has the vCenter Server logo next to it on the host protection page and VMware Tools is running on it.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:15 AM

0 Likes
0
780
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:15 AM

This reply was originally posted by Bill on APC forums on 8/26/2015


Brian,

If the error log in the PowerChute folder does not list anything for that date this is tough to troubleshoot. Since PowerChute recognizes that host has vCenter another possible cause is permissions. Again, the error log would help diagnose the cause.

Since the error log is not available could you rerun the shutdown and before doing so put PowerChute into debug mode. Kbase document FA230514 describes how to change PowerChute to debug mode. When the test is done please send the error log for review.

Reply
Share
BrianOwen_apc
Ensign BrianOwen_apc
Ensign

Posted: ‎2021-07-08 01:15 AM

0 Likes
0
780
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:15 AM

This was originally posted on APC forums on 8/26/2015


Gotcha. I will try debug mode next time to get more information.

I have another question. I just used the vSphere client to log into each of the 3 hosts. All 3 have a task started every two minutes 'Find entity by IP' and it was satrted by the service account I use for PCNS. Is this normal?

Attachments
Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:15 AM

0 Likes
0
780
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:15 AM

This reply was originally posted by Bill on APC forums on 8/27/2015


Brian,

PCNS uses Find by IP API to discover the host/s. I find it strange that this API would be called continually. Would you provide 1 of the system logs for review?

Reply
Share
BrianOwen_apc
Ensign BrianOwen_apc
Ensign

Posted: ‎2021-07-08 01:15 AM

0 Likes
0
780
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 01:15 AM

This was originally posted on APC forums on 8/27/2015


Sure, I would appreicate you looking at the logs. Which log in particular do you want? Or the whole log bundle of one of the ESXi hosts? Do you have somewhere I can upload it to?

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc