PCNS v3.01 With ESXi 5

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS v3.01 With ESXi 5
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
emy26_apc
Ensign emy26_apc
Ensign

Posted: ‎2021-07-01 01:34 AM . Last Modified: ‎2024-03-06 01:34 AM

0 Likes
5
1611
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:34 AM . Last Modified: ‎2024-03-06 01:34 AM

PCNS v3.01 With ESXi 5

Hi
i've followed documentation sited on VMWARE KB to install agent on my ESXi Host:
http://www2.schneider-electric.com/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/159000/FA159...

after the installation i got error (see attached)
same error appear on the documentation but i can't see the url for configuration..
Can you please help me?

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
emy26_apc
Ensign emy26_apc
Ensign

Posted: ‎2021-07-01 01:34 AM . Last Modified: ‎2024-03-06 01:34 AM

0 Likes
0
1614
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:34 AM . Last Modified: ‎2024-03-06 01:34 AM

yes server is on the list with FQDN name. No i've used IP of the Remote host am i wrong?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:34 AM . Last Modified: ‎2024-03-06 01:34 AM

0 Likes
0
1614
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:34 AM . Last Modified: ‎2024-03-06 01:34 AM

you should use the IP of the vMA cause that is where PCNS is installed.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:34 AM . Last Modified: ‎2024-03-06 01:34 AM

0 Likes
0
1614
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:34 AM . Last Modified: ‎2024-03-06 01:34 AM

hello,

can you clarify what you mean? you can't see log in to the PCNS configuration? cause you should be trying to access the vMA's IP address and not the ESXi host because that is where PCNS is installed.

if you look at the attached document you pasted, pages 54/55 tell you what to do when the error you get comes up. you need to do the command listed:

sudo vifp addserver 10.218.45.20

in my example, 10.218.45.20 is the ESXi host and you'd replace that with your IP if it did not add during the installation. did you run that command? if so, then you need to do like i mentioned and go to the URL: https://:6547

i hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

emy26_apc
Ensign emy26_apc
Ensign

Posted: ‎2021-07-01 01:34 AM . Last Modified: ‎2024-03-06 01:34 AM

0 Likes
0
1614
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:34 AM . Last Modified: ‎2024-03-06 01:34 AM

Hello what i've tried to do is to lauch command sudo ./install_en.sh

and it says Failed to add ESXi host
To add the host manually please run - sudo vifp addserver (my ip address)
at the end of command i've tried that but it still says: your Host (my IP address) is already a vMA target.

after that i've tried to open https://myipaddress:6547/
but i don't take PCNS webpage for configuration

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:34 AM . Last Modified: ‎2024-03-06 01:34 AM

0 Likes
0
1614
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:34 AM . Last Modified: ‎2024-03-06 01:34 AM

did you run the listservers command listed to verify you see it in the list?

and you are using the IP address of the vMA it sounds like on port 6547..?

Reply

Link copied. Please paste this link to share this article on your social media post.

emy26_apc
Ensign emy26_apc
Ensign

Posted: ‎2021-07-01 01:34 AM . Last Modified: ‎2024-03-06 01:34 AM

0 Likes
0
1615
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:34 AM . Last Modified: ‎2024-03-06 01:34 AM

yes server is on the list with FQDN name. No i've used IP of the Remote host am i wrong?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore