Hi,
before the shutdown of a Simplivity host the Omnistack Virtual Controller VM must gracefully shutdown. I do not know if this is included in the pcns procedure. The other way would be a script which connects via ssh to the OVC and executes an svt-shutdown-safe. The problem is that on the pcns appliance the ssh client is disabled.
Is APC PCNS with HPE Simpliivity Systems not supported?
Regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:03 AM . Last Modified: 2024-03-11 12:16 AM
Hi,
I apologize. The demos I have seen shows the VMware web interface as the management of the Simplivity hosts and VMs. They appeared to be standard hosts. After further review I was mistaken.
I have checked with Product Management and Simplivity is on the enhancement list for a future release of PCNS.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:03 AM . Last Modified: 2024-03-11 12:16 AM
Hi,
PCNS currently supports VMware and Microsoft Hypervisors. The understanding I have is Simplivity is an integration plugin to VMware vCenter Server. You can integrate PCNS with vCenter and PCNS will then power down VMs, and hosts as needed. See PCNS VMware User's Guide http://www.apc.com/salestools/PMAR-9DNLQK/PMAR-9DNLQK_R3_EN.pdf
Application Note 180 for PCNS VMware http://www.apc.com/salestools/SJHN-92FLU8/SJHN-92FLU8_R6_EN.pdf
PCNS brochure http://www.apc.com/salestools/SJHN-9D9PDZ/SJHN-9D9PDZ_R4_EN.pdf
PCNS compatibility chart http://www.apc.com/salestools/SJHN-7AYQNP/SJHN-7AYQNP_R84_EN.pdf
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:03 AM . Last Modified: 2024-03-11 12:16 AM
Hi,
the problem is that Simplivity Hosts are hyperconverged. The storage is local and is managed by a controller vm. This vm's are called OVC's. Simplivity installs a vSphere webclient plugin which offers the management of this controllers. If you want to shutdown this vm's you don't right click an choose "Power" and "Shutdown Guest OS" ! It has an own menu which is called "Shutdown Virtual Controller". I think that this will initiate a stop sequence of services inside the vm to guarantee that the datastores will be closed safely.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:03 AM . Last Modified: 2024-03-11 12:16 AM
Hi,
I apologize. The demos I have seen shows the VMware web interface as the management of the Simplivity hosts and VMs. They appeared to be standard hosts. After further review I was mistaken.
I have checked with Product Management and Simplivity is on the enhancement list for a future release of PCNS.