PCNS did not shut down environment

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS did not shut down environment
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:43 AM

0 Likes
4
1109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:43 AM

PCNS did not shut down environment

We experienced a recent power outage where our virtual PCNS 4.3 device did not shutdown our VMware environment (we are running vSphere 7 on VCSA, the two hosts in the same cluster are running ESXi 7).  All that happened was our UPS eventually drained its battery and all the equipment powered off with no safe shutdown.

The APC UPS is a Smart-UPS SRT 5000 (SRT5KXLI) and is using the built in management card AP9537SUM.

Both the VCSA and the PCNS are on the same IP range.  I can validate the communications settings on the PCNS when I click check details, the authentication phrase is the same one used on both the PCNS and the UPS.

The ESXi hosts and the UPS device are all plugged into the same switch in the same physical location.

When I check host protection I can see the hosts.

When I look at the event log I can see random alerts that 'Cannot connect to http://x.x.x.x:80' (IP address is the UPS) but then it also alerts saying it has successfully opened TCP port 3052 and 6547.  

I also see random events that vCenter Server authentication error but then seconds afterwards it says vCenter Server is accessible

I need advice as to where to start troubleshooting and confirmation that this setup should work.

Thanks.

 

 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • esxi
  • pcns
  • vmware
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:01 AM . Last Modified: ‎2024-03-08 01:42 AM

0 Likes
0
1108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:01 AM . Last Modified: ‎2024-03-08 01:42 AM

Thank you for pointing me in the right direction

We have now successfully managed to shutdown our environment by implementing the following:

  1. Adding local user accounts to each host + vsphere.local account to our vSphere setup with administrator access
  2. Performed setup wizard again on PCNS device using port 443 to access the UPS NMC and reapplying the authentication phrase

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:42 AM

0 Likes
0
1109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:42 AM

Hi,

 I would first look at the network card event log to find the date and time the UPS switched to the battery. Then you should check the PowerChute event log, error log, and debug log. The logs are in /opt/APC/PowerChute/group1. In the PowerChute event, log look to see if there is an entry posted when the UPS switched to the battery? Also, in the debug log do you see lost comm with the network card and or vCenter? 

Troubleshooting help starts on page 174 of the attached User's Guide.

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:42 AM

0 Likes
0
1109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:00 AM . Last Modified: ‎2024-03-08 01:42 AM

Thank you for coming back to me.

The debug log regularly performs this routine, I assume this is normal and it is checking to see if it needs to do anything?

2020-09-15T11:48:28,190 DEBUG pool-3-thread-1 com.apcc.m11.components.Shutdowner.VirtualHostStatusTask - run() - start
2020-09-15T11:48:28,191 DEBUG pool-3-thread-1 com.apcc.m11.components.Shutdowner.ShutdownState - getCriticalShutdownTimers() - no critical timers
2020-09-15T11:48:28,191 DEBUG pool-3-thread-1 com.apcc.m11.components.Shutdowner.VirtualHostStatusTask - checkCriticalHostsShutdown() - no critical timers, host shutdown not required
2020-09-15T11:48:28,191 DEBUG pool-3-thread-1 com.apcc.m11.components.Shutdowner.VirtualHostStatusTask - checkPerformStartup() - start
2020-09-15T11:48:28,191 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualizationUtils - isStartupWaitsForAllHostsOnlineEnabled() - found key: startup_waits_for_all_hosts_online
2020-09-15T11:48:28,192 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualizationUtils - isStartupWaitsForAllHostsOnlineEnabled() - end, result: false
2020-09-15T11:48:28,192 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualizationUtils - isESXI() - end, result: true
2020-09-15T11:48:28,193 DEBUG pool-3-thread-1 com.apcc.m11.components.Shutdowner.VirtualHostStatusTask - isVCSAStartupRequired() - start
2020-09-15T11:48:28,193 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualisationStatusStore - loadProperties() - start
2020-09-15T11:48:28,193 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualisationStatusStore - getVirtualStorePropertyFilePath() - end, result: /opt/APC/PowerChute/group1/VirtualizationFileStore.properties
2020-09-15T11:48:28,193 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualisationStatusStore - getProperty() - VCSA_HOST = null
2020-09-15T11:48:28,193 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualisationStatusStore - getVcsaHost() - end, result: null
2020-09-15T11:48:28,193 DEBUG pool-3-thread-1 com.apcc.m11.components.Shutdowner.VirtualHostStatusTask - isVCSAStartupRequired() - vCenterHostIP is null, returning false
2020-09-15T11:48:28,193 DEBUG pool-3-thread-1 com.apcc.m11.components.Shutdowner.VirtualHostStatusTask - proceedWithVirtualizationStartup() - VCSA startup is not required
2020-09-15T11:48:28,193 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualisationStatusStore - getLockedHostSetFromVirtualizationFileStore() - start
2020-09-15T11:48:28,193 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualisationStatusStore - loadProperties() - start
2020-09-15T11:48:28,193 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualisationStatusStore - getVirtualStorePropertyFilePath() - end, result: /opt/APC/PowerChute/group1/VirtualizationFileStore.properties
2020-09-15T11:48:28,193 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualisationStatusStore - getHostSetFromVirtualizationFileStore() - end, locked: false hosts: []
2020-09-15T11:48:28,193 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualisationStatusStore - loadProperties() - start
2020-09-15T11:48:28,193 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualisationStatusStore - getVirtualStorePropertyFilePath() - end, result: /opt/APC/PowerChute/group1/VirtualizationFileStore.properties
2020-09-15T11:48:28,193 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualisationStatusStore - getProperty() - Witness_VM_HOST = null
2020-09-15T11:48:28,193 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualisationStatusStore - loadProperties() - start
2020-09-15T11:48:28,193 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualisationStatusStore - getVirtualStorePropertyFilePath() - end, result: /opt/APC/PowerChute/group1/VirtualizationFileStore.properties
2020-09-15T11:48:28,193 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualisationStatusStore - getVMAndVAppHostList() - end, result: []
2020-09-15T11:48:28,194 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualizationUtils - isNutanixSupported() - end, result: false
2020-09-15T11:48:28,195 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualizationUtils - isNutanixESXi() - end, result: false
2020-09-15T11:48:28,195 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualizationUtils - isESXI() - end, result: true
2020-09-15T11:48:28,197 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualizationUtils - isESXI() - end, result: true
2020-09-15T11:48:28,197 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.AdvancedSetupHelper - isAdvancedShutdownMode() - result: false
2020-09-15T11:48:28,197 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VMware.VMWareConnection - isvCenterServerConnectionSuccessful() - result: true
2020-09-15T11:48:28,197 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualisationStatusStore - getClusterSetWithDrsChanged() - start
2020-09-15T11:48:28,197 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualisationStatusStore - loadProperties() - start
2020-09-15T11:48:28,197 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualisationStatusStore - getVirtualStorePropertyFilePath() - end, result: /opt/APC/PowerChute/group1/VirtualizationFileStore.properties
2020-09-15T11:48:28,198 DEBUG pool-3-thread-1 com.apcc.m11.components.WebServer.util.virtualization.VirtualisationStatusStore - getClusterSetWithDrsChanged() - end, result: []
2020-09-15T11:48:28,198 DEBUG pool-3-thread-1 com.apcc.m11.components.Shutdowner.VirtualHostStatusTask - run() - end

At the time of the power cut the debug log mentions nothing of power loss or issuing commands, it just repeats the above every two minutes until the UPS battery was drained.

The UPS log confirms that it switched to battery so there is no fault with the UPS (could it possibly need a firmware upgrade to work with newer version of 4.3 PCNS?)  The UPS firmware is running UPS 04.0 (ID1013) and the onboard card is running application/OS version 6.5.0 and boot monitor is running 1.08 - I have tried to look up our model on the APC UPS website for updates but cannot find any?

What we have wondered today is on PCNS device going into Communication Settings does the vCenter account have to also be a local admin account on each ESXi host but also be an admin account in vSphere?  At the moment, we are using the default administrator@vsphere.local account for the vCenter login

Regardless of the above, we may have solved this because on the PCNS device Configure Events only Logging was selected.

Can you confirm that we do need to set a shutdown action, for example, Runtime remaining below threshold set to x number of seconds before it will do anything?!

🙂

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:01 AM . Last Modified: ‎2024-03-08 01:42 AM

0 Likes
0
1110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:01 AM . Last Modified: ‎2024-03-08 01:42 AM

Hi,

On 9/17/2020 11:58 AM, T said:

What we have wondered today is on PCNS device going into Communication Settings does the vCenter account have to also be a local admin account on each ESXi host but also be an admin account in vSphere?  At the moment, we are using the default administrator@vsphere.local account for the vCenter login

You should create an admin account that PCNS will use to communicate to vCenter and each host. See the videos attached to Schneider Electric FAQ FA349917.

On 9/17/2020 11:58 AM, T said:

Can you confirm that we do need to set a shutdown action, for example, Runtime remaining below threshold set to x number of seconds before it will do anything?!

If you do not configure any shutdown setting, PCNS will trigger the shutdown process when the UPS reaches low battery. See Schneider Electric FAQ FA405707

I recommend configuring PCNS to shutdown after UPS runs on battery for x time or when runtime remaining fall below x. Setting one of those will prevent the battery from draining to the low battery state. 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:01 AM . Last Modified: ‎2024-03-08 01:42 AM

0 Likes
0
1109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:01 AM . Last Modified: ‎2024-03-08 01:42 AM

Thank you for pointing me in the right direction

We have now successfully managed to shutdown our environment by implementing the following:

  1. Adding local user accounts to each host + vsphere.local account to our vSphere setup with administrator access
  2. Performed setup wizard again on PCNS device using port 443 to access the UPS NMC and reapplying the authentication phrase
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of