PCNS constantly shutting down server

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS constantly shutting down server
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:11 AM

0 Likes
3
1286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:11 AM

PCNS constantly shutting down server

Hello,
My boss restarted a network card on one of our servers yesterday, which resulted in PCNS shutting down the server the "Communication: PowerChute cannot communicate with the Management Card" event was set to shutdown after 180 seconds. I can understand this happening the first time as it may be that it genuinely took that long and the network card had not re-initialised.

The event log reported:
03/15/2011 13:23:23 PowerChute Network Shutdown version 2.2.4 started
03/15/2011 13:25:23 Network Communication with address birmups3.crawco.co.uk has been lost
03/15/2011 13:25:23 Network Communication with address birmups4.crawco.co.uk has been lost
03/15/2011 13:25:23 PowerChute cannot communicate with the Management Cards
03/15/2011 13:28:23 Shutdown process started. Windows will shut down soon

Repeatedly (about 30 times)

The problem was however that the server kept on shutting down every time it was switched back on even though the network card was back up (my colleague was connecting the the server remotely using terminal services using the same LAN card so it definately initialised for that to happen). However he was only able to spend a few seconds on the server to fault find before it shut down again and in the end it took several hours before they realised that PCNS was to blame. The issue eventually resolved itself but is this something that others have experienced? The server in question is a primary backup server and as such it is important that downtime is minimal and we cannot really have this same scenario happen again. (I have increased the shutdown delay to 600 seconds in any case to give us more time to react if this does happen in future).

Thanks in advance for any advise.
Allan

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • network_management_card
  • pcns
  • shutdown
  • smart-ups
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:11 AM

0 Likes
0
1287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:11 AM

well this definitely just shows that PCNS could not communicate with the NMCs. my only thought is somehow the NMC got stuck in a certain state or lost communication with the UPS or something that caused the issue you saw. i cannot really say much more without seeing an event.txt from the NMC. if it is spammed out with the events you mentioned, then perhaps we will just have to guess at what happened.

we definitely dont have any known issues of this sort so if it happens again for some reason, ensure that you get the PCNS logs and the event.txt from the NMC to review.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:11 AM

0 Likes
0
1287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:11 AM

hi allan,

can you check the event.txt from the NMC at the time that this happened?

you can get it via FTP via these instructions -> http://nam-en.apc.com/app/answers/detail/a_id/9321/

also, can you post any more of the PCNS log besides what you posted?

thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:11 AM

0 Likes
0
1287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:11 AM

Thanks for your responce, apart from showing me that the date/SMTP server name were configured incorrectly (all events are out by a year and several reports of SMTP server resolution failed) the event.txt that I downloaded does not show much, Only events to happen on that day are - Started Self Test, failed to resolve SMTPservername, Passed Self Test.

Below are all of the events from the PCNS log that occured on the day:

03/15/2011 13:51:25 Communications have been established
03/15/2011 13:51:25 Management Card birmups3.crawco.co.uk communication has been established
03/15/2011 13:51:08 Management Card birmups4.crawco.co.uk communication has been established
03/15/2011 13:50:38 PowerChute Network Shutdown version 2.2.4 started
03/15/2011 13:37:46 Communications have been established
03/15/2011 13:37:46 Management Card birmups3.crawco.co.uk communication has been established
03/15/2011 13:37:30 Management Card birmups4.crawco.co.uk communication has been established
03/15/2011 13:37:12 PowerChute Network Shutdown version 2.2.4 started
03/15/2011 13:28:23 Shutdown process started. Windows will shut down soon.
03/15/2011 13:25:23 PowerChute cannot communicate with the Management Cards
03/15/2011 13:25:23 Network Communication with address birmups4.crawco.co.uk has been lost
03/15/2011 13:25:23 Network Communication with address birmups3.crawco.co.uk has been lost
03/15/2011 13:23:23 PowerChute Network Shutdown version 2.2.4 started
03/15/2011 13:10:09 Shutdown process started. Windows will shut down soon.
03/15/2011 13:07:09 PowerChute cannot communicate with the Management Cards
03/15/2011 13:07:09 Network Communication with address birmups3.crawco.co.uk has been lost
03/15/2011 13:07:09 Network Communication with address birmups4.crawco.co.uk has been lost
03/15/2011 13:05:09 PowerChute Network Shutdown version 2.2.4 started
03/15/2011 12:56:54 PowerChute cannot communicate with the Management Cards
03/15/2011 12:56:54 Network Communication with address birmups4.crawco.co.uk has been lost
03/15/2011 12:56:54 Network Communication with address birmups3.crawco.co.uk has been lost
03/15/2011 12:54:55 PowerChute Network Shutdown version 2.2.4 started
03/15/2011 12:45:44 Shutdown process started. Windows will shut down soon.
03/15/2011 12:42:44 PowerChute cannot communicate with the Management Cards
03/15/2011 12:42:44 Network Communication with address birmups3.crawco.co.uk has been lost
03/15/2011 12:42:44 Network Communication with address birmups4.crawco.co.uk has been lost
03/15/2011 12:40:44 PowerChute Network Shutdown version 2.2.4 started
03/15/2011 12:32:07 Shutdown process started. Windows will shut down soon.
03/15/2011 12:29:07 PowerChute cannot communicate with the Management Cards
03/15/2011 12:29:07 Network Communication with address birmups3.crawco.co.uk has been lost
03/15/2011 12:29:07 Network Communication with address birmups4.crawco.co.uk has been lost
03/15/2011 12:27:07 PowerChute Network Shutdown version 2.2.4 started
03/15/2011 12:18:28 Shutdown process started. Windows will shut down soon.
03/15/2011 12:15:27 PowerChute cannot communicate with the Management Cards
03/15/2011 12:15:27 Network Communication with address birmups4.crawco.co.uk has been lost
03/15/2011 12:15:27 Network Communication with address birmups3.crawco.co.uk has been lost
03/15/2011 12:13:27 PowerChute Network Shutdown version 2.2.4 started
03/15/2011 12:02:35 Shutdown process started. Windows will shut down soon.
03/15/2011 11:59:35 PowerChute cannot communicate with the Management Cards
03/15/2011 11:59:35 Network Communication with address birmups4.crawco.co.uk has been lost
03/15/2011 11:59:35 Network Communication with address birmups3.crawco.co.uk has been lost
03/15/2011 11:57:35 PowerChute Network Shutdown version 2.2.4 started
03/15/2011 11:48:15 Shutdown process started. Windows will shut down soon.
03/15/2011 11:45:15 PowerChute cannot communicate with the Management Cards
03/15/2011 11:45:15 Network Communication with address birmups3.crawco.co.uk has been lost
03/15/2011 11:45:15 Network Communication with address birmups4.crawco.co.uk has been lost
03/15/2011 11:43:15 PowerChute Network Shutdown version 2.2.4 started
03/15/2011 11:22:57 Shutdown process started. Windows will shut down soon.
03/15/2011 11:19:57 PowerChute cannot communicate with the Management Cards
03/15/2011 11:19:57 Network Communication with address birmups4.crawco.co.uk has been lost
03/15/2011 11:19:57 Network Communication with address birmups3.crawco.co.uk has been lost
03/15/2011 11:17:57 PowerChute Network Shutdown version 2.2.4 started
03/15/2011 11:07:34 Shutdown process started. Windows will shut down soon.
03/15/2011 11:04:34 PowerChute cannot communicate with the Management Cards
03/15/2011 11:04:34 Network Communication with address birmups4.crawco.co.uk has been lost
03/15/2011 11:04:34 Network Communication with address birmups3.crawco.co.uk has been lost
03/15/2011 11:02:34 PowerChute Network Shutdown version 2.2.4 started
03/15/2011 10:52:01 Shutdown process started. Windows will shut down soon.
03/15/2011 10:49:01 PowerChute cannot communicate with the Management Cards
03/15/2011 10:49:01 Network Communication with address birmups3.crawco.co.uk has been lost
03/15/2011 10:49:01 Network Communication with address birmups4.crawco.co.uk has been lost
03/15/2011 10:47:01 PowerChute Network Shutdown version 2.2.4 started
03/15/2011 10:38:35 Shutdown process started. Windows will shut down soon.
03/15/2011 10:35:35 PowerChute cannot communicate with the Management Cards
03/15/2011 10:35:35 Network Communication with address birmups3.crawco.co.uk has been lost
03/15/2011 10:35:35 Network Communication with address birmups4.crawco.co.uk has been lost
03/15/2011 10:33:35 PowerChute Network Shutdown version 2.2.4 started
03/15/2011 10:23:26 Shutdown process started. Windows will shut down soon.
03/15/2011 10:20:26 PowerChute cannot communicate with the Management Cards
03/15/2011 10:20:26 Network Communication with address birmups4.crawco.co.uk has been lost
03/15/2011 10:20:26 Network Communication with address birmups3.crawco.co.uk has been lost
03/15/2011 10:18:26 PowerChute Network Shutdown version 2.2.4 started
03/15/2011 10:10:06 Shutdown process started. Windows will shut down soon.
03/15/2011 10:07:06 PowerChute cannot communicate with the Management Cards
03/15/2011 10:07:06 Network Communication with address birmups3.crawco.co.uk has been lost
03/15/2011 10:07:06 Network Communication with address birmups4.crawco.co.uk has been lost
03/15/2011 10:05:06 PowerChute Network Shutdown version 2.2.4 started
03/15/2011 09:57:24 Shutdown process started. Windows will shut down soon.
03/15/2011 09:54:24 PowerChute cannot communicate with the Management Cards
03/15/2011 09:54:24 Network Communication with address birmups4.crawco.co.uk has been lost
03/15/2011 09:54:24 Network Communication with address birmups3.crawco.co.uk has been lost
03/15/2011 09:52:24 PowerChute Network Shutdown version 2.2.4 started
03/15/2011 09:42:21 Shutdown process started. Windows will shut down soon.
03/15/2011 09:39:21 PowerChute cannot communicate with the Management Cards
03/15/2011 09:39:21 Network Communication with address birmups4.crawco.co.uk has been lost
03/15/2011 09:39:21 Network Communication with address birmups3.crawco.co.uk has been lost
03/15/2011 09:37:22 PowerChute Network Shutdown version 2.2.4 started
03/15/2011 09:21:26 Shutdown process started. Windows will shut down soon.
03/15/2011 09:18:27 PowerChute cannot communicate with the Management Cards
03/15/2011 09:18:26 Network Communication with address birmups4.crawco.co.uk has been lost
03/15/2011 09:18:26 Network Communication with address birmups3.crawco.co.uk has been lost
03/15/2011 09:16:27 PowerChute Network Shutdown version 2.2.4 started
03/15/2011 08:36:45 Shutdown process started. Windows will shut down soon.
03/15/2011 08:33:44 PowerChute cannot communicate with the Management Cards
03/15/2011 08:33:44 Network Communication with address birmups3.crawco.co.uk has been lost
03/15/2011 08:33:28 Network Communication with address birmups4.crawco.co.uk has been lost

At 08.30 is when my manager re-initialised the LAN card on the server, so we can accept that it would have lost connection and possibly rebooted at that time.

Hope this helps - thanks, Allan

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:11 AM

0 Likes
0
1288
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:33 AM . Last Modified: ‎2024-03-13 04:11 AM

well this definitely just shows that PCNS could not communicate with the NMCs. my only thought is somehow the NMC got stuck in a certain state or lost communication with the UPS or something that caused the issue you saw. i cannot really say much more without seeing an event.txt from the NMC. if it is spammed out with the events you mentioned, then perhaps we will just have to guess at what happened.

we definitely dont have any known issues of this sort so if it happens again for some reason, ensure that you get the PCNS logs and the event.txt from the NMC to review.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore