PCNS cannot connect to the UPS. FA159624 is useless.
If you have no ideas, then post a link to sumx 6.2.0 firmware please. I did not find it on the official website and generally anywhere.
Time | IP address | Description |
---|---|---|
19:35:48 | 192.168.1.88 | Cannot connect to http://192.168.1.88:80 |
19:35:47 | 192.168.1.88 | Checking connection to http://192.168.1.88:80 |
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions

Posted: 2021-06-30 05:06 AM . Last Modified: 2024-03-08 03:14 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:06 AM . Last Modified: 2024-03-08 03:14 AM
Thank you very much!
It was necessary to enable HTTP for PowerChute in the NMC web interface, as written in the "useless" document.
Thank you again!
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:06 AM . Last Modified: 2024-03-08 03:14 AM
Hi,Sorry for the inconvenience. When an NMC is updated to firmware 6.8 and rebooted http is disabled. Step 14 of the mentioned FAQ discusses how to resolve the issue.
14. If the AP9630, AP9631, AP9635, AP9537SUM is running firmware 6.8.X or the NMC is a AP9640, AP9641 verify that HTTP and or HTTPS has been enable. To enable HTTP and or HTTPS open the NMC web interface and go to Configuration - Network - Web - Access. Also, verify that HTTP and or HTTPS protocol has been enable for PowerChute. To verify HTTP and or HTTPS protocol has been enable for PowerChute open the NMC web interface and go to Configuration - Shutdown. You will find the PowerChute Communication Protocol at the bottom of the page.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-30 05:06 AM . Last Modified: 2024-03-08 03:14 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:06 AM . Last Modified: 2024-03-08 03:14 AM
Thank you very much!
It was necessary to enable HTTP for PowerChute in the NMC web interface, as written in the "useless" document.