Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
PCNS cannot communicate with NMC when directly connected to host
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0806:07 AM. Last Modified: 2024-02-1512:06 AM
PCNS cannot communicate with NMC when directly connected to host
Hi,
I have an AP9631 NMC that I want to use to shutdown an ESXi 6.7 host running on a Dell R440, using the virtual appliance containing PCNS 4.2.
If I connect NMC Ethernet port to one of R400 NICs, Powerchute cannot communicate with NMC. My other virtual machines also cannot ping NMC. If I connect NMC to my laptop, I can access it normally.
However, if I connect NMC to a physical switch and then connect this switch to one of R440 NICs, everything works fine: PCNS finds the NMC and the shutdown feature works as expected.
Why PCNS cannot communicate with NMC when it's directly connected to the host?
I don't think it's an authentication issue, since it works fine when connected to the physical switch.
Some information:
ESXi IP address: 10.0.240.201, manually set.
NMC IP address: 10.0.240.205, manually set.
R440 has 4 NICs, all of them on the same vSwitch, which is also connected to the VM Management network.
The physical switch that do the trick is a Rockwell Stratix 5700, running Cisco IOS.
UPS is a SRC2000XLI.
ESXi host is licensed (Essentials kit).
I have two virtual machines running Windows Server 2012R2 besides PCNS VM, if it matters.