Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

PCNS 4.2 with two UPS and Multiple ESXi hosts

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS 4.2 with two UPS and Multiple ESXi hosts
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
vx_it_apc
Crewman vx_it_apc
Crewman

Posted: ‎2021-07-08 06:06 AM . Last Modified: ‎2024-02-15 12:07 AM

0 Likes
7
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:06 AM . Last Modified: ‎2024-02-15 12:07 AM

PCNS 4.2 with two UPS and Multiple ESXi hosts

Hello,

I'm trying to understand how to correctly set up this environment:

  • UPS 1, single non-redundant
    • ESXi Host #1 (standalone)
      • vCenter Server deployed here as a VM
      • PCNS 4.2 deployed here as a Virtual Appliance
    • ESXi Host #2 (standalone)
  • UPS 2, single non-redundant
    • ESXi Host #3 (standalone)

As you can see, we have a PCNS 4.2 appliance (the older, pre-CentOS7 release, if that makes any difference) deployed already on ESXi Host #1. There used to be a separate PCNS appliance on ESXi host 2 and 3 as well, but they did not get migrated over during the last upgrade.

My question is, for best control of graceful shutdown of the hosts/VMs, should I set up PCNS appliances for the other two ESXi hosts again, or is the one I have on ESXi Host #1 sufficient for management of all 3 hosts even though they are spread across different UPS's?

I don't mind deploying additional PCNS appliances per host if that's considered best practice. 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 06:06 AM . Last Modified: ‎2024-02-15 12:07 AM

0 Likes
0
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:06 AM . Last Modified: ‎2024-02-15 12:07 AM

Hi,

You should install PCNS on each of the host. Configure host 1 with vCenter to allow vCenter to be powered down properly. Configure PCNS on hosts 2 & 3 as standalone. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 06:07 AM . Last Modified: ‎2024-02-15 12:07 AM

0 Likes
0
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:07 AM . Last Modified: ‎2024-02-15 12:07 AM

Hi,

Sorry for the inconvenience. What version of PCNS appliance did you install? the latest version allow you to set the time zone when the OS first start up.  

QiJcOojnGx4T4Rmy%2FW3q7A%3D%3D.pngQiJcOojnGx4T4Rmy%2FW3q7A%3D%3D.png

to set the time zone from the command line the command is 

timedatectl set-timezone America/New_York 

That is assuming you are in Eastern time zone. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 06:07 AM . Last Modified: ‎2024-02-15 12:06 AM

0 Likes
0
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:07 AM . Last Modified: ‎2024-02-15 12:06 AM

Hi,

Go to /etc and edit the file hostname. Once the file has been edited you will need to restart the VM. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 06:06 AM . Last Modified: ‎2024-02-15 12:07 AM

0 Likes
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:06 AM . Last Modified: ‎2024-02-15 12:07 AM

Hi,

You should install PCNS on each of the host. Configure host 1 with vCenter to allow vCenter to be powered down properly. Configure PCNS on hosts 2 & 3 as standalone. 

Reply

Link copied. Please paste this link to share this article on your social media post.

vx_it_apc
Crewman vx_it_apc
Crewman

Posted: ‎2021-07-08 06:07 AM . Last Modified: ‎2024-02-15 12:07 AM

0 Likes
0
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:07 AM . Last Modified: ‎2024-02-15 12:07 AM

Thanks, Bill. Do you know how I can change the time zone of the PCNS CentOS7 virtual appliance after the initial setup? The older virtual appliances had a splash screen for this, the newer ones do not

3/4 /2019 7:35 AM, Bill said:

Hi,

You should install PCNS on each of the host. Configure host 1 with vCenter to allow vCenter to be powered down properly. Configure PCNS on hosts 2 & 3 as standalone. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 06:07 AM . Last Modified: ‎2024-02-15 12:07 AM

0 Likes
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:07 AM . Last Modified: ‎2024-02-15 12:07 AM

Hi,

Sorry for the inconvenience. What version of PCNS appliance did you install? the latest version allow you to set the time zone when the OS first start up.  

QiJcOojnGx4T4Rmy%2FW3q7A%3D%3D.pngQiJcOojnGx4T4Rmy%2FW3q7A%3D%3D.png

to set the time zone from the command line the command is 

timedatectl set-timezone America/New_York 

That is assuming you are in Eastern time zone. 

Reply

Link copied. Please paste this link to share this article on your social media post.

vx_it_apc
Crewman vx_it_apc
Crewman

Posted: ‎2021-07-08 06:07 AM . Last Modified: ‎2024-02-15 12:06 AM

0 Likes
0
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:07 AM . Last Modified: ‎2024-02-15 12:06 AM

On 2/4/2019 2:40 PM, Bill said:

timedatectl set-timezone America/New_York 

This is exactly what I was looking for! I accidentally left the timezone setting on default for two of the virtual appliances, so I needed to change it without redeploying. 

Reply

Link copied. Please paste this link to share this article on your social media post.

vx_it_apc
Crewman vx_it_apc
Crewman

Posted: ‎2021-07-08 06:07 AM . Last Modified: ‎2024-02-15 12:06 AM

0 Likes
0
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:07 AM . Last Modified: ‎2024-02-15 12:06 AM

Bill  Do you know the best way to change the hostname displayed in the top right of the web page for the PCNS virtual appliances?

All three of mine are displaying "localhost" at the moment - I know there are files in /etc/hosts and /etc/sysconfig/network that I can edit, but I'd like to know if there is a better way to do it from the command line.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 06:07 AM . Last Modified: ‎2024-02-15 12:06 AM

0 Likes
0
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:07 AM . Last Modified: ‎2024-02-15 12:06 AM

Hi,

Go to /etc and edit the file hostname. Once the file has been edited you will need to restart the VM. 

Reply

Link copied. Please paste this link to share this article on your social media post.

vx_it_apc
Crewman vx_it_apc
Crewman

Posted: ‎2021-07-08 06:07 AM . Last Modified: ‎2024-02-15 12:06 AM

0 Likes
0
1625
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:07 AM . Last Modified: ‎2024-02-15 12:06 AM

On 2/5/2019 7:22 AM, Bill said:

Hi,

Go to /etc and edit the file hostname. Once the file has been edited you will need to restart the VM. 

Perfect. Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore