[PCNS] Shutdown a host failed

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • [PCNS] Shutdown a host failed
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:55 AM . Last Modified: ‎2024-03-13 04:31 AM

0 Likes
3
1376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:55 AM . Last Modified: ‎2024-03-13 04:31 AM

[PCNS] Shutdown a host failed

Hi all,

I followed the VMware user guide to configure PCNS settings.

Unfortunately, I cannot shutdown the VM host. Could anyone help me to resolve this problem?

Thanks!

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • pcns
  • shutdown
  • vmware
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:56 AM . Last Modified: ‎2024-03-13 04:31 AM

0 Likes
0
1374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:56 AM . Last Modified: ‎2024-03-13 04:31 AM

Hi,

I need to see the error.log file and the pcnsconfig.ini file to help. Also, where is PCNS installed now? Is the appliance installed, is running on VMware vMA, or is it still installed on the stand-along as in the screen shots? 

What I see from the screen shots is PCNS is starting the shutdown

01/22/2016	13:05:14	UPS has switched to battery power.
01/22/2016	13:08:14	UPS critical event: On Battery.
01/22/2016	13:08:15	Shutdown sequence started on Hosts ucphksvrvm00001.uch.local, ucphksvrvm00002.uch.local, ucphksvrvm00003.uch.local in response to UPS critical event: On Battery.
01/22/2016	13:08:15	Starting Maintenance Mode Task on Host ucphksvrvm00001.uch.local.
01/22/2016	13:08:15	Shutting down VMs on Host ucphksvrvm00001.uch.local.
01/22/2016	13:08:43	Starting Maintenance Mode Task on Host ucphksvrvm00003.uch.local.
01/22/2016	13:08:43	Shutting down VMs on Host ucphksvrvm00003.uch.local.
01/22/2016	13:08:43	Starting Maintenance Mode Task on Host ucphksvrvm00002.uch.local.
01/22/2016	13:08:43	Shutting down VMs on Host ucphksvrvm00002.uch.local.
01/22/2016	13:20:49	UPS is no longer running on battery power or output power has been turned on.

but I do not see PCNS commanding VCSA down and then powering down the hosts. I also do not see PCNS shutting down the OS it is running on if this was from a stand-alone Windows system. The error.log file should list what may have happened. 

When you have time test the shutdown again and I would like you to put PCNS into debug mode (see Kbase FA230514) for instruction on how to put PCNS into debug mode. After running the test send error.log , EventLog.txt and pcnsconfig.ini 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:55 AM . Last Modified: ‎2024-03-13 04:31 AM

0 Likes
0
1374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:55 AM . Last Modified: ‎2024-03-13 04:31 AM

Hi,

It would be helpful to see the error.log and pcnsconfig.ini files which is in the folder / directory PowerChute is installed to.

Also, is PowerChute running on a virtual machine vMA, Appliance, or stand-alone Windows system? I see in the screenshot that the PCNS icon is not associated with any of the hosts. I should see the PCNS icon similar to what I how I see VCSA icon associated with host ucphksvrvm00001.uch.local if PCNS is running on a VM. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:56 AM . Last Modified: ‎2024-03-13 04:31 AM

0 Likes
0
1374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:56 AM . Last Modified: ‎2024-03-13 04:31 AM

Hi Bill,

Yes. We tested the PCNS twice. The first time using VM and the second time using Physical Windows(Also called Standalone, am I right?) and the testing result are the same.

In addition, the uploaded screenshot is captured from Windows.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:56 AM . Last Modified: ‎2024-03-13 04:31 AM

0 Likes
0
1375
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:56 AM . Last Modified: ‎2024-03-13 04:31 AM

Hi,

I need to see the error.log file and the pcnsconfig.ini file to help. Also, where is PCNS installed now? Is the appliance installed, is running on VMware vMA, or is it still installed on the stand-along as in the screen shots? 

What I see from the screen shots is PCNS is starting the shutdown

01/22/2016	13:05:14	UPS has switched to battery power.
01/22/2016	13:08:14	UPS critical event: On Battery.
01/22/2016	13:08:15	Shutdown sequence started on Hosts ucphksvrvm00001.uch.local, ucphksvrvm00002.uch.local, ucphksvrvm00003.uch.local in response to UPS critical event: On Battery.
01/22/2016	13:08:15	Starting Maintenance Mode Task on Host ucphksvrvm00001.uch.local.
01/22/2016	13:08:15	Shutting down VMs on Host ucphksvrvm00001.uch.local.
01/22/2016	13:08:43	Starting Maintenance Mode Task on Host ucphksvrvm00003.uch.local.
01/22/2016	13:08:43	Shutting down VMs on Host ucphksvrvm00003.uch.local.
01/22/2016	13:08:43	Starting Maintenance Mode Task on Host ucphksvrvm00002.uch.local.
01/22/2016	13:08:43	Shutting down VMs on Host ucphksvrvm00002.uch.local.
01/22/2016	13:20:49	UPS is no longer running on battery power or output power has been turned on.

but I do not see PCNS commanding VCSA down and then powering down the hosts. I also do not see PCNS shutting down the OS it is running on if this was from a stand-alone Windows system. The error.log file should list what may have happened. 

When you have time test the shutdown again and I would like you to put PCNS into debug mode (see Kbase FA230514) for instruction on how to put PCNS into debug mode. After running the test send error.log , EventLog.txt and pcnsconfig.ini 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore