PCNS Multiple Configuration -- When does the stand-by unit kick in?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS Multiple Configuration -- When does the stand-by unit kick in?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:51 PM . Last Modified: ‎2024-03-07 02:21 AM

0 Likes
5
1177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:51 PM . Last Modified: ‎2024-03-07 02:21 AM

PCNS Multiple Configuration -- When does the stand-by unit kick in?

About the setup:
We have two identical UPS each connected to one of the redundant power supplies on our server.

What we want:
In the event of a power outage, we want one UPS to power our server until it's battery is low, then switch to the other UPS until it's battery is low, then gracefully shutdown.

My understanding:
In a Multiple Configuration with two UPS, one UPS is designated as "primary" and one as "stand-by".

The question:
Under what circumstances does the "stand-by" UPS begin supplying power?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • multiple_configuration
  • pcns
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:52 PM . Last Modified: ‎2024-03-07 02:21 AM

0 Likes
0
1177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:52 PM . Last Modified: ‎2024-03-07 02:21 AM

PCNS will not shutdown your system until it receives an on battery signal (or other specific event you have configured) from both UPSs.

The only three events that could happen to only one UPS, that will cause the server to shutdown, are mentioned [in this article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=3143].

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-30 06:51 PM . Last Modified: ‎2024-03-07 02:21 AM

0 Likes
0
1177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:51 PM . Last Modified: ‎2024-03-07 02:21 AM

hmm...You will need to install the PCNS software through a Custom Installation in order to achieve your goal.

Custom:
PCNS is installed and listens for UPS events from two or more Network Management Cards.
Designed for graceful, unattended shutdown with redundant UPS systems.
PCNS treats all UPS units as one, meaning shutdown will not occur unless both UPS units switch to battery or report an event that requires shutdown.

A custom installation requires:
Two UPS units of the same product family (ie. Smart UPS)
Matching firmware on all Network Management Cards being monitored.

Regarding your question, the Server which has got dural power supplies will pull power from the standby UPS after the primary UPS stops providing power to it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:52 PM . Last Modified: ‎2024-03-07 02:21 AM

0 Likes
0
1177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:52 PM . Last Modified: ‎2024-03-07 02:21 AM

Thanks for the reply.

Does this mean the stand-by unit will not supply power until the primary unit signals low battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-30 06:52 PM . Last Modified: ‎2024-03-07 02:21 AM

0 Likes
0
1176
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:52 PM . Last Modified: ‎2024-03-07 02:21 AM

In this situation, the second UPS power will not be utilized until the first UPS stops power to its outlets due to low battery condition. Have you tried installing the PCNS through the custom installation?

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 06:52 PM . Last Modified: ‎2024-03-07 02:21 AM

0 Likes
0
1177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:52 PM . Last Modified: ‎2024-03-07 02:21 AM

In addition to what other people have said, it's your redundant power supplies that determine how they want to utilize the UPSes. If they draw power from both equally, then your UPSes will drain at the same time. If only one power supply is utilized at a time, then it will drain one UPS, then when the UPS shuts off, switch to the other power supply and UPS.

From the perspective of the UPS, it doesn't matter which of those scenarios occur. Your runtime should be about the same, and by following the advice of the other posters, you'll have PCNS set up so that it only shuts down your server when the amount of time left on the batteries of both of your UPSes is too low.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:52 PM . Last Modified: ‎2024-03-07 02:21 AM

0 Likes
0
1178
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:52 PM . Last Modified: ‎2024-03-07 02:21 AM

PCNS will not shutdown your system until it receives an on battery signal (or other specific event you have configured) from both UPSs.

The only three events that could happen to only one UPS, that will cause the server to shutdown, are mentioned [in this article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=3143].

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of