PCNS Insufficient Runtime Available

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS Insufficient Runtime Available
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
114
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:34 AM . Last Modified: ‎2024-03-05 12:35 AM

0 Likes
10
4516
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:34 AM . Last Modified: ‎2024-03-05 12:35 AM

PCNS Insufficient Runtime Available

Hello. I have a Smart UPS RT3000XL with Firmware v4.1 and:

Application Module

Name: sumx

Version: v3.5.5

APC OS (AOS)

Name: aos

Version: v3.5.5

Thing is Im getting the event "Available Runtime Has Been Exceeded" on only two servers, out of six. Im having to disable the shutdown event on "Runtime Exceeded" or else this servers shutdown. On the Managment Card, I see no log of this event. Im attaching some screenshots.

Ive uninstall PCNS, removed the Client from the UPS, restarted the Management Card, with no luck. ¿Any ideas?

Thanks.

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:35 AM . Last Modified: ‎2024-03-05 12:34 AM

0 Likes
0
4515
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:35 AM . Last Modified: ‎2024-03-05 12:34 AM

Your low battery duration is set for 1 minute. That indicates that condition 1 as described in the help file would be the cause.

When the total shutdown time required by PowerChute is greater than

the Low Battery Duration configured for the UPS. In the event of a low

battery condition, PowerChute will not have enough time to complete the

shutdown sequence before the UPS powers off.

Resolution:

Increase the Low Battery Duration value on the NMC using Configure -

Shutdown or decrease the shutdown delays being used by PowerChute.


See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:34 AM . Last Modified: ‎2024-03-05 12:35 AM

0 Likes
0
4515
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:34 AM . Last Modified: ‎2024-03-05 12:35 AM

Hi,

What version of PowerChute are you running and on what OS? Also, please send copies of the PCNS event log and the NMC event log.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:34 AM . Last Modified: ‎2024-03-05 12:34 AM

0 Likes
0
4517
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:34 AM . Last Modified: ‎2024-03-05 12:34 AM

OS: Windows Server 2008 R2, mainly.

APC OS: 3.5.5

UPS Firmware: 4.1

PCNS: 3.1 Build 4512

In the attachment "events_description_help" is the help file description on "Available Runtime Has Been Exceeded". Let me explain why neither of the two conditions described are our scenario:

Maximum Required Delay: 10 minutes

Low Battery Duration: 12 minutes

Shutdown Delay: 1 minute

Runtime Remaining: 26 minutes

Condition 1:

The event "Available Runtime Has Been Exceeded" should be present if the "Maximum Required Delay" is greater than the "Low Battery Duration". 10 minutes is not greater than 12 minutes. This event is not our scenario.

Condition 2:

When the "Shutdown Delay" configured for the UPS On Battery plus the total shutdown time required by PowerChute is greater than the "Runtime Remaining" minus 2 minutes. 1 minute + 10 minutes = Not greater than 26 minutes. Condition 2 is not our scenario.

But, we are still getting the events "Available Runtime Has Been Exceeded", as shown in the attachement "avilable_runtime_exceeded_events". We also notice this behaviour on another UPS of ours. Is this a reported/unreported bug or am I still not understanding something?

Thanks.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:35 AM . Last Modified: ‎2024-03-05 12:34 AM

0 Likes
0
4517
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:35 AM . Last Modified: ‎2024-03-05 12:34 AM

Hi,

The issue may be being caused by the available runtime on the UPS fluctuating. Change the data logging interval on the NMC to 1 minute for a period of time to see if the runtime is changing.

Another thing you should do is upgrade the NMC firmware to 3.7.2 I don't see any known issue with the firmware but to be safe getting theNMC upgraded to the latest make sense.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:35 AM . Last Modified: ‎2024-03-05 12:34 AM

0 Likes
0
4517
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:35 AM . Last Modified: ‎2024-03-05 12:34 AM

Well, we upgraded the firmware to the latest version, configured an event that sends an email on "Maximum Required Delay" fluctuation and changed the logging interval... we are still having fluctuations on the "Maximum Required Delay". Thing is that the "Maximum Required Delay" never goes over the "Available Runtime Remaining". Its either less time or the same, but never above. ¿Any ideas?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:35 AM . Last Modified: ‎2024-03-05 12:34 AM

0 Likes
0
4517
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:35 AM . Last Modified: ‎2024-03-05 12:34 AM

Hi,

What was recorded in the data log?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:35 AM . Last Modified: ‎2024-03-05 12:34 AM

0 Likes
0
4517
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:35 AM . Last Modified: ‎2024-03-05 12:34 AM

Hello. I have a Smart UPS RT3000XL with Firmware v4.1 and:

Application Module

Name: sumx

Version: v3.5.5

APC OS (AOS)

Name: aos

Version: v3.5.5

Thing is Im getting the event "Available Runtime Has Been Exceeded" on only two servers, out of six. Im having to disable the shutdown event on "Runtime Exceeded" or else this servers shutdown. On the Managment Card, I see no log of this event. Im attaching some screenshots.

Ive uninstall PCNS, removed the Client from the UPS, restarted the Management Card, with no luck. ¿Any ideas?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:35 AM . Last Modified: ‎2024-03-05 12:34 AM

0 Likes
0
4517
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:35 AM . Last Modified: ‎2024-03-05 12:34 AM

Some helpful information is available within the PCNS help file for this. Go to PCNS 3.1 and then navigate to Help->Help Contents and select PowerChute Events and Logging-> and Configurable Events under that within the box that pops up. This "Available Runtime Has Been Exceeded" is explained as the first event on the list.

If this does not help, we may need to know how much runtime your UPS reports as well as your PowerChute Network Shutdown configuration file (pcnsconfig.ini - located in the install path or group1 directory).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:35 AM . Last Modified: ‎2024-03-05 12:34 AM

0 Likes
0
4517
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:35 AM . Last Modified: ‎2024-03-05 12:34 AM

Thanks, Angela. Ive read the help file, but its not my case. Here are a couple of snapshots of the UPS status and configuration. Also, the pcnsconfig.ini.

What seems weird, at least to my understanding, is that only two out of six servers are getting the event. Last friday we simulated a power outage and every server got the event at the same time. ¿Do I have a wrong concept?

Mauro.

Attachments
pcnsconfig.ini.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:35 AM . Last Modified: ‎2024-03-05 12:34 AM

0 Likes
0
4516
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:35 AM . Last Modified: ‎2024-03-05 12:34 AM

Your low battery duration is set for 1 minute. That indicates that condition 1 as described in the help file would be the cause.

When the total shutdown time required by PowerChute is greater than

the Low Battery Duration configured for the UPS. In the event of a low

battery condition, PowerChute will not have enough time to complete the

shutdown sequence before the UPS powers off.

Resolution:

Increase the Low Battery Duration value on the NMC using Configure -

Shutdown or decrease the shutdown delays being used by PowerChute.


Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:35 AM . Last Modified: ‎2024-03-05 12:34 AM

0 Likes
0
4517
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:35 AM . Last Modified: ‎2024-03-05 12:34 AM

That did the trick. Seems Im not getting the procedure all that clear. Will have to read and test a bit more. Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of