PCNS Command file path not accepted
Hello,
i have a very strange problem. I have tried to run a command file for shutting down the netapp but as you can see in the image the folder i use is not accepted. Everything seems ok but i don't know what is it's problem.
I have installed PowerChute 4.4 and i didn't find anything on bugs.
You should verify the file custom_script.sh is an executable. To do so log into the PowerChute VM. Go to the user-files directory and enter the command ls -la If custom_script.sh is not listed as -rwxr-xr-x for permissions enter chmod +x custom_script.sh