PCNS Advice Needed Please - VMware integration in a HA Cluster Environment

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS Advice Needed Please - VMware integration in a HA Cluster Environment
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 01:51 AM . Last Modified: ‎2024-02-29 10:29 PM

0 Likes
4
1989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:51 AM . Last Modified: ‎2024-02-29 10:29 PM

PCNS Advice Needed Please - VMware integration in a HA Cluster Environment

Hi all,

I am currently in the process of configuring PCNS for our environment.  I have setup all my physical Windows servers how I want them, but I am struggling to work out the best thing to do for our virtual environment.  We have the following environment:

2 x HA Clusters (each cluster consisting of 3 x hosts)

vCenter is a running on a VM

PCNS (with the VMWare integration) is installed on physical Windows server

From what I understand, it is NOT possible to gracefully shutdown and/or restart VM's in an HA cluster environment and it needs to be scripted.

Is this correct?  What about just shutting down?  Is it possible to automate the graceful shutting down as this is more important to us than the restarting?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • pcns
  • PowerChute
  • software
  • vmware
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:51 AM . Last Modified: ‎2024-02-29 10:29 PM

0 Likes
0
1986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:51 AM . Last Modified: ‎2024-02-29 10:29 PM

Hi,

On 11/10/2015 4:53 AM, Mike said:

I have read so much about the necessity to enable "virtual machine startup/shutdown" on the hosts, but this is greyed out (by design) in a HA cluster environment.

Startup/shutdown are grayed out on the host when a host is part of a HA cluster. VMware designed the system to do that with the understanding that VMs would be migrated to a new host and therefore would not need to be powered down.

Starting with PCNS 3.1 PowerChute can be configured to shutdown/startup the VMs. Beginning with PCNS version 4.1 VM shutdown/startup can be prioritized. VM Shutdown/Startup is discussed beginning on page 32 of the User's guide and prioritization is discussed starting on page 38.

NOTE: each VM must have VMware tools installed to enable PowerChute to shut it down and start it up. 

On 11/10/2015 4:53 AM, Mike said:

Also, will PCNS automatically restart the hosts > VMs > vCenter VM when power is restored?

PowerChute will restart the VMs and vCenter. Since PowerChute is off just like any other software application it cannot restart the host. To have the host restart when AC is restored you must configure PowerChute to shutdown the UPS after all the VMs, and host are powered off and configure the BIOS of each of the host to restart when AC is restored. This way the UPS cuts power to its outlets and when AC is restored will restore power to the outlets. When the UPS restores AC the computers BIOS will see that AC has been restored and the hosts will restart. Once the hosts are restarted PowerChute will restart vCenter and then the VMs. 

Host shutdown is discussed starting on page 19 of the User's Guide.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:51 AM . Last Modified: ‎2024-02-29 10:29 PM

0 Likes
0
1986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:51 AM . Last Modified: ‎2024-02-29 10:29 PM

Mike,

PowerChute will shutdown and restart VMs in a HA cluster and it is possible to prioritize the shutdown and start up of the VMs. Basically PowerChute shuts down the VMs, then vCenter, then the hosts, and finally the system PowerChute is running on.

Please review Application note 180  and PowerChute VMware User's Guide.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:51 AM . Last Modified: ‎2024-02-29 10:29 PM

0 Likes
0
1986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:51 AM . Last Modified: ‎2024-02-29 10:29 PM

Hi Bill,

Thanks for your reply.  Application note 180 is very useful

I have read so much about the necessity to enable "virtual machine startup/shutdown" on the hosts, but this is greyed out (by design) in a HA cluster environment.

Is this something that is different between 4.0 and 4.1 and is no longer necessary to enable this feature?

Also, will PCNS automatically restart the hosts > VMs > vCenter VM when power is restored?

Also - apologies for my lack of space bar skills!  Not sure what is going on there!

  • Tags:
  • vmware
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:51 AM . Last Modified: ‎2024-02-29 10:29 PM

0 Likes
0
1987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:51 AM . Last Modified: ‎2024-02-29 10:29 PM

Hi,

On 11/10/2015 4:53 AM, Mike said:

I have read so much about the necessity to enable "virtual machine startup/shutdown" on the hosts, but this is greyed out (by design) in a HA cluster environment.

Startup/shutdown are grayed out on the host when a host is part of a HA cluster. VMware designed the system to do that with the understanding that VMs would be migrated to a new host and therefore would not need to be powered down.

Starting with PCNS 3.1 PowerChute can be configured to shutdown/startup the VMs. Beginning with PCNS version 4.1 VM shutdown/startup can be prioritized. VM Shutdown/Startup is discussed beginning on page 32 of the User's guide and prioritization is discussed starting on page 38.

NOTE: each VM must have VMware tools installed to enable PowerChute to shut it down and start it up. 

On 11/10/2015 4:53 AM, Mike said:

Also, will PCNS automatically restart the hosts > VMs > vCenter VM when power is restored?

PowerChute will restart the VMs and vCenter. Since PowerChute is off just like any other software application it cannot restart the host. To have the host restart when AC is restored you must configure PowerChute to shutdown the UPS after all the VMs, and host are powered off and configure the BIOS of each of the host to restart when AC is restored. This way the UPS cuts power to its outlets and when AC is restored will restore power to the outlets. When the UPS restores AC the computers BIOS will see that AC has been restored and the hosts will restart. Once the hosts are restarted PowerChute will restart vCenter and then the VMs. 

Host shutdown is discussed starting on page 19 of the User's Guide.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:51 AM . Last Modified: ‎2024-02-29 10:29 PM

0 Likes
0
1987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:51 AM . Last Modified: ‎2024-02-29 10:29 PM

Excellent - thank you very much for all your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of