PCNS_4.1; PowerChute cannot locate the vCenter Server VM in the Inventory

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS_4.1; PowerChute cannot locate the vCenter Server VM in the Inventory
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:13 AM . Last Modified: ‎2024-03-13 01:42 AM

0 Likes
4
2429
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:13 AM . Last Modified: ‎2024-03-13 01:42 AM

PCNS_4.1; PowerChute cannot locate the vCenter Server VM in the Inventory

We just installed a new SRT5kRMXLT UPS. We have 5 ESXi servers connected to the unit. I installed PowerChute 4.1 Network Shutdown VM to manage shutting down the VM's, and then the ESXi host as well. During the configuration of PowerChute I get this error message: "PowerChute cannot locate the vCenter Server VM in the Inventory.". It is true that I did select 4 servers during configuration of PowerChute, none of these servers are hosting the vCenter VM. The server running vCenter is not listed in our Data Store as a host. Incidentally, the same server running vCenter VM is also running PowerChute VM. Is this a requirement of PowerChute to have all servers listed in the Data Store? I would think PowerChute would contact vCenter by IP. We also do not use a domain in our environment. I have not upgraded the ESXi host running vCenter to version 6.0 just yet but vCenter at version 6.0. 

Ideas?

Kristen

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:13 AM . Last Modified: ‎2024-03-13 01:42 AM

0 Likes
0
2429
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:13 AM . Last Modified: ‎2024-03-13 01:42 AM

Frank,

The options are

1 - Run PCNS and VCSA on standalone Windows server 

2 - Run PCNS on standalone Windows server and VCSA on a host that is included in the cluster

3 - Run PCNS and VCSA on a host that is included in the cluster

In your set up you should follow the set up on page 4 of Application Note 180. 

I will ask that the User's Guide get update to state the need for VCSA to be running on a host that is a member of a protected cluster or as Kristen did add the host running VCSA to the data store. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:13 AM . Last Modified: ‎2024-03-13 01:42 AM

0 Likes
0
2429
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:13 AM . Last Modified: ‎2024-03-13 01:42 AM

Hi,

Open the PCNS web interface and go to Communications Settings. Enter the IP address, user name, and password for vCenter Server, select vCenter Server is running on a VM and then click apply. PCNS will attempt to connect to vCenter Server. Assuming PCNS is able to connect if the error continues verify that VMware tools are install on the vCenter Server VM. 

in the above example vCenter server is running on host luna.scvmmgal.net and PCNS is running on sol.scvmmgal.net If vmware tools are not installed on vCenter Server the host running it will not be signified with the VMware icon. 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:13 AM . Last Modified: ‎2024-03-13 01:42 AM

0 Likes
0
2429
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:13 AM . Last Modified: ‎2024-03-13 01:42 AM

The instructions you provide have been followed and completed. I double checked as well. The server that runs vCenter VM is 192.168.130.18. As you can see, that server is not in the list below. 

I did try to update VMware Tools on the vCenter VM by logging on to the ESXi host. But that attempt gave a useless error. The image below shows that vCenter is managed by another tool set. I do not think you can update vCenter with its own VM tool set.

I resolved the issue by adding the host vCenter runs on to the Data Store. Now the server shows up to be added for host protection. 

Thanks for your assistance

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:13 AM . Last Modified: ‎2024-03-13 01:42 AM

0 Likes
0
2429
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:13 AM . Last Modified: ‎2024-03-13 01:42 AM

I get the same error message "PowerChute cannot locate the vCenter Server VM in the Inventory"

We have 3x ESXi server in a cluster.

We are running the vCenter server appliance and the PCNS 4.1 appliance on a different ESXi host ("standalone") that is not part of the cluster.

Is it recommended (or mandatory) to have the vCenter server appliance and the PCNS 4.1 appliance on the cluster ?

Will the VM shutdown work if the vCenter server appliance and/or the PCNS 4.1 appliance is on a different ESXi host?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:13 AM . Last Modified: ‎2024-03-13 01:42 AM

0 Likes
0
2430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:13 AM . Last Modified: ‎2024-03-13 01:42 AM

Frank,

The options are

1 - Run PCNS and VCSA on standalone Windows server 

2 - Run PCNS on standalone Windows server and VCSA on a host that is included in the cluster

3 - Run PCNS and VCSA on a host that is included in the cluster

In your set up you should follow the set up on page 4 of Application Note 180. 

I will ask that the User's Guide get update to state the need for VCSA to be running on a host that is a member of a protected cluster or as Kristen did add the host running VCSA to the data store. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore