PCNS 3.0.0 takes 10 minutes for console to start

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS 3.0.0 takes 10 minutes for console to start
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:05 AM . Last Modified: ‎2024-03-06 02:09 AM

0 Likes
5
1492
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:05 AM . Last Modified: ‎2024-03-06 02:09 AM

PCNS 3.0.0 takes 10 minutes for console to start

I'm a little frustrated that APC support wasn't very helpful in this issue, so I'm posting it here in hopes someone else has run into the same issue.

The problem is that when the PCNS service is started, it takes over 10 minutes before the console is available via HTTP or HTTPS. There are no apparent errors in the Windows event logs, and the taskmanager shows very little CPU use. For 10 minutes, there just appears to be nothing happening, and netstat shows that the listening ports for 3052 and 6547 have not been opened. Then after that 10 minutes, suddenly the ports are listening and the console is available.

I'm frustrated trying to figure out what is going on with this, and APC support didn't really understand the problem at all. I'd appreciate if anyone can provide some suggestions.

Environment:
Server 2008 R2 Standard
JRE 6_25 (manually installed)
PCNS 3.0.0
SMX3000RMLV2UNC

Thanks in advance!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • 2008
  • 3
  • 3.3.0
  • pcns
  • r2
  • v3
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:06 AM . Last Modified: ‎2024-03-06 02:08 AM

0 Likes
0
1491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:06 AM . Last Modified: ‎2024-03-06 02:08 AM

ok..got a few more questions.

you start the service - this seems as though its reproducible all the time? after a reboot, manually, starting/stopping, correct?

also, when you start the PCNS service and then check the PCNS event log when you are able to access the software - is the time stamp for the entry PowerChute Network Shutdown version 3.0.0 started indicating it started when you actually start the service (before the 10-15 min access delay) or is the time stamp for that event indeed 10-15 minutes later when the service becomes available?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:06 AM . Last Modified: ‎2024-03-06 02:08 AM

0 Likes
0
1491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:06 AM . Last Modified: ‎2024-03-06 02:08 AM

I think I just identified the problem....

The server has a dual Gb NIC, but only one is connected and in use. The other interface is still enabled, even though it's not connected. I disabled the unused interface in Windows and the PCNS console immediately came up. I restarted it again to be sure, and again the startup was immediate. I also re-ran the configuration wizard, which then registered the proper IP address for the NIC interface, rather than the default 127.0.0.1 for locahost.

It would appear as though PCNS was completely thrown off by the one disconnected NIC interface, even though the other interface was up and running just fine.

Thanks for your help! Also, if you have any insights into why this was happening, I'm sure it would be helpful to others down the road, or to APC for correcting that in future releases.

Message was edited by: cosadmin

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:06 AM . Last Modified: ‎2024-03-06 02:08 AM

0 Likes
0
1492
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:06 AM . Last Modified: ‎2024-03-06 02:08 AM

ah ok well ill pass it along like you said incase it comes up. thanks for reporting back with your fix.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:06 AM . Last Modified: ‎2024-03-06 02:08 AM

0 Likes
0
1491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:06 AM . Last Modified: ‎2024-03-06 02:08 AM

just to clarify - in this 10 minute time period, does the service actually indicate its started or does the progress bar show its still trying to start the service? from what you say it seems like the service starts within 10-15 seconds as it should and then indicates Started but is not accessible via the web browser. are you checking this on the server itself or remotely via IP address on a different computer? what does the event log in PCNS say if you access PCNS when it is running after encountering this issue?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:06 AM . Last Modified: ‎2024-03-06 02:08 AM

0 Likes
0
1492
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:06 AM . Last Modified: ‎2024-03-06 02:08 AM

Yes, the service IS fully started within the 10-15 seconds, but he console is unavailable. I'm accessing the console both locally, and remotely. Neither work. I've used netstat to confirm that the ports (3052, 6547) have not been opened.

When I can finally access PCNS, there was a log entry about not being able to communicate with the NMC, but I was able to correct that. Interestingly, when I re-ran the configuration wizard, it registered 127.0.0.1 with the NMC instead of it's actual IP address.

Also, this was an upgrade from PCNS 2.2.4 (which works fine). I've tried completely uninstalling PCNS and deleting it's directories from Program Files and Program Files (x86), then reinstalling from scratch. Same result. Have also tried both the included private JRE and installing the latest JRE manually from Sun.... nothing seems to change this startup problem.

Thanks,
DK

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:06 AM . Last Modified: ‎2024-03-06 02:08 AM

0 Likes
0
1492
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:06 AM . Last Modified: ‎2024-03-06 02:08 AM

ok..got a few more questions.

you start the service - this seems as though its reproducible all the time? after a reboot, manually, starting/stopping, correct?

also, when you start the PCNS service and then check the PCNS event log when you are able to access the software - is the time stamp for the entry PowerChute Network Shutdown version 3.0.0 started indicating it started when you actually start the service (before the 10-15 min access delay) or is the time stamp for that event indeed 10-15 minutes later when the service becomes available?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore