PCNS 3.0.0 does not accept special characters like ! and - in password

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS 3.0.0 does not accept special characters like ! and - in password
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 11:44 PM . Last Modified: ‎2024-02-14 11:39 PM

0 Likes
5
1650
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:44 PM . Last Modified: ‎2024-02-14 11:39 PM

PCNS 3.0.0 does not accept special characters like ! and - in password

I just installed PCNS 3.0.0 under SLES11SP1 today. Following the web-wizard, I entered all the required information including the UPS password. This password contains special characters like ! or -

I then tried to log into PCNS3 locally on the machine, it refused to take the username/password combination an locked me out.

I then reinstalled PCNS 3 with "test" as password to make sure I could log in at all. This worked and I was able to log in. I then tried to change this password from "test" to some simple words containing ! or - and it refused!

Are you seriously limiting passwords to letters and numbers ONLY?
I mean, if an attacker gets access to PCNS, he could easily shutdown the system! Thus, the passwords should be maximally secure...

Thanks for any help on this.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:44 PM . Last Modified: ‎2024-02-14 11:39 PM

0 Likes
0
1650
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:44 PM . Last Modified: ‎2024-02-14 11:39 PM

This is completely unacceptable behavior from this software. Complex passwords are a requirement these days.

The fact that this software made it out for public consumption shows a complete disregard for your customer's systems security, and a complete disregard for the quality of the products you create.

APC should be ashamed that this made it past QA.

There are TONS of UPS vendors on the market these days. I assure you if this is the quality we can come to expect from APC in the future, there are MANY other vendors that will take our money for power protection.

After using APC products for a decade, I'm extremely disappointed in what appears to be a very amateurish product design.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:44 PM . Last Modified: ‎2024-02-14 11:39 PM

0 Likes
0
1650
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:44 PM . Last Modified: ‎2024-02-14 11:39 PM

Good day endzone,

Sorry about the inconvenience but the PowerChute Network Shutdown (PCNS) password does not allow special characters like ! or @. The only acceptable characters are:

o the alphabet in both lowercase and uppercase (a to z and A to Z),
o numbers from 0 to 9,
o and the underscore (underline) character.

Kindly look into [this document|http://nam-en.apc.com/app/answers/detail/a_id/11382/kw/11382] that addresses the concern you have with the password.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 11:44 PM . Last Modified: ‎2024-02-14 11:39 PM

0 Likes
0
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:44 PM . Last Modified: ‎2024-02-14 11:39 PM

First of all, thank you very much for the quick reply! It's great that there is a KB article about the issue.

As far as I remember, 2.2.4 DID allow these characters in passwords, so you are forcing your customers to change their existing passwords (possibly on a large number of UPSes/servers) due to a software problem! To be honest, this is simply unacceptable. I would NOT have installed version 3.0.0 if I had known about this issue before the installation.

So, whatever technical reasons it might have, please consider allowing special characters again in the next release.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:44 PM . Last Modified: ‎2024-02-14 11:39 PM

0 Likes
0
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:44 PM . Last Modified: ‎2024-02-14 11:39 PM

I completely understand and I'd like to apologize if we currently have no solution available at the moment, but I'm sure that our engineers are working on this and it'll be addressed in a future release. As of the moment we currently have no ETAs for the update so please check the website regularly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 11:44 PM . Last Modified: ‎2024-02-14 11:39 PM

0 Likes
0
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:44 PM . Last Modified: ‎2024-02-14 11:39 PM

Hi... sry... but: big fat lol?

I've got the same Problem... but our company password policy DONT allow such low security passwords.

You're kidding me eh? Do u want to tell our Security Officer pls: "sry, Ur Admins can use secure Passwords with the NEW software, because the older one could, so... !!!!! happens".


I hope there will be an update soon... very soon... im sorry, but... i cant find other words for that than: lol...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:44 PM . Last Modified: ‎2024-02-14 11:39 PM

0 Likes
0
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:44 PM . Last Modified: ‎2024-02-14 11:39 PM

This is completely unacceptable behavior from this software. Complex passwords are a requirement these days.

The fact that this software made it out for public consumption shows a complete disregard for your customer's systems security, and a complete disregard for the quality of the products you create.

APC should be ashamed that this made it past QA.

There are TONS of UPS vendors on the market these days. I assure you if this is the quality we can come to expect from APC in the future, there are MANY other vendors that will take our money for power protection.

After using APC products for a decade, I'm extremely disappointed in what appears to be a very amateurish product design.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore