PCNS @ vMA + ESXi

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS @ vMA + ESXi
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-08 11:42 PM . Last Modified: β€Ž2024-02-14 11:40 PM

0 Likes
18
4441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-08 11:42 PM . Last Modified: β€Ž2024-02-14 11:40 PM

PCNS @ vMA + ESXi

Hello together

At the moment I'm trying to get this to work but as you can imagine it won't work.

Test situation:

1 ESXi host with installed license!
1 vMA-4.1.0.0-268837
2 SmartUPS 2200

I installed the vMA and on top "PCNS224_VIMA41".
I configured PCNS for multiple devices.
I added the ESXI host as target via vifp addserver
I configured the ESXi to shutdown/start VMs with the host.
The PCNS software has registered successfully on both UPS management cards.
The communication seems to work. If I unplug the power cables the PCNS EventLog.txt sais:

PowerChute Network Shutdown version 2.2.4 started
Management Card 192.168.251.208 communication has been established
Management Card 192.168.251.207 communication has been established
Communications have been established
.
.
.
UPS 192.168.251.207 is running on battery power.
UPSs have switched to battery power
Shutdown process started. Linux will shut down soon.
Multiple Critical Event occurred: OnBattery, UPSTurnOffInitiated
Multiple UPS turn offs have been initiated.
and so on ...

BUT nothing happens.
It seems that the ESXi gets no shutdown signal, at least I can't see anything in the ESXi's log.

Maybe there is a Problem with the shutdownhost.pl in /opt/APC/Powerchute/group1/bin

if run it manually ./shutdownhost.pl

Can't load '/usr/lib/perl5/site_perl/5.8.8/libvmatargetlib_perl.so' for module vmatargetlib_perl: libtypes.so: cannot open shared object file: No such file or directory at /usr/lib64/perl5/5.8.8/x86_64-linux-thread-multi/DynaLoader.pm line 230.
at /usr/lib/perl5/site_perl/5.8.8/VMware/VmaTargetLib.pm line 10
Compilation failed in require at /usr/lib/perl5/site_perl/5.8.8/VMware/VIFPLib.pm line 10.
BEGIN failed--compilation aborted at /usr/lib/perl5/site_perl/5.8.8/VMware/VIFPLib.pm line 10.
Compilation failed in require at ./shutdownhost_o.pl line 16.
BEGIN failed--compilation aborted at ./shutdownhost_o.pl line 16.

I found a Solution for that in the VMware community:

I changed the name of the shutdownhost.pl to shutdownhost_o.pl
I created a new script called shutdownhost.pl.

#!/bin/bash
#
LD_LIBRARY_PATH=/opt/vmware/vma/lib64:/opt/vmware/vma/lib
export LD_LIBRARY_PATH
PATH=/usr/kerberos/bin:/usr/local/bin:/bin:/usr/bin:/usr/java/jre-vmware/bin:/sbin:/usr/sbin:/home/vi-admin/bin
export PATH
/opt/APC/PowerChute/group1/bin/shutdownhost_o.pl

Now the scripts runs but it seems that there are some operations/parameters missing. Maybe PCNS adds them if it calls the script.

Any ideas?
Are there some additional logs where I can see what's probably wrong?

Regards
Patrick

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • esxi
  • pcs
  • shutdownhost.pl
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-07-08 11:44 PM . Last Modified: β€Ž2024-02-14 11:39 PM

0 Likes
0
4441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-08 11:44 PM . Last Modified: β€Ž2024-02-14 11:39 PM

JonPro wrote:
Are you using the paid version of VMWare and have you tried PCNS 3.0?
We're using the free version of ESXi. I haven't tried PCNS 3.0. So it is your recommendation to do this next?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 18
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

0 Likes
0
4442
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

Good morning

No haven't tried version 3.0 yet.
And just on a vMA.

Message was edited by: Patrick1

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

0 Likes
0
4444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

Thanks for the heads up.

Is it possible for us to try this on PowerChute Network Shutdown 3.0?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

0 Likes
0
4444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

Hello,

I am having the same exact error in PCNS 3.0.0

Scenario:
APC UPS with a NIC.
ESXi 4.1 U1 installed on a HP server. License is vSphere Essentials Kit.
vMA 4.1 installed on the ESXi host.
APC PowerChute Network Shutdown installed on vMA, [following these instructions, starting on p.6 bottom|http://www.apcmedia.com/salestools/PMAR-8EMDEM_R0_EN.pdf]
This was all set up ~1mo. ago with latest available software.

We tested this setup by simulating a power outage. ESXi did not shut down gracefully, it just lost power, as if it never received the shutdown command from PCNS.
I learned from [this page|http://blog.rebelit.net/?p=118] that you can trigger the shutdown command by executing the shutdown script manually. I get errors when I execute it -- see attached file.

There are 3 files in that directory: notifier, shutdown, and shutdown.pl. Is my syntax correct? Am I executing the right file?
I edited the 'shutdown' file -- see attached file. (the PCNS instructions don't include this)

I have triple-checked all APC NIC and PCNS settings, they all seem correct. Why is the perl script erroring out?

If you need any more info on the environment let me know. Thank you.

Crossposted to VMWare forums here: http://communities.vmware.com/message/1778053

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

0 Likes
0
4444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

Hello again

Your linked procedure is pre installation, isn't it?
I'll give it a try.
And for us it doesn't matter if we use 2.2.4 or 3.0, it only has to work properly πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

0 Likes
0
4444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

Patrick,

If you wish to proceed on using PCNS 2.2.4, please follow the steps outlined on this APC Knowledgebase.

[Procedure for running PCNS 2.2.4 installtion patch on VMware vMA 4.1|http://nam-en.apc.com/app/answers/detail/a_id/11144/kw/11144]

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

0 Likes
0
4444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

by the way ... who's right, PCNS installation or the knowledgebase?
The knowledgebase says:

sudo cp shutdown /opt/APC/PowerChute/group1/bin/shutdown

but the scripts is called shutdown.pl

Message was edited by: Patrick1

Message was edited by: Patrick1

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

0 Likes
0
4444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

Meanwhile I tried PCNS3.0 on Windows 7 x64 with two UPS and one ESXi 4.1 host.

It works!

If both UPS are on battery, PCNS launches a PowerCLI script which sends a shutdown command to the ESXi. ESXi waits xxx seconds to shutdown guests properly and then itself.

Maybe I'll try the vMA solution again.

For PCNS 2.2.4 I got a download link from the APC support for a vMA edition.
With PCNS 3.0 what version is the right one? for Linux or ESXi?

Regards

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

0 Likes
0
4444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

Good morning

//Edit:

Finally I got it πŸ™‚

The file "shutdown" from the patch does what I already mentioned in my first post.

#!/bin/sh

# Patch for PCNS-1635
LD_LIBRARY_PATH=$LD_LIBRARY_PATH:/opt/vmware/vma/lib64:/opt/vmware/vma/lib
export LD_LIBRARY_PATH

perl *./bin/shutdownhost.pl* operation shutdown username xxxxx --password xxxxx


1. So you just can run shutdown if you copy it to /opt/APC/PowerChute/group1 or edit the path to ./shutdownhost.pl if both scripts are located in the bin dir.
2. You better don't touch the original shutdownhost.pl πŸ™‚

But now it works also with vMA and PCNS 2.2.4 + Patch

But will PCNS on vMA directly use this script if I configure "Shut Down System" or do I need to use "Run Command File" and call the shutdown script?


Regards




Regards
Patrick

Message was edited by: Patrick1

Message was edited by: Patrick1

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

0 Likes
0
4444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

I haven't tried it personally but most of our customers who followed the kbase that I gave you got it working. With regards to PCNS 3.0, this is the first time that I've encountered the issue that was posted above.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

0 Likes
0
4444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

Are you using the paid version of VMWare and have you tried PCNS 3.0?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

0 Likes
0
4444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

That's good to hear Patrick.

Just a reminder the script that comes from APC/PCNS should never be edited or changed. If a customer edits our script, we will not be supporting it.

PowerChute Network Shutdown calls the script shutdown and that calls shutdownhost.pl he does not need to do anything as long as he copies the shutdown script to the proper place as indicated in the APC Knowledgebase Article.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

0 Likes
0
4445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:40 PM

JonPro wrote:
PowerChute Network Shutdown calls the script shutdown and that calls shutdownhost.pl he does not need to do anything as long as he copies the shutdown script to the proper place as indicated in the APC Knowledgebase Article.
I believe this is not correct. The script "shutdown" points to ./bin/shutdownhost.pl but it already lies in the "bin" folder, together with "shutdownhost.pl".

Edit: Of course, if the "shutdown" script is executed in the folder "group1", this may work...

Message was edited by: blub

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:39 PM

0 Likes
0
4445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:39 PM

I'm experiencing almost exactly the same problem as user Patrick1, so I don't open a new thread.

I have set up ESXi 4.1 with (patched) PCNS 2.2.4. The ESXi is visible when issuing a "sudo vifp listservers". Everything seems to be communicating, calling the shutdown script manually also gives a message

Connecting to server localhost ...
Operation :shutdown
Version on xxx.xxx.xxx.xxx:
----------------------------------------

Folder :host
Host :
Shutting down host

but nothing happens.

Is calling the shutdown script trough the shell an appropriate way for testing the ability to shut down?

Is there something additional that must be done to enable the communication between PCNS and ESXi?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:39 PM

0 Likes
0
4445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:39 PM

Hi Lucky,

Unfortunately you will need to purchase a licensed copy of VMWare. We do have an APC Knowledgebase Articles regarding this .

[VMware ESXi server not shutting down when commanded to by PowerChute Network Shutdown.|http://nam-en.apc.com/app/answers/detail/a_id/10727/kw/paid%20vmware]

It also says it on the [PCNS Compatibility Chart|http://www.apcmedia.com/salestools/SJHN-7AYQNP_R25_EN.pdf]

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:39 PM

0 Likes
0
4445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-08 11:43 PM . Last Modified: β€Ž2024-02-14 11:39 PM

Hey there!

I know the thread is old, but the topic is still relevant to me.

Would PCNS work with the VMware vSphere Essentials Kit listed here http://www.vmware.com/products/datacenter-virtualization/vsphere/small-business/essentials-kits.html ? This seems to be the cheapest one (495$ + 65$), the others are too expensive for my budget. Prices are listed here: http://www.vmware.com/products/vsphere/pricing.html

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-08 11:44 PM . Last Modified: β€Ž2024-02-14 11:39 PM

0 Likes
0
4445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-08 11:44 PM . Last Modified: β€Ž2024-02-14 11:39 PM

Hi Patrick,

Have you tried using the latest PCNS 3.0? Also, do you have a viMA installed on the ESXi as well or just the vMA?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-08 11:44 PM . Last Modified: β€Ž2024-02-14 11:39 PM

0 Likes
0
4445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-08 11:44 PM . Last Modified: β€Ž2024-02-14 11:39 PM

That's good to hear Pat.

Here is the download page for PCNS 3.0, it is categorized by Operating System - [PCNS 3.0 Download|http://www.apc.com/tools/download/software_comp.cfm?sw_sku=SFPCNS300&id=127&family=127&part_num=SFPC...]

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-08 11:44 PM . Last Modified: β€Ž2024-02-14 11:39 PM

0 Likes
0
4442
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-08 11:44 PM . Last Modified: β€Ž2024-02-14 11:39 PM

JonPro wrote:
Are you using the paid version of VMWare and have you tried PCNS 3.0?
We're using the free version of ESXi. I haven't tried PCNS 3.0. So it is your recommendation to do this next?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore