Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

PCNS 2.2.4 Graceful Shutdown Process

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: PCNS 2.2.4 Graceful Shutdown Process
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
mcctech_apc
Ensign mcctech_apc
Ensign

Posted: ‎2021-06-30 07:48 PM

0 Likes
4
411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 07:48 PM

PCNS 2.2.4 Graceful Shutdown Process

This was originally posted on APC forums on 10/13/2010


Hi all,

SMX1500RM2UNC (AP9631 w/ v5.1.3 firmware)
PCNS 2.2.4 (win7 64bit)

I am currently in the process of testing PCNS shutdown behaviors and would like to know what I should expect from this particular combo.

If I specify the 'on battery' event to trigger a shutdown after 5 minutes and the option to turn off the UPS after the client has shutdown is enabled, I want to know what to expect and the time frames involved after the client OS has gracefully shutdown assuming no external commands are executed and 'shutdown delay = 10secs'.

Should the UPS turn off after the 5 min shutdown + 10seconds or are there other built-in timers that I should know about?

My concern is that if the UPS shutdown procedure has started and then power is restored and somebody decides to manually turn on a machine, that the shutdown procedure will continue to execute, thus the UPS and groups are reset taking the machine down with it and corrupting drive(s).

I basically want connected machines to shutdown gracefully via PCNS but then power-on again after power is restored without any human intervention. My understanding is that the 'shutdown UPS after' option must be enabled for this to happen (obviously the last machine to shutdown).

TIA.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • pcns
  • shutdown
  • timers
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
mcctech_apc
Ensign mcctech_apc
Ensign

Posted: ‎2021-06-30 07:48 PM

0 Likes
0
411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 07:48 PM

This was originally posted on APC forums on 10/13/2010


Yes, explains things perfectly, thanks! I just confirmed the entire shutdown process and now I am trying to get command execution working, but I will start a new thread about this.

See Answer In Context

Reply
Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:48 PM

0 Likes
0
411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 07:48 PM

This reply was originally posted by Angela on APC forums on 10/13/2010


check out the picture (from the PCNS help file) that is in [this knowledgebase article|http://nam-en.apc.com/app/answers/detail/a_id/10563] to help you understand what is expected.

that article doesnt have much to do with the question to asked but it has a good picture. alternatively, you can get the same image from the PCNS help file.

Reply
mcctech_apc
Ensign mcctech_apc
Ensign

Posted: ‎2021-06-30 07:48 PM

0 Likes
0
411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 07:48 PM

This was originally posted on APC forums on 10/13/2010


Thanks. Yeah, I saw that in the PCNS help file last week, but I was in the process of working out some other issues with tech support - bad PSU in the workstation was the blame.

So if I understand correctly from #4, the UPS begins its shutdown process by waiting the low battery duration (in my case set to 5 mins). Then a built-in 2 min wait timer has to expire. The UPS reboot process starts, and waits the shutdown delay (in my case set to 10 secs).

So is it correct in assuming that I am looking at 5 mins + 2 mins + 10 sec = 7mins 10 secs minimum waiting time for the UPS to turn off AFTER the machine gracefully shuts down?

Can you explain what happens if power is restored after the UPS shutdown process has begun? From a quick test last week, it would appear as if the shutdown process continued after power was restored, thus making it dangerous to manually turn on the box.

From a logic point of view, I guess this is the only way to ensure that the box which was shutdown actually turns back on.

comments/thoughts?

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:48 PM

0 Likes
0
411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 07:48 PM

This reply was originally posted by Angela on APC forums on 10/13/2010


hi - you are incorrect.

the entire shutdown process including when the UPS is shutting down in addtion to the time the server has to shutdown is the entire 7 minutes and 10 seconds.

based on what you told us, you only configured the low battery duration in the NMC from the default 2 minutes to 5 minutes. after that, you should try that "force negotiation" setting mentioned in that article above. it will go out and make sure none of your PCNS clients have a command file with an additional delay time that it needs to account for. if it does, it will add that to the 5 minutes of time, which in your case, it doesnt appear to have done that. this also happens with the NMC is rebooted.

moving on, let's say you have an 60 minutes of runtime total. the input power is lost. the UPS will run on battery for ~55 minutes and then when there is 5 minutes remaining, the UPS will tell PCNS via the NMC that it has a low battery condition. the PCNS client will begin its OS shutdown and continue to shutdown while the UPS is in the low battery condition. then, it factors in an extra 2 minutes for unforseen circumstances and then it adds your shutdown delay of 10 seconds and then it goes ahead and turns the UPS off. if the power had come back during this 7 minutes and 10 seconds, the UPS will still shutdown since you cannot interrupt this process but it will reboot and turn back on and start providing output power (thus your PCNS client should see that power has returned and turn back on if the BIOS is set correctly).

if you try to turn on the PCNS client during the low battery condition, which will be 5 minutes of runtime remaining to when the UPS runs out of battery, yes it will force the PCNS client to shutdown again if you try to turn it back on. the NMC is unicasting the low battery signal and will force the PCNS client to shutdown so that it does not turn off ungracefully? (is that a word) and drop when the UPS cuts output power.

hope that helps!

Reply
mcctech_apc
Ensign mcctech_apc
Ensign

Posted: ‎2021-06-30 07:48 PM

0 Likes
0
412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 07:48 PM

This was originally posted on APC forums on 10/13/2010


Yes, explains things perfectly, thanks! I just confirmed the entire shutdown process and now I am trying to get command execution working, but I will start a new thread about this.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc