PCBE 7.0.5 & Email

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCBE 7.0.5 & Email
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
114
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:32 AM . Last Modified: ‎2024-03-07 03:01 AM

0 Likes
9
1551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:32 AM . Last Modified: ‎2024-03-07 03:01 AM

PCBE 7.0.5 & Email

Hello,

We have around 25 Smart UPSs of various models connected to various machines which are all running PCBE 7.0.5.
All these installations have PCBE server configured to email a number of addresses in the standard configuration profile, all using the same SMTP server and all using the same email account.

Some of these email us when things happen, such as a power failure, some don't. All of these have the applicable networking hardware attached to the UPS so there's no question of whether they have access to the mail server or not.

To test, I currently have a flat XP SP3 machine next to me with PCBE 7.0.5 installed, attached to a Smart UPS 700 via RS232. I configured it as usual and sent/received a test email successfully. I then disconnected the UPS from the mains supply and noted that the software recognised that there was a power failure. It however did NOT email me.

In short, why is the software failing to send an email, and how do I fix it? I could of course configure each agent to send emails through the web interface, but to be honest, I'd just rather have this working as intended!

Thanks.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:00 AM

0 Likes
0
1552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:00 AM

The agent and server are installed on the same workstation and as far as I can see are communicating correctly. Can't really see another way of troubleshooting from this direction.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:01 AM

0 Likes
0
1552
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:01 AM

Hello,

We have around 25 Smart UPSs of various models connected to various machines which are all running PCBE 7.0.5.
All these installations have PCBE server configured to email a number of addresses in the standard configuration profile, all using the same SMTP server and all using the same email account.

Some of these email us when things happen, such as a power failure, some don't. All of these have the applicable networking hardware attached to the UPS so there's no question of whether they have access to the mail server or not.

To test, I currently have a flat XP SP3 machine next to me with PCBE 7.0.5 installed, attached to a Smart UPS 700 via RS232. I configured it as usual and sent/received a test email successfully. I then disconnected the UPS from the mains supply and noted that the software recognised that there was a power failure. It however did NOT email me.

In short, why is the software failing to send an email, and how do I fix it? I could of course configure each agent to send emails through the web interface, but to be honest, I'd just rather have this working as intended!

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:01 AM

0 Likes
0
1553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:01 AM

when you DON'T get the emails, the event log works fine right? so you see the events logged in the PCBE log.

how do we know PCBE isnt emailing? how do we know that the mail server is reachable when being emailed? have we checked this aspect of it?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:01 AM

0 Likes
0
1553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:01 AM

yeah i saw that but what does your agent configuration look like even so?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:01 AM

0 Likes
0
1553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:01 AM

are you using powerchute business edition deluxe and using the console GUI to configure email?

i would want to access each agent and see what type of notifications it is set up for but i realize you don't want to do that for each UPS.

see my screenshots. the first is the GUI for PCBE deluxe which i am wondering is where you have configured emails and then the second is the agent web interface that you can navigate to in order to check what events are configured via email for that particular agent.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:01 AM

0 Likes
0
1553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:01 AM

The only difference between my config and your screenshot is that I don't have "notification" for the event "power failed" configured.
Originally "e-mail" wasn't configured for this event either but I manually enabled it during testing.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:01 AM

0 Likes
0
1553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:01 AM

Hi

Configured through the PCBE GUI.
As mentioned, I recognise that I can configure the agent to email directly rather than using the PCBE server, but would rather not!

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:01 AM

0 Likes
0
1553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:01 AM

hmm ok. one other thing i thought of would be to make sure communication is open between the components of business edition.

not sure if that would cause this since everything else appears to be working but you can double check: [see this link|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=2790]

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:00 AM

0 Likes
0
1553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:00 AM

Yes the events are logged correctly, everything else happens as expected, just no email.

The only way I can verify that PCBE isn't emailing is indeed that nothing is being received by any of the listed recipients.

My test consisted of a machine which was consistently able to contact the mail server, connected to a smart UPS 700. When power failed, an email was received from the PCBE agent but not from the server... is that good enough as proof that the mail server/networking works?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:00 AM

0 Likes
0
1553
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:33 AM . Last Modified: ‎2024-03-07 03:00 AM

The agent and server are installed on the same workstation and as far as I can see are communicating correctly. Can't really see another way of troubleshooting from this direction.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of