Good Day,
ACRD600s, if the condenser and the unit are at the same level and the piping is over head are P traps to be used, if yes, where in the piping should it placed
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 01:32 AM . Last Modified: 2024-03-18 11:26 PM
thanks for the information
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 01:32 AM . Last Modified: 2024-03-18 11:26 PM
Hello Terrence.
I am assuming that you are going out the top of the RD600 unit and then changing to horizontal piping out to the condenser and then going down to the condenser. In this case, you would want a inverted trap at the top of the unit where the piping goes from vertical to horizontal on the discharge line. This is also assuming that you are not going to far (5-10 feet max) above the unit before going horizontal. If you have a drawing of the piping run, we can see if any others would be needed.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 01:32 AM . Last Modified: 2024-03-18 11:26 PM
Thank you. An inverted trap at the top of the discharge pipe coming out of the unit will be needed. No other traps are needed from the drawing. Make sure to pitch the horizontal discharge piping towards the condenser and the horizontal liquid piping towards the unit per the guidelines in the manual.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 01:32 AM . Last Modified: 2024-03-18 11:26 PM
Just to clarify. The Inverted trap is at the top of the vertical portion as it is changing to the horizontal run.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 01:32 AM . Last Modified: 2024-03-18 11:26 PM
thanks for the information
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.