Posted: 2021-06-28 01:34 AM . Last Modified: 2024-03-18 11:26 PM
Hello,
in the forum I found the same discussion with "lost communication to UPS". And the answer was "you need another firmware".
Can anybody me help to. My hardware is:
yezFXKza%2F4BqS4SCf%2FjmOA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png
Thanks.
Best regards
Lutz Fischer
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 01:34 AM . Last Modified: 2024-03-18 11:26 PM
What type/model of UPS is your AP9631 installed in? Currently you have Symmetra 3phase UPS firmware loaded onto it. If you have a Smart-UPS or different type of model, the firmware needs to be changed to that application so that the AP9631 and your UPS can "talk."
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 01:34 AM . Last Modified: 2024-03-18 11:26 PM
What type/model of UPS is your AP9631 installed in? Currently you have Symmetra 3phase UPS firmware loaded onto it. If you have a Smart-UPS or different type of model, the firmware needs to be changed to that application so that the AP9631 and your UPS can "talk."
Link copied. Please paste this link to share this article on your social media post.