High Discharge: Warning - Fix?
  • High Discharge: Warning - Fix?
Posted: ‎2021-06-28 01:34 AM . Last Modified: ‎2024-03-18 11:26 PM
854
I have tried clearing the event log and the alarm log for it to reset and start working again. However, same error keeps popping up. 'High Discharge: Warning'.
Hello. It sounds like there is an issue at the condenser. Make sure that the breaker for the condenser it has not tripped and check if the fan on the condenser start spinning when the unit inside comes on. If the fan is not coming on then an HVAC tech will be needed to check the controls and the motor on the condenser.
Thank you
Hello Tahmidur.
Do you have the model number of the unit that this is happening on? Does the compressor ever start on the unit or does it go right to high discharge?
Thank you
It turns on, spits out some cool air before start beeping and having a critical light on (red). I think the model is ACRD100
Thank you