Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
AP8853 PDU Fuse Protection on C13 sockets
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2801:35 AM. Last Modified: 2024-03-1811:26 PM
AP8853 PDU Fuse Protection on C13 sockets
I feel I'm missing something on this one but with only a 16A breaker protecting each bank on a AP8853 what is protecting the 10A rating of each C13 socket? Or indeed if a device says "fuse at 5A" how does that work when plugged into a PDU like this?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2801:35 AM. Last Modified: 2024-03-1811:26 PM
Hi,
Other than the bank breakers, the individual outlets on the AP8853 do not have additional protection, apart from the requirements that apply to C13/C14 connectors and cables. C13/C14 connectors/cables are standardized at 10A so devices with a C14 input connection would not pull a higher than 10A current.
A device that says "fused at 5A" typically has a 5A fuse built into its power supply circuit to limit its maximum current draw to 5A.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2801:35 AM. Last Modified: 2024-03-1811:26 PM
Hi,
Other than the bank breakers, the individual outlets on the AP8853 do not have additional protection, apart from the requirements that apply to C13/C14 connectors and cables. C13/C14 connectors/cables are standardized at 10A so devices with a C14 input connection would not pull a higher than 10A current.
A device that says "fused at 5A" typically has a 5A fuse built into its power supply circuit to limit its maximum current draw to 5A.