Output Frequency Range Setting

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Output Frequency Range Setting
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Kerjef
Kerjef
Cadet

Posted: ‎2024-11-27 08:04 AM

0 Likes
1
807
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-27 08:04 AM

Output Frequency Range Setting

Hello,


Yesterday afternoon the power coming into our Building lost a Phase of the Three Phase Input. The SMART-UPS (Model# SRT5KRMXLT) seemed to go into Battery Backup from the Log Entry below.

11/26/2024 15:56:25 Device UPS: Bypass not in range ; either frequency or voltage. 0x020F
11/26/2024 15:56:24 Device UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 0x0210
11/26/2024 15:56:17 Device UPS: Bypass not in range ; either frequency or voltage. 0x020F
11/26/2024 15:56:16 Device UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 0x0210
11/26/2024 15:56:10 Device UPS: Bypass not in range ; either frequency or voltage. 0x020F
11/26/2024 15:55:41 Device UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 0x0210
11/26/2024 15:55:41 Device UPS: Bypass not in range ; either frequency or voltage. 0x020F

Unfortunately the Server / Network equipment (Single Server, Switch and Router) did not keep running for some reason even though we had 34 Minutes Runtime from the UPS Status. My questions is since the Input Frequency was no longer 50/60 Hz, I am assuming the Output Frequency Range then was not 50/60Hz. The Power Configuration setting for the "Output Frequency Range" is set to Auto_50/60Hz. From the manual, the output frequency adjusts to match the input frequency when Auto_50/60 is selected. Would this setting have prevented the equipment from running off the Battery? If so should the "Output Frequency Range be set to "60 +/- .01 or 60 +/- 3.0" to ensure the Output Frequency Range is a constant 60Hz? I have attached a screenshot of the current Power Setting and the Event Log.

 

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX-RM
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Teken
Kirk Teken
Kirk

Posted: ‎2024-11-28 04:30 AM

0 Likes
0
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-28 04:30 AM

The system should be locked to 60 Hz and defined 60 +/- 0.1 Hz. This should stop the unit from hunting.

 

As an aside the NMC needs to be updated to the latest firmware. You also need to update the SMTP email settings for those failed aliases.

 

If you ignore doing so at the current firmware level it can / will cause the NMC to lock up and stop access and reporting alerts and connectivity to any connected NMS. ☝️

 

Questions Ask - If not please mark this as a solution to help the next person asking the same. ☝️

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore