Output Efficiency: load too low

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Output Efficiency: load too low
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:54 AM . Last Modified: ‎2024-03-18 03:02 AM

0 Likes
2
8452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:54 AM . Last Modified: ‎2024-03-18 03:02 AM

Output Efficiency: load too low

Hello,

We have three PowerEdge rack servers connected to one UPS (SMT3000RMI2U) which is presumably enough load but the UPS status is showing ''Output Efficiency: load too low''. The servers are running OK. No alert from the UPS as well.

Do you see any problem in the status screenshot please?  Do I have to replace the battery or send the UPS for servicing? 

Thanks for your help!

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 3000
  • battery
  • network-management-card
  • smart-ups
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 05:54 AM . Last Modified: ‎2024-03-18 03:02 AM

0 Likes
1
8447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:54 AM . Last Modified: ‎2024-03-18 03:02 AM

It's not a problem -- it just means efficiency is not reported at low loads. If we look at the efficiency graph for the SMX3000 we can guess it's around 80-90% efficient but the slope here is really steep so our guess is probably not very accurate.

There's two ways you can look at it:

- Since there's not much load, most of the power is being used by the UPS which is inefficient. You could get greater efficiency by putting more load on the UPS or using a smaller UPS.

- Just putting more load on the UPS won't save any energy even if it's more efficient, so why worry about it. The way to save energy would be to use fewer UPSes or use smaller ones.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 05:54 AM . Last Modified: ‎2024-03-18 03:02 AM

0 Likes
1
8448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:54 AM . Last Modified: ‎2024-03-18 03:02 AM

It's not a problem -- it just means efficiency is not reported at low loads. If we look at the efficiency graph for the SMX3000 we can guess it's around 80-90% efficient but the slope here is really steep so our guess is probably not very accurate.

There's two ways you can look at it:

- Since there's not much load, most of the power is being used by the UPS which is inefficient. You could get greater efficiency by putting more load on the UPS or using a smaller UPS.

- Just putting more load on the UPS won't save any energy even if it's more efficient, so why worry about it. The way to save energy would be to use fewer UPSes or use smaller ones.

Reply

Link copied. Please paste this link to share this article on your social media post.

clchow88
clchow88
Cadet

Posted: ‎2023-01-30 06:41 PM

In response to voidstar_apc
0 Likes
0
6442
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-30 06:41 PM

Hi, 

i have the same problem, i already turn off the alarm but it still keep with beep sound, please assist.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore