Outlet group getting "Available runtime exceeded..."

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Outlet group getting "Available runtime exceeded..."
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:16 AM . Last Modified: ‎2024-03-08 01:19 AM

0 Likes
2
728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:16 AM . Last Modified: ‎2024-03-08 01:19 AM

Outlet group getting "Available runtime exceeded..."

Hi,

From the FAQ on the "Available runtime exceeded..." event it seems the event is based on the "Low battery duration" setting. That is weird because based on the PCNS manual if the UPS has outlet groups the "Low battery duration" configuration is completely ignored, so why would there be an event on such a UPS based on that redundant setting? Unless there is a use for that setting even in an outlet group configuration, if then what is it? 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:16 AM . Last Modified: ‎2024-03-08 01:19 AM

0 Likes
0
728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:16 AM . Last Modified: ‎2024-03-08 01:19 AM

Hi,

On 2/24/2021 10:10 AM, Sol said:

That is weird because based on the PCNS manual if the UPS has outlet groups the "Low battery duration" configuration is completely ignored

PCNS does not ignore the low battery duration setting on any Smart-UPS. When the UPS reaches the low battery threshold the NMC reports the event to all registered PCNS clients. When the PCNS client see that the UPS is at low battery it will immediately begin the shutdown process. By default, PCNS will trigger a shutdown sequence if a low battery condition occurs or the UPS is commanded to turn off. The shutdown cannot be disabled for these events using the PCNS UGI. 

The Low Battery Duration set on the NMC should be equal to or greater than the Power Off Delay for the assigned outlet group. By default, the outlet group Power Off Delay will be the same value as the Low Battery duration configured on the NMC. PowerChute will automatically increase the Power Off Delay for the outlet group it is registered with, if the total shutdown time it needs is greater than the Power Off Delay.

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:16 AM . Last Modified: ‎2024-03-08 01:19 AM

0 Likes
0
729
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:16 AM . Last Modified: ‎2024-03-08 01:19 AM

Hi,

On 2/24/2021 10:10 AM, Sol said:

That is weird because based on the PCNS manual if the UPS has outlet groups the "Low battery duration" configuration is completely ignored

PCNS does not ignore the low battery duration setting on any Smart-UPS. When the UPS reaches the low battery threshold the NMC reports the event to all registered PCNS clients. When the PCNS client see that the UPS is at low battery it will immediately begin the shutdown process. By default, PCNS will trigger a shutdown sequence if a low battery condition occurs or the UPS is commanded to turn off. The shutdown cannot be disabled for these events using the PCNS UGI. 

The Low Battery Duration set on the NMC should be equal to or greater than the Power Off Delay for the assigned outlet group. By default, the outlet group Power Off Delay will be the same value as the Low Battery duration configured on the NMC. PowerChute will automatically increase the Power Off Delay for the outlet group it is registered with, if the total shutdown time it needs is greater than the Power Off Delay.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:16 AM . Last Modified: ‎2024-03-08 01:19 AM

0 Likes
0
728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:16 AM . Last Modified: ‎2024-03-08 01:19 AM

I guess I mistook "The maximum delay" for low battery threshold.

Thanks for pointing this out.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of