Out of warranty AP7752 fluttering between power sources. Help!

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Out of warranty AP7752 fluttering between power sources. Help!
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:59 AM . Last Modified: ‎2024-03-18 12:16 AM

0 Likes
5
876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:59 AM . Last Modified: ‎2024-03-18 12:16 AM

Out of warranty AP7752 fluttering between power sources. Help!

This unit is about 2.5 years old since installation, about four years old by MFR date.  When it's plugged into two power sources, it flutters between the two (click-click-click-click) and has even popped a circuit breaker due to this.  I replaced it with our spare, but as a several-hundred $$ unit, I'd like to know if it can be repaired before we go out and buy a new one.

Can anyone help?

Dave R.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:59 AM . Last Modified: ‎2024-03-18 12:16 AM

0 Likes
0
876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:59 AM . Last Modified: ‎2024-03-18 12:16 AM

Hi Dave,

First thing I'd do is log into it if you can and tell us what firmware is on it.

The event log in the device and just the current status in the interface may be very helpful in assisting with identifying the problem. The unit could've been damaged due to older firmware and being installed in a location with out of phase sources or a simple setting change based on the recommendations here (Common Rack Automatic Transfer Switch Scenarios and Questions | FAQs | Schneider Electric US) may help after we verify other bits of information I asked above.

Also, what are the input sources for A and B you're using currently (utility power, generator, UPS, etc)? Where was this installed previously and what were the input sources at that time?

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:59 AM . Last Modified: ‎2024-03-18 12:16 AM

0 Likes
0
876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:59 AM . Last Modified: ‎2024-03-18 12:16 AM

The original firmware did not support out of phase switching and we don't really suggest using these with a generator. It is likely that source A and B are out of phase and could've potentially damaged the unit.

Even if the other ones are still in operation, it is worthwhile to see what revs they are at to prevent future problems. It is also feasible they could be damaged if exposed to out of phase switching or a generator and it won't be identified until too late.

Tripping upstream breakers is usually an indication of welded relays due to out of phase sources and a hardware issue. Can you verify the firmware version numbers on this one for now and your others? What about access to the event log?

AP7750 is an older generation product (replaced by AP7750A now) that also does not support out of phase switching. AP7752 and the other models listed in the following link can at least be upgraded -> INFORMATION BULLETIN - Upgrading Rack ATS Firmware (AP77XX) - potential to permanently damage ATS du...

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:59 AM . Last Modified: ‎2024-03-18 12:16 AM

0 Likes
0
876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:59 AM . Last Modified: ‎2024-03-18 12:16 AM


Thank you.  I'll test this either today or tomorrow on this unit.

Where this was in production, the 'A' side was Gen/Flywheel UPS, and the street-side is not backed up in any way.  Two others in the same Data center configured the same, along with another 13 AP7750's (Installed in 2010) in the same building connected the same way are running fine.

We do monthy Generator tests (JACHO requirement), so the street sides are dropped monthly for all these units.

Dave R

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:59 AM . Last Modified: ‎2024-03-18 12:16 AM

0 Likes
0
876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:59 AM . Last Modified: ‎2024-03-18 12:16 AM

I am just realizing you referenced "on-net" so I take that to mean on the network?

Not sure if you need set up instructions but they are here (this is an NMC1 device and if you have its serial cable, its a RJ-12 to DB9, part # 940-0144 - if none of the other methods are an option anyway)->http://www.apc.com/support/index?page=content&country=US〈=en&id=FA156064

I also don't think we've ever tested this with a Flywheel UPS..

Anyway, the log might report something obvious too - i.e. power supply fault.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:59 AM . Last Modified: ‎2024-03-18 12:16 AM

0 Likes
0
876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:59 AM . Last Modified: ‎2024-03-18 12:16 AM

This unit is about 2.5 years old since installation, about four years old by MFR date.  When it's plugged into two power sources, it flutters between the two (click-click-click-click) and has even popped a circuit breaker due to this.  I replaced it with our spare, but as a several-hundred $$ unit, I'd like to know if it can be repaired before we go out and buy a new one.

Can anyone help?

Dave R.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:59 AM . Last Modified: ‎2024-03-18 12:16 AM

0 Likes
0
877
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:59 AM . Last Modified: ‎2024-03-18 12:16 AM

Hi Dave,

First thing I'd do is log into it if you can and tell us what firmware is on it.

The event log in the device and just the current status in the interface may be very helpful in assisting with identifying the problem. The unit could've been damaged due to older firmware and being installed in a location with out of phase sources or a simple setting change based on the recommendations here (Common Rack Automatic Transfer Switch Scenarios and Questions | FAQs | Schneider Electric US) may help after we verify other bits of information I asked above.

Also, what are the input sources for A and B you're using currently (utility power, generator, UPS, etc)? Where was this installed previously and what were the input sources at that time?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of