Older Symmetra 16000 with XR frame fault

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Older Symmetra 16000 with XR frame fault
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:48 PM . Last Modified: ‎2024-03-18 11:51 PM

0 Likes
3
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:48 PM . Last Modified: ‎2024-03-18 11:51 PM

Older Symmetra 16000 with XR frame fault

I have an older symmetra 16k (model symstr-pdblk) with an xr frame (model syxr12-bm) that is giving me a generic "An extended run frame fault exists". on the xr frame itself, it will flash an "E1" during the split-seconds it's failing. unfortunately, I cannot find out what this error code means. the units are from december 2002, and, other than replacing batteries and (I think) a power module, the parts are all still original. The message is sent to me via a NMC 9617.

if anyone can help me figure out what the error code means, I would appreciate it!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • code
  • e1
  • error
  • frame
  • symmetra
  • xr
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:48 PM . Last Modified: ‎2024-03-18 11:51 PM

0 Likes
0
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:48 PM . Last Modified: ‎2024-03-18 11:51 PM

Thanks for the response; unfortunately, the fault came back almost immediately. I've purchased a new card, but I can't find out if I can hot-swap the cards, or if I need to power down the xr frame to make the replacement.

EDIT: nevermind; called tech support and, yea! hot-swappable! I now have a happy xr frame again! laughing

See Answer In Context

  • Tags:
  • syxrcc
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:48 PM . Last Modified: ‎2024-03-18 11:51 PM

0 Likes
0
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:48 PM . Last Modified: ‎2024-03-18 11:51 PM

so, after reducing my search terms to a more generic "symmetra e1" (yell) I found the following FAQ on APC's site, FA157590, which suggests that it is the xr frame's communication card that is throwing the error and the solution is to "try and reseat the card". if this is really what is going on, can I reseat the card without having to remove power to the xr frame?

thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:48 PM . Last Modified: ‎2024-03-18 11:51 PM

0 Likes
0
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:48 PM . Last Modified: ‎2024-03-18 11:51 PM

bleh...more searching results in this FAQ: FA157406...

it suggests that, to reseat the comm card, all I have to do is loosen the thumbscrew until the microlatch disengages...seems a bit simplistic and doesn't seem to go all the way of actually reseating the entire card...

am I wrong, or is this all this involved in reseating the comm card on the xr frame?!?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:48 PM . Last Modified: ‎2024-03-18 11:51 PM

0 Likes
0
1442
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:48 PM . Last Modified: ‎2024-03-18 11:51 PM

Thanks for the response; unfortunately, the fault came back almost immediately. I've purchased a new card, but I can't find out if I can hot-swap the cards, or if I need to power down the xr frame to make the replacement.

EDIT: nevermind; called tech support and, yea! hot-swappable! I now have a happy xr frame again! laughing

  • Tags:
  • syxrcc
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of