Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-07-09 04:26 AM . Last Modified: 2024-02-14 10:22 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:26 AM . Last Modified: 2024-02-14 10:22 PM
Hi, I need to measure power consumed by the individual server and I am using APC 8641PDU.
How can I get power usage of each individual outlet? 1 through 24.
OID “rPDUOutletStatusLoad” is supposed to get the results but its not bringing.
http://oidref.com/1.3.6.1.4.1.318.1.1.12.3.5.1.1.7
Thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:26 AM . Last Modified: 2024-02-14 10:21 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:26 AM . Last Modified: 2024-02-14 10:21 PM
Thank you Angela.
Here is what I get. I have machines connected to PDU
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:26 AM . Last Modified: 2024-02-14 10:22 PM
Hi,
The OID you mentioned is intended for older Rack PDUs as noted here: http://www.apc.com/us/en/faqs/FA156179
For what you want, check under here - iso(1).org(3).dod(6).internet(1).private(4).enterprises(1).apc(318).products(1).hardware(1).rPDU2(26).rPDU2Outlet(9).rPDU2OutletMetered(4).rPDU2OutletMeteredStatusTable(3).rPDU2OutletMeteredStatusEntry(1)
Theres a few OIDs in this table for current, power, peak power, etc. Power is rPDU2OutletMeteredStatusEntry(1).rPDU2OutletMeteredStatusPower(7) or 1.3.6.1.4.1.318.1.1.26.9.4.3.1.7 which you should get an instance returned for each outlet on AP8641.
Hope that helps you.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:26 AM . Last Modified: 2024-02-14 10:21 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:26 AM . Last Modified: 2024-02-14 10:21 PM
Thank you Angela.
Here is what I get. I have machines connected to PDU