Posted: 2021-07-09 04:26 AM
This was originally posted on APC forums on 10/16/2017
Hi, I need to measure power consumed by the individual server and I am using APC 8641PDU.
How can I get power usage of each individual outlet? 1 through 24.
OID “rPDUOutletStatusLoad” is supposed to get the results but its not bringing.
http://oidref.com/1.3.6.1.4.1.318.1.1.12.3.5.1.1.7
Thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:26 AM
This was originally posted on APC forums on 10/16/2017
Thank you Angela.
Here is what I get. I have machines connected to PDU
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:26 AM
This reply was originally posted by Angela on APC forums on 10/16/2017
Hi,
The OID you mentioned is intended for older Rack PDUs as noted here: http://www.apc.com/us/en/faqs/FA156179
For what you want, check under here - iso(1).org(3).dod(6).internet(1).private(4).enterprises(1).apc(318).products(1).hardware(1).rPDU2(26).rPDU2Outlet(9).rPDU2OutletMetered(4).rPDU2OutletMeteredStatusTable(3).rPDU2OutletMeteredStatusEntry(1)
Theres a few OIDs in this table for current, power, peak power, etc. Power is rPDU2OutletMeteredStatusEntry(1).rPDU2OutletMeteredStatusPower(7) or 1.3.6.1.4.1.318.1.1.26.9.4.3.1.7 which you should get an instance returned for each outlet on AP8641.
Hope that helps you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:26 AM
This was originally posted on APC forums on 10/16/2017
Thank you Angela.
Here is what I get. I have machines connected to PDU