Hi, I need to measure power consumed by the individual server and I am using APC 8641PDU.
How can I get power usage of each individual outlet? 1 through 24.
OID “rPDUOutletStatusLoad” is supposed to get the results but its not bringing.
http://oidref.com/1.3.6.1.4.1.318.1.1.12.3.5.1.1.7
Thanks in advance.
Posted: 2021-07-09 04:26 AM
This was originally posted on APC forums on 10/16/2017
Thank you Angela.
Here is what I get. I have machines connected to PDU
Posted: 2021-07-09 04:26 AM
This reply was originally posted by Angela on APC forums on 10/16/2017
Hi,
The OID you mentioned is intended for older Rack PDUs as noted here: http://www.apc.com/us/en/faqs/FA156179
For what you want, check under here - iso(1).org(3).dod(6).internet(1).private(4).enterprises(1).apc(318).products(1).hardware(1).rPDU2(26).rPDU2Outlet(9).rPDU2OutletMetered(4).rPDU2OutletMeteredStatusTable(3).rPDU2OutletMeteredStatusEntry(1)
Theres a few OIDs in this table for current, power, peak power, etc. Power is rPDU2OutletMeteredStatusEntry(1).rPDU2OutletMeteredStatusPower(7) or 1.3.6.1.4.1.318.1.1.26.9.4.3.1.7 which you should get an instance returned for each outlet on AP8641.
Hope that helps you.