Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-07-01 04:39 AM . Last Modified: 2024-03-05 02:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:39 AM . Last Modified: 2024-03-05 02:03 AM
Hello,
In one of our sites we multiple APC UPS devices (5 in total) and one of the devices has reported errors on battery failure.
The UPS is programmed to send a shutdown command to the servers that are connected when the battery has 20 minutes runtime left.
So this UPS failure caused a shutdown of these servers, while there was power from an other circuit.
Is there any way to prevent the shutdown command on battery failure, and only send a shutdown command on power failure?
Thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:39 AM . Last Modified: 2024-03-05 02:03 AM
Assuming you are using PowerChute you could change the configuration profile. However, it makes more sense to determine why the UPS is witching to battery and correct that. You should also determine of UPS battery can sustain the load for the needed amount of time.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:39 AM . Last Modified: 2024-03-05 02:03 AM
Assuming you are using PowerChute you could change the configuration profile. However, it makes more sense to determine why the UPS is witching to battery and correct that. You should also determine of UPS battery can sustain the load for the needed amount of time.