Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-07-01 04:39 AM . Last Modified: 2024-03-05 02:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:39 AM . Last Modified: 2024-03-05 02:03 AM
Hello,
In one of our sites we multiple APC UPS devices (5 in total) and one of the devices has reported errors on battery failure.
The UPS is programmed to send a shutdown command to the servers that are connected when the battery has 20 minutes runtime left.
So this UPS failure caused a shutdown of these servers, while there was power from an other circuit.
Is there any way to prevent the shutdown command on battery failure, and only send a shutdown command on power failure?
Thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:39 AM . Last Modified: 2024-03-05 02:03 AM
Assuming you are using PowerChute you could change the configuration profile. However, it makes more sense to determine why the UPS is witching to battery and correct that. You should also determine of UPS battery can sustain the load for the needed amount of time.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 04:39 AM . Last Modified: 2024-03-05 02:03 AM
Assuming you are using PowerChute you could change the configuration profile. However, it makes more sense to determine why the UPS is witching to battery and correct that. You should also determine of UPS battery can sustain the load for the needed amount of time.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.